On Tue, Mar 12, 2013 at 1:39 AM, Willie McKemie <[email protected]> wrote:
> On Mon, Mar 11, 2013 at 07:51:34PM -0700, peri hartman wrote:
>> Incidentally, a year or so ago, i emailed the program director for the
>> wash-ore I5 ESVE network.  They said, i'm pretty certain, the cost was
>> about  $20K per station.  I presume most of that is bringing the power to
>> the  location.  At any rate, the cost of the connector and contactor is
>> relatively small.  I have no idea how much it costs to install RV hookups -
>> presumably a lot less.  Maybe they are substantially lower power?
>
> I believe most 240vac RV panels do 50 amps while most J1772 EVSEs do
> only about 30 amps.

Technically, if you're charging an EV on your typical RV panel with a
14-50 outlet, you should only be charging at 40A maximum as charging
an EV counts as a continuous load and the NEC dictates that the
ampacity of a circuit be derated by 20%.

This is why your typical 30A J1772 EVSE is installed on a circuit that
can handle at least 40A and is protected by a 40A breaker.

-Dave