>From another angle:

When is a circuit considered NOT connected to earth ground?  In other
words, if the only connections to earth in a SELV circuit are through
isolating components such as 3kV capacitors (from point B to PE in the
drawing), is that circuit considered unearthed?  I understand that a
circuit isolated from protective earth by optos and relays is considered
unearthed.

Thanks,

Jack
Netaccess, Inc.

> -----Original Message-----
> From: [email protected] 
> Sent: Tuesday, July 14, 1998 1:08 PM
> To:   [email protected]
> Subject:      Re: protective earth 
> 
>  Alan,
>  
>  You asked:
>  >When considering the protectively earthed SELV circuit below are
>  >all points of the circuit (A,B and C) deemed to be connected to
>  >protective earth or just the current return leg.
>  
>  Yes, all points (A, B & C) depicted in the circuit in your drawing
> are, in 
>  fact, electrically connected to earth. They may not be directly
> connected as C 
>  is in this case, but all are electrically connected nonetheless. It
> is 
>  important to note here that each circuit [NOT EACH POINT IN A
> CIRCUIT] is 
>  "deemed" to be connected to earth if earth is connected to an
> appropriate point 
>  (usually a single point) in each circuit (e.g., the circuit supply
> return leg). 
>  Earthing requirements of IEC60950 referred to in previous emails of
> this thread 
>  must also be met, if your product is ITE.
>  
>  I hope this clears this up as this concept draws on fundamental
> circuit theory.
>  
>  The above represents only my humble opinion.
>  
>  Comments?
>  
>  Best regards,
>  Ron Pickard
>  [email protected]
> 

Reply via email to