Yes, we double-checked that. I have seen that happen before and it's one of
my early diagnostic steps for something like this.




On Tue, Jun 9, 2020 at 9:18 AM Mac Lewis <[email protected]> wrote:

> Hi Jason,
>
> Are you certain that the branch circuits aren't crisscrossed somewhere,
> meaning that an L1 branch 1, isn't connected to an L2 branch 2?  That could
> explain two different breakers tripping.
>
> Good luck
>
>
> On Wed, Jun 3, 2020 at 1:07 PM Jason Szumlanski <
> [email protected]> wrote:
>
>> Undoubtedly, the termination caps are the second thing we check after the
>> rooftop junction box(es). These are prone to installation errors, even when
>> the right parts are used. And given the cost, I've thought very long and
>> hard about abandoning them altogether and terminating strings in small
>> j-boxes with watertight fittings. But in this case, there was no evidence
>> of improper installation (we replaced them) and it was not correlated to
>> rain events.
>>
>> We are well equipped with bare Q-cable and field wireables that we could
>> use for troubleshooting to bypass certain sections, but the intermittent
>> nature of the problem and unpredictable timeframe between faults is very
>> frustrating. While this is a rare occurrence, it is definitely a "con" to
>> consider when comparing string vs. microinverters that I had not strongly
>> considered in the past. I'm intent on getting to the bottom of this in
>> order to learn what to look for in the future and how to approach diagnoses
>> of Enphase branch circuit faults.
>>
>> Jason
>>
>>
>>
>>
>>
>> On Wed, Jun 3, 2020 at 2:31 PM Amos Post <[email protected]>
>> wrote:
>>
>>> I was just at a site last week where the Enphase branch circuit breaker,
>>> outside utility disconnect breaker, and feed breaker in the main panel all
>>> tripped simultaneously, and it happened about 1 hour before I showed up
>>> onsite.  The customer said it had happened 1 other time last fall but that
>>> time it was just the 1 branch circuit in the Enphase combiner panel.
>>> Interestingly the customer mentioned that he had just washed off the
>>> panels, also about 1 hour before I got there.  I went on the roof and found
>>> that the installing contractor had not put on the Enphase termination caps.
>>>  1 string was wire-nutted with regular wire nuts and sitting on the roof,
>>> and the roof was damp right there. This was a fairly flat roof.  The other
>>> micro trunk cable was just cut with no protection at all, tied to the rail…
>>>
>>>
>>>
>>>
>>>        Amos Post
>>>    Integrity Energy
>>>   W 802.763.7023
>>>    C 802.291.2188
>>>     ienergyVT.com
>>> <https://mailtrack.io/trace/link/f1ae9e0c71265067b985055083179eea0fff7f47?url=http%3A%2F%2Fwww.ienergyvt.com&userId=1613865&signature=7ffa18528c69326a>
>>>         Facebook
>>> <https://mailtrack.io/trace/link/dd75f6ff58a0e98e9008c1388c3a91e7995d1093?url=https%3A%2F%2Fwww.facebook.com%2Fintegrityenergyllp%3Fref%3Dhl&userId=1613865&signature=8fbb658055c3a9ea>
>>>
>>> On Jun 3, 2020, at 2:05 PM, Jason Szumlanski <
>>> [email protected]> wrote:
>>>
>>> The breaker in the main panel IS tripping simultaneously with one of the
>>> branch circuit breakers each time.
>>>
>>>
>>>
>>>
>>>
>>>
>>> On Wed, Jun 3, 2020 at 12:43 PM Jay <[email protected]> wrote:
>>>
>>>> A question that keeps nagging me is why do these breakers trip and not
>>>> the breaker in the main panel?
>>>> Presuming there is a 40 amp in the main
>>>>
>>>> I would have thought that given all the times the breakers have tripped
>>>> at some point that one would have tripped and I can’t understand why not?
