RE: NEAR/ FAR FIELD CORRELATION ISSUES

1999-06-18 Thread Morse, Earl

I beg to differ.

It is ludicrous to believe that components or for that matter subassemblies
can be certified and then combined to make a compliant system.

CE + CE doesn't always equal CE

The reduction of emissions is highly  reliant on component placement.  The
same parts can be arranged on circuit boards in compliant and non-compliant
patterns.  Same with subassemblies.

While the current measurement techniques are difficult they are about as
close to the truth as we can get.  Even if that means an 8 dB swing from
site to site.

The reason that we see PCs consistently fail by as much as 20 dB is because
of a lack of enforcement.  Many computer manufacturers sneak through the
requirements with their one of a kind golden units never to worry about
compliance again.  Very few get caught and it is worth the bucks to keep the
production lines going rather than shutdown the lines.

Who was the last computer manufacturer you heard of that was forced to
shutdown until an EMC problem was fixed?  I have a book of test reports on
competitor's products.  They fall into the categories of compliant, near
compliant (looks like they tried), and fails miserably (didn't try, didn't
care, and outright lied on any self declarations).  The failing companies
seem to be doing just as brisk a business as the passing companies without
having to worry about the cost of EMC.


Earl Morse
Portable Division EMC Design
Compaq Computer Corporation
Phone:  281.927.3607
Pager:  713.717.0824
Fax:  281.927.3654
Email:  earl.mo...@compaq.com mailto:earl.mo...@compaq.com 


-Original Message-
From:   Grasso, Charles (Chaz)
[mailto:gra...@louisville.stortek.com]
Sent:   Friday, June 18, 1999 10:33 AM
To: 'Lou Gnecco'; emc-p...@majordomo.ieee.org
Subject:RE: NEAR/ FAR FIELD CORRELATION ISSUES


I cannot agree more!! We, not the government, need to
drive the technology for EMC.

I have followed this thread with interest. I have long
believed
that if EMC was to maintain credibility we (EMC ) would have
to
come up with a method of demonstrating compliance in spite
of the
many and varied combinations. One way is to test at the
component
level - like our Safety brethren - and call the assembly of
tested
components good!!

This is methodology can be made consistent with good
engineering 
design practice unlike the existing FCC rules for Class B
equipment.
On the surface the FCC Rules appear to be similar to
component level
testing - but under the hood, they are completely different.
There are
PCs out there that fail by as much as 20dB. 

I am all for a more logical and consistent design approach
to EMC!!

Thank you
Charles Grasso
Advisory Engineer
StorageTek
2270Sth 88th Street
Louisville CO 80027 M/S 4247.
Tel:303-673-2908
Fax:303-661-7115
email:gra...@louisville.stortek.com
Web Site:
http://www.ewh.ieee.org/r5/denver/rockymountainemc/




-Original Message-
From: Lou Gnecco [mailto:l...@tempest-inc.com]
Sent: Friday, June 18, 1999 6:52 AM
To: emc-p...@majordomo.ieee.org
Subject: Re: NEAR/ FAR FIELD CORRELATION ISSUES



For this to work, the government would have to change the
rules completely,
setting a new set of near field procedures and  limits. This
is doable but
hard to sell.

A good way to start would be if we did it. If
someone in industry
writes up a procedure and a set of limits, then everyone
could use that as a
straw man, (criticizing and refining it) until eventually
most people
agreed.
Eventually it could become an industrial (such as
IEEE) standard.
Then the govt would find it much easier to adopt it as is or
after making
their own modifications. 

lou 


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
   

Re: NEAR/ FAR FIELD CORRELATION ISSUES

1999-06-18 Thread khardin

Arun:

I agree that a lower cost and simpler method would be nice but you have a very
difficult
problem to solve.  Your basic problem is correlating to an OATS site.
Theoretically
this is possible using the equivalence principle but it is hard to do.  First
one must
create a surface that totally incloses the system to be tested.  Next you need
to
measure instantaneous  electric and magnetic fields as a function of time and
direction while the product
performs all its functions over this surface.  From this information, one can
predict the
fields at 3m or 10m.  If you just find the magnitude of the magnetic field, you
do not know
if it will add or cancel with another magnetic field from some other place in
the product.
Phase and time are both important.  What if I have two pulsing fields that
happen a different
times.  Do you add them?

