Nick,
     
     Regarding your item 1, the receptacles ratings can vary depending upon 
     the branch circuit (in the building) rating.  The U.S. National 
     Electrical Code (210-21(b) supplies tables for receptacle ratings for 
     various size circuits, as well as the maximum load (cord & plug) that
     can be connected to such receptacles.  I have combined information 
     from two tables in the NEC, as follows:
     
                                                        Cord & Plug
          Circuit Rating      Receptacle Rating        Maximum Load
             Amps                   Amps                    Amps
              15                  Not over 15                12
              20                           15                12
              20                           20                16
              30                           30                24
              40                     40 or 50                --*
              50                           50                --*

                                                 * These would be industrial
                                                   type plugs and not detachable
                                                   cord sets.

     Other things you might need to consider:
     1.   A single receptacle installed on an individual branch circuit is 
          required to have an ampere rating of not less than that of the 
          branch circuit.  For example, a single receptacle on a 20-ampere
          branch circuit must be rated at 20 amps; however two or more 15-ampere
          receptacles are permitted on a 20-ampere general-purpose branch 
          circuit.

     Another way of putting it, your anticipated load should not exceed 80%
     of the receptacle rating.

     Regarding your item 2, the NEC specifies various permissible loads and
     branch circuit ratings in volt-amperes, and I do not have building
     construction experience to tell you what is "typical".  However, the
     typical nominal supply voltage in the U.S. is 120; 120/240; 240, and
     208Y/120 volts.  My electrical dryer is rated at 240 volts and is
     connected via a heavy duty industrial type plug (I need to go home and
     check the receptacle rating!)  Hope someone else can provide you with more
     information.

          Tania Grant, Lucent Technologies, Octel Messaging Division
          [email protected]

______________________________ Reply Separator _________________________________
Subject: BOUNCE [email protected]:    Non-member submission from ["N
Author:  [email protected] at P_Internet_Mail
List-Post: [email protected]
Date:    12/17/97 11:50 AM


From: "Nick Evans" <[email protected]>
Subject: US supply Voltage questions

I wonder if anyone can help me with a couple of practical questions concerning 
USA supply voltages.

1.  Does anyone know what the normal maximum current rating is on a 110V 
supply for a domestic socket outlet.

2.  Are there any situations (for example in commercial installations) where a 
single phase supply of greater than 110V can (would normally be supplied)?  If 
so what would be the normal maximum current supply for this increased voltage.

Thanks a lot for any assistance.

Best regards


Nick Evans
Managing Director
Genesys IBS Ltd
Worldwide Product Compliance & Localisation
Tel:            +44 1600 710300
Fax:    +44 1600 710301
Mobile: +44 385 367348  (GSM)
E-mail: [email protected] (data transfer limit: 2Mb)
Web:    Http://www.gentel.co.uk/genesys



Received: from curly.eng.octel.com (148.147.200.26) by m-internet.corp.octel.com
with SMTP
  (IMA Internet Exchange 2.1 Enterprise) id 0032DE28; Wed, 17 Dec 97 08:59:22
-0800
Received: from gw3.octel.com (gw3.octel.com [148.147.1.15]) by
curly.eng.octel.com (8.6.12/8.6.12) with ESMTP id JAA28004; Wed, 17 Dec 1997
09:00:49 -0800
Received: (from daemon@localhost) by gw3.octel.com (8.6.10/8.6.12) id JAA11693;
Wed, 17 Dec 1997 09:00:19 -0800
Received: from europe.std.com(199.172.62.20) by gw3.octel.com via smap (V1.3)
        id sma011134; Wed Dec 17 08:59:09 1997
Received: by europe.std.com (8.7.6/BZS-8-1.0)
        id LAA24528; Wed, 17 Dec 1997 11:50:33 -0500 (EST)
Received: from world.std.com by europe.std.com (8.7.6/BZS-8-1.0)
        id LAA24523; Wed, 17 Dec 1997 11:50:30 -0500 (EST)
Received: from localhost by world.std.com (5.65c/Spike-2.0)
        id AA11733; Wed, 17 Dec 1997 11:50:30 -0500
List-Post: [email protected]
Date: Wed, 17 Dec 1997 11:50:30 -0500 (EST)
From: Jon D Curtis <[email protected]>
To: [email protected]
Subject: BOUNCE [email protected]:    Non-member submission from ["Nick Evans"
<[email protected]>]    (fwd)
Message-Id: <[email protected]>
Mime-Version: 1.0
Content-Type: TEXT/PLAIN; charset=US-ASCII
Sender: [email protected]
Precedence: list
Reply-To: [email protected]

Reply via email to