>>>>
>>>> Jay
>>>>
>>>> On Jun 3, 2020, at 8:27 AM, Jerry Shafer <[email protected]>
>>>> wrote:
>>>>
>>>> 
>>>> Wrenches
>>>> Looking g at the bigger breaker tripping at the same time is very
>>>> likely do to response time of the breaker nothing more. As l suggested in a
>>>> previous message. Use a non bridged breaker to see if it is one or both
>>>> legs that trip. Also an eguage will help to see what if anything leads up
>>>> to the failure and when.
>>>> Jerry
>>>> Jerry
>>>>
>>>> On Wed, Jun 3, 2020, 7:58 AM Jason Szumlanski <
>>>> [email protected]> wrote:
>>>>
>>>>> I wonder about that. Of course, it could be the "inverter output
>>>>> circuit" having a fault in the wiring still (an intermittent issue
>>>>> somewhere within the IQ cable or home run wiring). But internal to the
>>>>> microinverter, is it possible that a fault could still occur at night? I
>>>>> had a suggestion from another wrench that there are film capacitors on the
>>>>> AC output side, but are these isolated when there is no DC input? It seems
>>>>> unlikely that this would be an issue, but I have seen microinverters
>>>>> reporting a couple of watts at night (in Enlighten). I'm not sure how real
>>>>> that is.
>>>>>
>>>>> The overriding question I have is what kind of fault would cause BOTH
>>>>> a branch circuit and the main solar breaker to trip simultaneously? That
>>>>> seems odd to me. If any normal load branch circuit has a fault, you don't
>>>>> often see premises main breakers tripping, or even feeder circuit 
>>>>> breakers.
>>>>>
>>>>> I got to thinking that maybe there is some kind of issue between the
>>>>> BR220 and CH240 breakers not playing nicely together. But I would think
>>>>> this would be a well-known issue because I'm sure there are tons of CH
>>>>> feeder breakers in the wild with BR branch circuits downstream.
>>>>>
>>>>>
>>>>>
>>>>> On Tue, Jun 2, 2020 at 9:25 AM <[email protected]>
>>>>> wrote:
>>>>>
>>>>>> If it trips at night, we know it is not the output from the inverters
>>>>>> causing the tripping. The current must be coming from the grid.
>>>>>> ---
>>>>>>
>>>>>>
>>>>>>
>>>>>> On 2020-06-01 12:05, Jason Szumlanski wrote:
>>>>>>
>>>>>>
>>>>>> It's not weather. It's at all times of the day and night, and I
>>>>>> confirmed that there is no correlation to rain or high winds. That was my
>>>>>> first suspicion.
>>>>>>
>>>>>>
>>>>>> On Mon, Jun 1, 2020 at 10:27 AM Ray <[email protected]> wrote:
>>>>>>
>>>>>> Is it at all weather related?  Rain, or high humidity?  High
>>>>>> temperatures?  Do you have any indication what time of day it trips off 
>>>>>> at?
>>>>>>
>>>>>> Ray Walters
>>>>>> Remote Solar
>>>>>> 303 505-8760
>>>>>>
>>>>>> On 6/1/20 10:23 AM, Jason Szumlanski wrote:
>>>>>>
>>>>>> Well, that didn't resolve it. The main breaker and a branch circuit
>>>>>> breaker tripped again a few days ago. It was the same branch this time.
>>>>>>
>>>>>> As my next diagnostic step I swapped two circuits (on which breaker
>>>>>> they are landed). If history is a guide, it will work for about two weeks
>>>>>> and then trip again.
>>>>>>
>>>>>> I'm dumbfounded. I really don't want to have to tear this whole
>>>>>> system apart. At this point, if I have to remove all the modules, I feel
>>>>>> that I need to replace all of the trunk cable which is an expensive
>>>>>> proposition. I really don't know what else to do at this point.