We use near field probing to locate radiated problems and many times we will
eliminate
a strong near field source to find out that the far field has not changed.  If
you keep reducing
the near field sources then eventually you find the one that solves the problem
in the far field
and all other fixes can then be removed.

This is a good debate and I wish you luck!

Sincerly,
Keith Hardin Ph.D., NCE
Senior Engineer
Lexmark International Inc.




lou%tempest-inc@interlock.lexmark.com on 06/17/99 08:24:26 AM

Please respond to lou%tempest-inc@interlock.lexmark.com

To:   emc-pstc%majordomo.ieee@interlock.lexmark.com
cc:(bcc: Keith Hardin/Lex/Lexmark)
Subject:  Re: NEAR/ FAR FIELD CORRELATION ISSUES





Arun:
I heartily agree  with everything you said. Well done!

It will not be easy to sell this idea to the emc world.
When the standards are vague, acane and constantly-changing, and when it is
unnecessarily expensive to set up and perform a test, this constitutes what
is known in business as a Barrier To Entry that is, a way to artificially
limit competition. Test laboratories (like us, for example) can charge more
money when there are barriers to entry.
People who make special instruments and antennas for EMC testing
(like us) would lose out if there were fewer barriers to entry. Also people
who install  test shielded rooms, etc. There are substantial entrenched
interests whose rice bowls would be threatened if emc became something
anyone could do.

I personally believe that the process can and should be simplified.
It would help the manufacturers, who are the ones that really drive the
economy.
It would specially help small manufacturers.

Like us.

Lou


At 11:18 AM 6/17/99 +1000, you wrote:


Greetings and Salutations! I was wondering if this could be mailed out via
the epc-pstc channels.

I want to know if anyone is doing any work in near/ far field correlation
to commercial EMC standard limits area and possibly correspond with them
with a view to exchanging notes.

Brief Follows:

Brief:

Application of Near Field and possibly Surface probe techniques in
Evaluating Emissions from source equipment and correlating/quantifying this
data to an OATS, LISN, Absorbing Clamp etc based measurement..

Details:

We assume that the current EMC compliance regime around the world has
quantified limits of compliance to which if every source equipment adheres
to, then it has a reasonable chance of performing as intended in a real life
situation, noting that the immunity threshold test levels are much more
stringent than EM emission limits.

Current EMC measurements are very cumbersome, require large expense in
setting up and maintaining (calibrating) OATS, LISNS, Absorbing Clamps,
Ferrite tiled lined semi- anechoics etc. Despite this expense, the
measurement uncertainities are still of the order of 6 to 10dB (inherent).

Every newly released EMC standard by IEC CISPR or CENELEC has potentially
new transducers and new headaches from point of view of sourcing and
maintenance, calibration.  EMC today is where Safety was 10 years ago. I am
of the opinion that EMC testing should be simplified and reasonably
accessible to all end users.

Continued progress and urban development has led to increasing levels of
broad and narrowband noise to the extent that ambient profiles sometimes
swamp out the limits; this has led to most test houses in the EU to opt for
GTEMS or semi-anechoics (referred to as alternative all weather test
sites) at considerable expense.

Current techniques such as emission E Field prescanning in shielded rooms
prior to OATS based testing with biconilog antennae have the drawbacks of
peaking the emissions and reflections/standing waves.

Hence:

I propose to develop near or surface probe H (inverse of E)  field
techniques which actually senses the emission profiles and correlate them to
an Absorber clamp, or OATS or LISN (Common mode fix) or whatever. Cables,
panels, slots etc could be sniffed with a Loop and if it is possible to
correlate this near or induction field data to compliance limits then it
becomes very easy 

EU participating countries

1999-06-18 Thread Dave Clark

Does anyone have an updated list of the EU countries?  Or better yet the
countries which recoginze the EEC Directives (CE Marking).  I think there
are some EFTA countries included in this list.

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Pacemakers

1999-06-18 Thread Brian At Work
How do I know if a product MIGHT interfere with a Pacemaker or not?  What types 
of emissions and levels are Pacemakers sensitive to?  Does a product evaluation 
check list exist to help determine this.

I know nothing about Pacemakers. BTW, we manufacture laboratory and IT 
equipment.

