Thanks to everyone for the input so far. Good information.
We know that if we put an isolation transformer in series it resolves the
program but the transformer would need to be large and expensive.
The Other
Brian
From: Mike Sherman ----- Original Message ----- [mailto:[email protected]]
Sent: Tuesday, July 21, 2015 4:42 PM
To: [email protected]
Subject: Re: [PSES] GFCI Nuisance Tripping
Does anyone know of an off the shelf product that could be plugged between the
product and the GFCI that would reduce the nuisance trips? Might give Brian
some relief as he redesigns his product.
Mike Sherman
Sent from Xfinity Connect Mobile App
------ Original Message ------
From: Ted Eckert
To: [email protected]<mailto:[email protected]>
Sent: July 21, 2015 at 1:16 PM
Subject: Re: [PSES] GFCI Nuisance Tripping
Hello Brian,
UL 943 does require testing for conducted immunity. The standard calls out the
IEC 61000-4-6 test method. The test level is 0.5 V with a frequency range of
150 kHz - 230 MHz. However, UL 943C states that the immunity tests of 943 are
not required to be performed on special purpose GFCIs covered under 943C.
GFCIs typically are fairly simple in design. There is just a simple circuit
looking for an imbalance on line and neutral. The standard call out no
frequency response and they can have problems with high frequency noise. I had
one product that passed the IEC 60950-1 leakage current test with 1.5 mA of
leakage current when using the specified human body model circuit. However, if
you used a multimeter, you could measure 9 mA due to the high frequency
components. This product would regularly trip GFCIs.
The long standing assumption was that GFCIs would only be used for kitchens,
bathrooms and garages where moisture may be present. The standards haven't
caught up to the concept that your kitchen appliances might have built-in
computers with switching power supplies.
Ted Eckert
The opinions expressed are my own an may not reflect those of my employer.
-----Original Message-----
From: Kunde, Brian [mailto:[email protected]]
Sent: Tuesday, July 21, 2015 9:04 AM
To: [email protected]<mailto:[email protected]>
Subject: [PSES] GFCI Nuisance Tripping
Standard Class A 115V~ GFCI (Ground-Fault Circuit Interrupters) are designed to
TRIP at currents around 6mA. I assume this current is accurately detected
between DC and some harmonic of 60hz. However, it is common knowledge that
GFCIs can false trip or nuisance trip when used with motor speed controllers,
lighting dimmer switches, frequency drives, etc. .
I'm not familiar with UL 943C. Does this standard call out specific immunity
levels, energy and frequency, that GFCI must properly operate at? Are there
published Trip Curves that shows current vs frequency?
Has anyone run across published data showing high frequency trip
characteristics of GFCIs?
We have been burned in the past with nuisance tripping GFCIs when products with
frequency drives ramp start a motor. We are trying to understand exactly what
is causing the GFCI to trip so we can design out the problem in future
products. Any insight, recommendations, or suggestions would be most
appreciated.
Best regards,
The Other Brian
________________________________
LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]<mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher: <[email protected]<mailto:[email protected]>>
David Heald: <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]<mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher: <[email protected]<mailto:[email protected]>>
David Heald: <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]<mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
________________________________
LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>
For policy questions, send mail to:
Jim Bacher: <[email protected]>
David Heald: <[email protected]>