>>>>>>
>>>>>> Jason
>>>>>>
>>>>>>
>>>>>> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski <
>>>>>> [email protected]> wrote:
>>>>>>
>>>>>> I strongly suspect the CH240 combined breaker was compromised (we
>>>>>> will see). Since it happened that two different strings tripped, I doubt 
>>>>>> I
>>>>>> have two microinverters with internal faults. It has to be the combined
>>>>>> breaker. I was just surprised that branch circuit breakers were tripping
>>>>>> simultaneously with the combined output breaker.
>>>>>>
>>>>>> Of all the supply side connected systems I have installed, I have
>>>>>> never seen a combined output fusible disconnect fuse blow, but I have 
>>>>>> seen
>>>>>> many combined output breakers tripped. I was worried early on that I 
>>>>>> would
>>>>>> be replacing fuses constantly, but that has not been an issue whatsoever.
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> On Thu, May 21, 2020 at 11:15 AM <[email protected]> wrote:
>>>>>>
>>>>>> Actually, we had a IQ7 string loaded up to its max panel size and max
>>>>>> string length and in the spring on cool, clear day, it tripped the 
>>>>>> string's
>>>>>> associated breaker in the Enphase combiner.
>>>>>>
>>>>>>
>>>>>> We reset but of course that breaker was impaired and it tripped
>>>>>> again. We replaced and never had an issue going forward. We suspect the
>>>>>> breaker was less than perfect from the start as we've add equally nice 
>>>>>> days
>>>>>> since.
>>>>>>
>>>>>>
>>>>>> This almost reminds me of loading up Outback FM80. It says 4,000
>>>>>> watts but in reality, 3,600 is the max when amps spike. I will be extra
>>>>>> careful going forward on IQ7 string length when going to the max
>>>>>> published...
>>>>>>
>>>>>>
>>>>>> My story.
>>>>>>
>>>>>>
>>>>>> Scot
>>>>>>
>>>>>>
>>>>>> *From:* RE-wrenches <[email protected]> *On
>>>>>> Behalf Of *Jason Szumlanski
>>>>>> *Sent:* Thursday, May 21, 2020 8:57 AM
>>>>>> *To:* RE-wrenches <[email protected]>
>>>>>> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng
>>>>>>
>>>>>>
>>>>>> I'm trying to resolve an intermittent frustrating problem with and
>>>>>> Enphase IQ system. There are three AC Branch circuits of 9 microinverters
>>>>>> each coming into an Enphase AC combiner.
>>>>>>
>>>>>>
>>>>>> What has been happening is one of the BR220 branch circuit breakers
>>>>>> and the combine CH240 breaker in the main backfed load center have been
>>>>>> tripping simultaneously. It has happened about four times in the last 6
>>>>>> months. It was always the same branch circuit breaker, so we kept
>>>>>> investigating that string, checking the junction box, trunk cable, and 
>>>>>> cap,
>>>>>> etc. Finally we swapped out the BR220 breaker.
>>>>>>
>>>>>>
>>>>>> Fast forward 4 weeks, and we got another call. This time a different
>>>>>> branch circuit breaker and the main breaker tripped simultaneously. We
>>>>>> checked that branch circuit and could not find any fault. It seems 
>>>>>> unlikely
>>>>>> that two branch circuit breakers would be faulty, so we have now switched
>>>>>> out the CH240 main breaker in hopes that it is the culprit.
>>>>>>
>>>>>>
>>>>>> I'm not totally confident in this resolution and I have my fingers
>>>>>> crossed. If that doesn't work, does anyone have any suggestions on 
>>>>>> another
>>>>>> diagnostic step? These intermittent problems are a major hassle. One
>>>>>> thought I had was to switch to a supply side interconnection with a 
>>>>>> fusible
>>>>>> disconnect. Maybe the intermittent fault would blow one of the two line
>>>>>> fuses so at least I could narrow it down to which line the fault is on if
>>>>>> there is in fact a fault.