Thank you,
Brian


RE: NEAR/ FAR FIELD CORRELATION ISSUES

1999-06-18 Thread Roman, Dan

I also have been following this thread with interest, but even more
practical and technically less challenging alternate methods of testing take
too long for acceptance in my opinion.  Forget near-field measurements with
probes, I'd like to see quicker movement on acceptance of standards like
EN50147-3 for fully anechoic compact chambers.  I'm not going to get greedy
and look for (or expect) near field or cable clamp measurement acceptance in
the near future.

Since I mentioned it, does anyone know if there is movement or progress in
the area of standards tailored specifically for compact chambers like
EN50147-3?

-- 
Dan Roman, Compliance Engineer * mailto:dan.ro...@dialogic.com 
*Voice: +1 (973) 993-3000 ext. 6485  Fax: +1 (973) 993-8466 

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



US/CE Compatible Equipment Designs

1999-06-18 Thread pitteri



Hello Group:

My company produces a broad line of power-operated, commercial food
equipment. This equipment is UL Listed for the U.S. market and a number of
these models have the CE Mark for Europe. Currently, there is some overlap
in design but still a number of differences mainly to satisfy requirements
for the CE Mark as those standards seem to be more stringent and
all-encompassing (including more stringent safety and hygiene
requirements).

We are investigating the possibilities of having essentially one design
meet both sets of requirements or at least as close as practical what with
the different voltage and frequency requirements involved, etc.

I'm sure that this isn't the first time that this has been thought of or
tried but I would like any comments anyone in the group might care to share
as to the success (or pitfalls experienced) that they have had in
attempting such.

Thanks for your responses.

Richard Pittenger
PMI Food Equipment Group
Troy, Ohio



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2

1999-06-18 Thread Patrick Lawler

On Fri, 18 Jun 1999 14:25:09 -0400, David George
george.da...@unisys.comwrote:
61000-3-2 is a horizontal standard and it applies to all products unless
specifically excluded by 61000-3-2.  The criteria is defined by CENELEC and
it is not necessarily specified by the individual product standards.  This
is why it is so important to watch basic and horizontal standards even
though they may not called out in the product standards. These
cross-the-board standards are sleepers and can effect manufacturer's through
the back door.  
I just sent a reply on this very issue - you must have been reading my mind.

Can you give examples of other horizontal standards?
What search keyword would be appropriate at the CENELEC/DGIII web sites?

Industry has decided to fight 61000-3-2 in the IEC and try to achieve
realistic requirements.  The US national committee has just released a
position paper on harmonics requirements.  If anyone needs a copy I can post
it on this net.
Yes, I'd like to see it.


Dave George
Unisys

-Original Message-
From: plaw...@west.net [mailto:plaw...@west.net]
Sent: Thursday, June 17, 1999 7:55 PM
To: emc-p...@majordomo.ieee.org
Subject: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2



I was asked the following question, and wasn't sure about the answer:

1) A manufacturer can claim his system complies with the Medical Device
Directive by testing to EN 60601-1-2:1993.

2) EN 60601-1-2:1993 does not have any requirements to test to IEC 1000-3-2.

3) Does that mean that the harmonic standard does not apply to this system
when
it becomes mandatory in 2001?


I realize the Second Edition of IEC60601-1-2 is just around the corner, and
that edition _does_ call out the harmonic test.  However, I've been told
that
it may not take effect until 2003.

--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2

1999-06-18 Thread Dave Clark

Yes but does it appear in the Official Journal for the Medical Device
Directive?  I don't believe it does but I am not sure.  If not then it is
not applicable.

Dave Clark

-Original Message-
From: rehel...@mmm.com [mailto:rehel...@mmm.com]
Sent: Friday, June 18, 1999 8:48 AM
To: plaw...@west.net
Cc: emc-p...@majordomo.ieee.org
Subject: Re: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2





It is my understanding that 61000-3-2 is a family standard (at least that
is what it says in the introduction of the copy that I have) and as such
includes all equipment equal to or less than 16 amps.

Bob Heller

===
===




plaw...@west.net (Patrick Lawler) on 06/17/99 06:55:21 PM

Please respond to plaw...@west.net (Patrick Lawler)


To:   emc-p...@majordomo.ieee.org
cc:(bcc: Robert E. Heller/US-Corporate/3M/US)
Subject:  Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2





I was asked the following question, and wasn't sure about the answer:

1) A manufacturer can claim his system complies with the Medical Device
Directive by testing to EN 60601-1-2:1993.

2) EN 60601-1-2:1993 does not have any requirements to test to IEC
1000-3-2.

3) Does that mean that the harmonic standard does not apply to this system
when
it becomes mandatory in 2001?


I realize the Second Edition of IEC60601-1-2 is just around the corner, and
that edition _does_ call out the harmonic test.  However, I've been told
that
it may not take effect until 2003.
--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).









-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2

1999-06-18 Thread George, David L

Pat:
61000-3-2 is a horizontal standard and it applies to all products unless
specifically excluded by 61000-3-2.  The criteria is defined by CENELEC and
it is not necessarily specified by the individual product standards.  This
is why it is so important to watch basic and horizontal standards even
though they may not called out in the product standards. These
cross-the-board standards are sleepers and can effect manufacturer's through
the back door.  

Industry has decided to fight 61000-3-2 in the IEC and try to achieve
realistic requirements.  The US national committee has just released a
position paper on harmonics requirements.  If anyone needs a copy I can post
it on this net.
Dave George
Unisys

-Original Message-
From: plaw...@west.net [mailto:plaw...@west.net]
Sent: Thursday, June 17, 1999 7:55 PM
To: emc-p...@majordomo.ieee.org
Subject: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2



I was asked the following question, and wasn't sure about the answer:

1) A manufacturer can claim his system complies with the Medical Device
Directive by testing to EN 60601-1-2:1993.

2) EN 60601-1-2:1993 does not have any requirements to test to IEC 1000-3-2.

3) Does that mean that the harmonic standard does not apply to this system
when
it becomes mandatory in 2001?


I realize the Second Edition of IEC60601-1-2 is just around the corner, and
that edition _does_ call out the harmonic test.  However, I've been told
that
it may not take effect until 2003.
--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Fw: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2

1999-06-18 Thread Patrick Lawler

On Fri, 18 Jun 1999 09:25:51 -0800, Jon Griver wrote:

  From: Jon Griver jgri...@itl.co.il
  Subject: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2
  Date: Fri, 18 Jun 1999 14:52:16 +0300 
  To: emc-p...@majordomo.ieee.org

 Patrick,
 
 1) EN 60601-1-2 just covers EMC, while the scope the Medical Devices 
 Directive includes safety, risk analysis, medical efficacy, biocompatibily, 
 software validation, etc.
My job responsibilities involve EMC, so I tend to have narrow focus.
Should the original sentence should have read:
A manufacturer can claim his system complies with the Medical Device
Directive by testing to EN 60601-1.
I think EN 60601-1 Amendment 1 includes the reference to EN 60601-1-2.

 Medical products are classified into Classes, 1, 11a, 11b and 111. Self 
 declaration can be used for most, but not all, Class 1 products (the least 
 critical). Even this this case, self declaration is based on a technical 
 file that includes much more than EN 60601-1-2.
 
 In all other cases, approval is via a Notified Body under the Medical 
 Devices Directive. Approval covers the manufacturer as well as the product, 
 as some level of ISO 9000 approval is required. The ISO 9000 audit is 
 carried out by the Notified Body itself. There is a complex relationship 
 between the Class of product and the level of ISO 9000 approval required.
 
 2) EN 60601-1-2 does have ESD requirements, but to IEC 801-2, which is older 
 than IEC 1000-3-2.
 
 3) EMC requirements for medical equipment are covered by the Medical Devices 
 Directive, not the EMC Directive. So if harmonics are not mentioned in EN 
 60601-1-2, then it is not required.
 
 Jon Griver
 ITL (Product Testing) Ltd.
 http://www.itl.co.il
 
 
 I was asked the following question, and wasn't sure about the answer:
 
 1) A manufacturer can claim his system complies with the Medical Device
 Directive by testing to EN 60601-1-2:1993.
 
 2) EN 60601-1-2:1993 does not have any requirements to test to IEC 1000-3-2.
 
 3) Does that mean that the harmonic standard does not apply to this system 
 when
 it becomes mandatory in 2001?
 
 
 I realize the Second Edition of IEC60601-1-2 is just around the corner, and
 that edition _does_ call out the harmonic test.  However, I've been told 
 that
 it may not take effect until 2003.
 --
 Patrick Lawler
 plaw...@west.net
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 
 

---End of Original Message-

--
Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA.  USA
619-505-2780
Date: 06/18/1999
Time: 09:25:53
Military  Avionics EMC Services Our Specialty
Also Environmental / Metrology / Reliability

--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Fw: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2

1999-06-18 Thread ed . price

Posted for Jon Griver:
 
 
 
 
 
 


  From: Jon Griver jgri...@itl.co.il
  Subject: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2
  Date: Fri, 18 Jun 1999 14:52:16 +0300 
  To: emc-p...@majordomo.ieee.org


 Patrick,
 
 1) EN 60601-1-2 just covers EMC, while the scope the Medical Devices 
 Directive includes safety, risk analysis, medical efficacy, biocompatibily, 
 software validation, etc.
 