>>>>>>
>>>>>>
>>>>>> I have experienced two other tripping breaker issues with Enphase
>>>>>> systems in the past. Neither of them were systems I installed. One turned
>>>>>> out to be branch circuits that were not properly paired up and landed on
>>>>>> different breakers. Another time we had an inverter with an internal 
>>>>>> fault
>>>>>> which eventually"blew up" with a loud popping noise and smoke billowing 
>>>>>> out
>>>>>> of it. That happened after resetting a trip breaker multiple times. This
>>>>>> case seems to be unrelated to those issues. I'm perplexed.
>>>>>>
>>>>>>
>>>>>> Jason Szumlanski
>>>>>>
>>>>>> Florida Solar Design Group
>>>>>>
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> List Address: [email protected]
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/abcb879ec34ff2316c6c04adb6f43fb133c4b18d?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=a7bf07d268af1ce9>
>>>>>>
>>>>>> List-Archive:
>>>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>>>> <https://mailtrack.io/trace/link/6685b067141605e37a6f31b7ffff135296f2785f?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=c540d40c34907fa1>
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>> <https://mailtrack.io/trace/link/5789f30d88036bcf5bcf6dd652a8dd9353993d28?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8898fa5d278e3c3c>
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/b68193d7a34f224fa682fd9fa59c4ff98acd2c18?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=1adbfb43c6cb7d19>
>>>>>>
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> List Address: [email protected]
>>>>>>
>>>>>> Change listserver email address & 
>>>>>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>  
>>>>>> <https://mailtrack.io/trace/link/f2afb5351fb14412ed4c81236b9e8ebd3200928c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=0a5d3677a74cb352>
>>>>>>
>>>>>> List-Archive: 
>>>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>>>>  
>>>>>> <https://mailtrack.io/trace/link/99279ef375e9fec51dd19aa352f83e695a609ad4?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=2685b6f4b3f7107c>
>>>>>>
>>>>>> List rules & etiquette:www.re-wrenches.org/etiquette.htm 
>>>>>> <https://mailtrack.io/trace/link/45524f706af56f5eb5555c370b0abd19934f9f37?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=95bd53c5cb33f15d>
>>>>>>
>>>>>> Check out or update participant bios:www.members.re-wrenches.org 
>>>>>> <https://mailtrack.io/trace/link/c757a47333a36d3408799e19126166251b289857?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=54885f17dec2e25e>
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> List Address: [email protected]
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/c6f08a67b986c33b8b59ac0bd339b308a48a175e?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=bb93d63238d5d8dc>
>>>>>>
>>>>>> List-Archive:
>>>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>>>> <https://mailtrack.io/trace/link/0c041ae67b1c6fe20de95e55c0bb2afc83dd5d81?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=78edab1e4fc7a8ad>
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>> <https://mailtrack.io/trace/link/cf59d00ab405496a630f1d4d45e4b2bd77030f72?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f0c62395d90274f6>
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/f430c5dffc2801d7039673d54479b25f79815f3f?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=e4226ffba1872824>
>>>>>>
>>>>>> <blocked.gif>
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> List Address: [email protected]
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/be8ac4a7f6307d1a0528ce4ce2586b8a5badd580?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=028ed403dc9f1705>
>>>>>>
>>>>>> List-Archive:
>>>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>>>> <https://mailtrack.io/trace/link/de4c20c5241e85f88c3ecbf4e9f02ed8a3d8df62?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=a31a829e96a0f613>
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>> <https://mailtrack.io/trace/link/bcdfbf919a38fca7daa9f63a3753be2a8839516f?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=cb1fc0e3eed5b766>
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/d7a869026f13f093bec9fc2ab43a041ff1e67d36?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=39eab98d8d1600b2>
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> List Address: [email protected]
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/e3206568e51fa8041d7b58880132ee3d54ede7db?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=641eeb4d1170e066>
>>>>>>
>>>>>> List-Archive:
>>>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>>>> <https://mailtrack.io/trace/link/564cfb19b6bbc4ad08d0ef25d751bd90fe873102?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5cc41caa96af4fa0>
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>> <https://mailtrack.io/trace/link/38090a08053d58be1cdaaf1fe313d70b74804384?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=277296e778ef7ded>
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/1bb76ebe37c98898e6e271e9c1e1952e3bd41406?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=84e48e17343f641a>
>>>>>>