 Medical products are classified into Classes, 1, 11a, 11b and 111. Self 
 declaration can be used for most, but not all, Class 1 products (the least 
 critical). Even this this case, self declaration is based on a technical file 
 that includes much more than EN 60601-1-2.
 
 In all other cases, approval is via a Notified Body under the Medical Devices 
 Directive. Approval covers the manufacturer as well as the product, as some 
 level of ISO 9000 approval is required. The ISO 9000 audit is carried out by 
 the Notified Body itself. There is a complex relationship between the Class 
 of product and the level of ISO 9000 approval required.
 
 2) EN 60601-1-2 does have ESD requirements, but to IEC 801-2, which is older 
 than IEC 1000-3-2.
 
 3) EMC requirements for medical equipment are covered by the Medical Devices 
 Directive, not the EMC Directive. So if harmonics are not mentioned in EN 
 60601-1-2, then it is not required.
 
 
 Jon Griver
 ITL (Product Testing) Ltd.
 http://www.itl.co.il
 
 
 
 
 
 I was asked the following question, and wasn't sure about the answer:
 
 1) A manufacturer can claim his system complies with the Medical Device
 Directive by testing to EN 60601-1-2:1993.
 
 2) EN 60601-1-2:1993 does not have any requirements to test to IEC 1000-3-2.
 
 3) Does that mean that the harmonic standard does not apply to this system 
 when
 it becomes mandatory in 2001?
 
 
 I realize the Second Edition of IEC60601-1-2 is just around the corner, and
 that edition _does_ call out the harmonic test.  However, I've been told that
 it may not take effect until 2003.
 --
 Patrick Lawler
 plaw...@west.net
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 
 
 
 
 

---End of Original Message-

--
Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA.  USA
619-505-2780
List-Post: emc-pstc@listserv.ieee.org
Date: 06/18/1999
Time: 09:25:53
Military  Avionics EMC Services Our Specialty
Also Environmental / Metrology / Reliability
--



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Fw: ITE Equipment installed in hospitals

1999-06-18 Thread ed . price

Posted for Jon Griver:
 
 
 
 
 
 


  From: Jon Griver jgri...@itl.co.il
  Subject: ITE Equipment installed in hospitals
  Date: Fri, 18 Jun 1999 14:30:42 +0300 
  To: emc-p...@majordomo.ieee.org


 
 Charles,
 
 There should not be any problem using ITE equipment in hospitals, when the 
 equipment is used by staff and nowhere near patients, and not connected to 
 any other medical equipment.
 
 If ITE equipment is connected to medical equipment, then its use is covered 
 by the standard IEC 601-1-1 (no, there are not too many 1's), for medical 
 SYSTEMS. Basically, if the equipment is located outside of the 'patient 
 vicinity' (see the standard for definition), then it only needs to comply 
 with IEC 950. If it is located in the 'patient vicinity', then it must comply 
 with IEC 601-1, for medical EQUIPMENT. In both cases, check IEC 601-1-1 to 
 see how the equipment is connected, particularly with regard to grounding.
 
 Regards,
 
 Jon Griver
 ITL (Product Testing) Ltd.
 http://www.itl.co.il
 
 
 
 Does anyone know if ITE equipment is required to
 meet any Medical requirements if installed in
 a hospital. (No patient connections!!)
 Thank you
 Charles Grasso
 StorageTek
 2270 Sth 88th Street
 Louisville CO 80027
 Tel: (303)673-2908
 Fax(303)661-7115
 
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 
 
 
 
 

---End of Original Message-

--
Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA.  USA
619-505-2780
List-Post: emc-pstc@listserv.ieee.org
Date: 06/18/1999
Time: 09:12:51
Military  Avionics EMC Services Our Specialty
Also Environmental / Metrology / Reliability
--



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2

1999-06-18 Thread Jon Griver

Patrick,

In my previous answer, please ignore item 2. I misread IEC 1000-3-2 for IEC 
1000-4-2.

Jon



Patrick,

1) EN 60601-1-2 just covers EMC, while the scope the Medical Devices Directive 
includes safety, risk analysis, medical efficacy, biocompatibily, software 
validation, etc.

Medical products are classified into Classes, 1, 11a, 11b and 111. Self 
declaration can be used for most, but not all, Class 1 products (the least 
critical). Even this this case, self declaration is based on a technical file 
that includes much more than EN 60601-1-2.

In all other cases, approval is via a Notified Body under the Medical Devices 
Directive. Approval covers the manufacturer as well as the product, as some 
level of ISO 9000 approval is required. The ISO 9000 audit is carried out by 
the Notified Body itself. There is a complex relationship between the Class of 
product and the level of ISO 9000 approval required.

2) EN 60601-1-2 does have ESD requirements, but to IEC 801-2, which is older 
than IEC 1000-3-2.

3) EMC requirements for medical equipment are covered by the Medical Devices 
Directive, not the EMC Directive. So if harmonics are not mentioned in EN 
60601-1-2, then it is not required.


Jon Griver
ITL (Product Testing) Ltd.
http://www.itl.co.il





I was asked the following question, and wasn't sure about the answer:

1) A manufacturer can claim his system complies with the Medical Device
Directive by testing to EN 60601-1-2:1993.

2) EN 60601-1-2:1993 does not have any requirements to test to IEC 1000-3-2.

3) Does that mean that the harmonic standard does not apply to this system 
when
it becomes mandatory in 2001?


I realize the Second Edition of IEC60601-1-2 is just around the corner, and
that edition _does_ call out the harmonic test.  However, I've been told that
it may not take effect until 2003.
--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).





-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: NEAR/ FAR FIELD CORRELATION ISSUES

1999-06-18 Thread jrbarnes

Even now, correlation between 3 meters and 10 meters
is not guaranteed.  And further, 3 meter to 10 meter
correlation is at least better (define better anyway
you wish) in the horizontal.  Vertically it's terrible
(define terrible anyway you wish). At least in my
experience.

Doug,
In our 3m chamber we use a Vertical Correction Factor (VCF) to account for the
worst-case difference between 3m and 10m vertical Radiated Emissions
measurements.  We usually have +/-1dB correlation, occasionally out to +/-2dB,
between measurements taken in the chamber at 3m including the VCF against
official measurements taken on our 10m Open Air Test Site (OATS).  We also
sometimes have some measurements taken at 10m that are much better than what we
predicted at 3m with VCF, meaning that we have over-engineered the product in
trying to ensure that we will pass the 10m tests...

The VCF is more pessimistic than the 10m CISPR limits by:
*  About 1dB at 30MHz, increasing to
*  About 7.5dB at 230MHz, dropping to
*  About 0dB at 450MHz and above.

As I understand it, the VCF was calculated by modelling:
*  A transmitting dipole antenna 1m above the groundplane with a receiving
antenna 3m away, at 1m to 1.7m above the groundplane (the
   range of available heights in our 3m chamber)
  VERSUS
*  A transmitting dipole antenna 1m above the groundplane with a receiving
antenna 10m away, at 1m to 4m above the groundplane (the
   range of heights required by CISPR testing).

  maximum received signal at 10m at f MHz 10^2
VCF (f MHz) = - * --
  maximum received signal at 3m at f MHz3^2

In the far field we expect the signal to drop off at 1/r^2.  But for
vertically-polarized signals the receiving antenna sees not only a direct-path
signal but one bounced off the groundplane.  These two can add to double the
voltage at the receiving antenna, or subtract to nearly zero, depending on the
phase difference between the two paths.   Running the antenna up and down helps
get away from the worst nulls, but
doesn't compensate for them completely.  Considering that the actual source of
the radiation may be at various heights or angles, not centered on the table,
and the signal may reflect off other metal pieces, the Vertical Correction
Factor is a huge help to us in trying to meet the Radiated Emissions limits.
  John Barnes   Advisory Engineer
  Lexmark International






dmckean%corp.auspex@interlock.lexmark.com on 06/17/99 04:39:53 PM

Please respond to dmckean%corp.auspex@interlock.lexmark.com

To:   emc-pstc%majordomo.ieee@interlock.lexmark.com
cc:(bcc: John Barnes/Lex/Lexmark)
Subject:  Re: NEAR/ FAR FIELD CORRELATION ISSUES





At 11:18 AM 6/17/99 +1000, you wrote:

Greetings and Salutations! I was wondering if this could be mailed out via
the epc-pstc channels.