>>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address: [email protected]
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/f1307c0514322bf32baa72086de9c35101d48c60?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c3e9d23a555228ba>
>>>>>
>>>>> List-Archive:
>>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>>> <https://mailtrack.io/trace/link/575f921af0d3546276fa0ca0c8c24a9e2b0caa94?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=3120c1fd0ece06ce>
>>>>>
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> <https://mailtrack.io/trace/link/38090a08053d58be1cdaaf1fe313d70b74804384?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=277296e778ef7ded>
>>>>>
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/1bb76ebe37c98898e6e271e9c1e1952e3bd41406?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=84e48e17343f641a>
>>>>>
>>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: [email protected]
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/0ed0026af0ea60bda04e52f7009cafc651d72e1b?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=487858d5ab249895>
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>> <https://mailtrack.io/trace/link/98f120799307aa490bfbd65a2a944b512d63bf6d?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=dbac2d7020c86632>
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/1d80b29154c3660bd9bb3195c5cdb6c1de2d3a99?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=dd536a814d770bb0>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/1465b63e1e7264f2e7b056b5fe561362e1f81102?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=97112590ab5148e7>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: [email protected]
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/0ed0026af0ea60bda04e52f7009cafc651d72e1b?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=487858d5ab249895>
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>> <https://mailtrack.io/trace/link/98f120799307aa490bfbd65a2a944b512d63bf6d?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=dbac2d7020c86632>
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/1d80b29154c3660bd9bb3195c5cdb6c1de2d3a99?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=dd536a814d770bb0>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/1465b63e1e7264f2e7b056b5fe561362e1f81102?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=97112590ab5148e7>
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/0ed0026af0ea60bda04e52f7009cafc651d72e1b?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=487858d5ab249895>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> <https://mailtrack.io/trace/link/98f120799307aa490bfbd65a2a944b512d63bf6d?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=dbac2d7020c86632>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/220b27b7aa679943c177cae16e6bb10d13d30726?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f4e65d052a6aee2a>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/e1af49991f4be545d5111c2d35a50447dd6748ee?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=c835a4ae01918ae8>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/e2b5dd1c6150d45819d191a5e6dd8c3c5d8d23d2?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=9e6854f9a2cdbbe3>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> <https://mailtrack.io/trace/link/b7feb32ad9295c42bdccb9c0947958cf1a4e4600?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=67663234ecc53a8a>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/220b27b7aa679943c177cae16e6bb10d13d30726?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f4e65d052a6aee2a>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/d1685bebfada0e102cd25b06611d42c7f7d4cf7c?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=c95cb20c5e26d7db>
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/e2b5dd1c6150d45819d191a5e6dd8c3c5d8d23d2?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=9e6854f9a2cdbbe3>
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>> <https://mailtrack.io/trace/link/b7feb32ad9295c42bdccb9c0947958cf1a4e4600?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=67663234ecc53a8a>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/220b27b7aa679943c177cae16e6bb10d13d30726?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f4e65d052a6aee2a>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/d1685bebfada0e102cd25b06611d42c7f7d4cf7c?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=c95cb20c5e26d7db>
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/e2b5dd1c6150d45819d191a5e6dd8c3c5d8d23d2?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=9e6854f9a2cdbbe3>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/b7feb32ad9295c42bdccb9c0947958cf1a4e4600?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=67663234ecc53a8a>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/8df50da71b9ff285f72be0473fd43a926ec7f7c2?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=70b9da309bd22425>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/648132ad8da551fe2db09087fd1d2052a1ac2509?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=82631c272f677300>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to