I want to know if anyone is doing any work in near/ far field correlation
to commercial EMC standard limits area and possibly correspond with them
with a view to exchanging notes.

Hi Arun,

At a former company I spent a very large amount of time
trying to correlate near field probe measurements of
the surface currents and voltages of a product to far
field (10 meter) measurements.

In brief - it didn't happen.


And a product could be analyzed as being constructed of
a variety of antennas - slots, corner reflectors, tuned
cavity, tuned arrays, and either electric or magnetic
dipoles ... each reacting it's own way in the far field.

Now I'm not going to say it's impossible, but it seems to
me that one must assume something to begin with instead of
being able to blindly take a surface current measurement
or near field measurement of X and state confidently that
it WILL be Y in the far field under all circumstances.

That's ultimately what one would have to be able to do
without regard to the product.  After a few rounds with
a particular product, I've done this.  I'm sure everyone
at some point has done this.  But with NO prior history
of the product, I don't see how it's done.

Regards,  Doug McKean


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).









-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: NEAR/ FAR FIELD CORRELATION ISSUES

1999-06-18 Thread Matejic, Mirko

I remember many discussions on different CISPR Subcommittees on 
Swiss and Sweden's proposals and numerous papers presented on 
EMC Symposia in eighties and early nineties to replace OATS with 
absorbing clamp type measurements or to add clamp method as the 
alternative. All these proposals were rejected.

Keep in mind that correlation between two good, acceptable 'reference' 
OATS using the same measurement distance is not that great, could be 
as poor as 8 dB just due to a NSA deviation. How much more dB would 
be acceptable, that is the question.

I wish you and other EMC test method developers throughout the world 
good luck and success in developing acceptable alternative method to OATS. 

Mirko Matejic

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: ITE Equipment installed in hospitals

1999-06-18 Thread WOODS, RICHARD

There is no legal requirement, but the customer may ask for it.

--
From:  Grasso, Charles (Chaz) [SMTP:gra...@louisville.stortek.com]
Sent:  Thursday, June 17, 1999 9:58 PM
To:  'EMC Group'
Subject:  ITE Equipment installed in hospitals


Does anyone know if ITE equipment is required to
meet any Medical requirements if installed in
a hospital. (No patient connections!!)
Thank you
Charles Grasso
StorageTek
2270 Sth 88th Street
Louisville CO 80027
Tel: (303)673-2908
Fax(303)661-7115


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: NEAR/ FAR FIELD CORRELATION ISSUES

1999-06-18 Thread Arun Kaore

Hi, all

You are absolutely right about correlation issues at 3 m/10 m, which arise
predominantly from near field effects/ mutual coupling which is best
demarcated from the far field by the equation 2*D*exp 2/lambada. Depending
on the size of the object under test, the 3/10 m correlation, particularly
in the frequency range say  30-100MHz could be out by as much as 5-6 dB
(Remember the Mutual Impedance Correction Factors in Table G4 of CISPR 16-1,
they were supposed to fix Site Attenuation defects at 3 metres !!). A
baseline with some of the less complex artifacts would provide some
assistance.

Pauls Cook is right in saying that both E and H fields ought to be measured
and mutual coupling effects between loop  and object under test be
accounted.(ie. the effect of the measurement transducer on the EUT)

I have recently been quite puzzled by CISPR 11: 1992,  when they quoted that
below 30MHz the quasi-peak limits refer to the magnetic component of
electromagnetic radiation. Contrary to this the limits are specified in
dBuV/m instead of dBuA/m (Group 2 Class A, Table 5)!! Now, Because of the
frequencies, test object sizes and test distance lengths involved I cannot
invoke the golden 120*pi rule and make the conversion. But, is this what is
expected of a test house?

Also, ITE frequencies have shot past 500MHz, is an equivalent CISPR 22
frequency upgrade in the pipeline?


Arun Kaore
EMC Engineer

ADI Limited 
Systems Group
Test  Evaluation Centre
Forrester Road, St Marys, NSW 2760
P O Box: 315, St Marys NSW 1790

Tel: 61 2 9673 8375
Fax: 61 2 9673 8321
Email: kao...@sg.adi-limited.com.au

 -Original Message-
 From: Douglas McKean [SMTP:dmck...@corp.auspex.com]
 Sent: Friday, 18 June, 1999 6:40
 To:   emc-p...@majordomo.ieee.org
 Subject:  Re: NEAR/ FAR FIELD CORRELATION ISSUES
 
 
 At 11:18 AM 6/17/99 +1000, you wrote:
 
 
 Even now, correlation between 3 meters and 10 meters 
 is not guaranteed.  And further, 3 meter to 10 meter 
 correlation is at least better (define better anyway 
 you wish) in the horizontal.  Vertically it's terrible 
 (define terrible anyway you wish). At least in my 
 experience. 
 
 And a product could be analyzed as being constructed of 
 a variety of antennas - slots, corner reflectors, tuned 
 cavity, tuned arrays, and either electric or magnetic 
 dipoles ... each reacting it's own way in the far field. 
 
 Now I'm not going to say it's impossible, but it seems to 
 me that one must assume something to begin with instead of 
 being able to blindly take a surface current measurement 
 or near field measurement of X and state confidently that 
 it WILL be Y in the far field under all circumstances. 
 
 That's ultimately what one would have to be able to do 
 without regard to the product.  After a few rounds with 
 a particular product, I've done this.  I'm sure everyone 
 at some point has done this.  But with NO prior history 
 of the product, I don't see how it's done. 
 
 Regards,  Doug McKean 
 
 

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: NEAR/ FAR FIELD CORRELATION ISSUES

1999-06-18 Thread Paul Cook

I also wish you great luck.  Two major issues will confound you:

1) To convert a near field measurment to the far field, by
definition you need to know the wave impedance of the source.
We know that in the far field, the wave impedance will
have become 377 ohms, but in the near field it may thousands of
ohms from an electric field source, or it may be tens of ohms
from a magnetic field source.  With measurments from a loop
probe, you are measuring only the magnetic field component,
and you will have trouble doing the extrapolation to the far
field.  Once you have solved this problem, its closely related cousin
lurks for you in the darkness.

2)   The cousin: Antennas like dipoles and biconicals produce
a voltage that is related to the electromagnetic field in the vicinity
of the antenna.  That field in turn is generated by the EUT, and
the strength of that field is determined by two factors,
the current flowing in the radiating element, and the
geometry of the radiating element (its length/area).  A small loop probe
produces a voltage that is only proportional to the current
flowing in the radiating structure. Thus to calculate the farfield
effects of the current you need to be continually moving the
loop probe and doing line integrals and area integrals.

PS  If those two dont get you, I've always had a sneaking
suspicion that the process of making nearfield loop probe
measurements can affect the emissions coming from
an EUT, but I've never actually tried to prove it.

Anyways, good luck is in order, but I won't be holding
my breath.

Paul Cook
NARTE Certified EMC Engineer
Alpha EMC Inc
8540 West River Rd
Minneapolis, Minnestoa 55444
Tel # (612)-561-2844
Fax #(612)-561-3400
E-mailpaulc...@skypoint.com
Specialty  -  EMC Consulting







-Original Message-
From: Arun Kaore kao...@sg.adi-limited.com.au
To: 'emc-p...@majordomo.ieee.org' emc-p...@majordomo.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: Wednesday, June 16, 1999 11:58 PM
Subject: NEAR/ FAR FIELD CORRELATION ISSUES




Greetings and Salutations! I was wondering if this could be mailed out via
the epc-pstc channels.

I want to know if anyone is doing any work in near/ far field correlation
to commercial EMC standard limits area and possibly correspond with them
with a view to exchanging notes.

Brief Follows:

Brief:

Application of Near Field and possibly Surface probe techniques in
Evaluating Emissions from source equipment and correlating/quantifying this
data to an OATS, LISN, Absorbing Clamp etc based measurement..

Details:

We assume that the current EMC compliance regime around the world has
quantified limits of compliance to which if every source equipment adheres
to, then it has a reasonable chance of performing as intended in a real
life
situation, noting that the immunity threshold test levels are much more
stringent than EM emission limits.

Current EMC measurements are very cumbersome, require large expense in
setting up and maintaining (calibrating) OATS, LISNS, Absorbing Clamps,
Ferrite tiled lined semi- anechoics etc. Despite this expense, the
measurement uncertainities are still of the order of 6 to 10dB (inherent).

Every newly released EMC standard by IEC CISPR or CENELEC has potentially
new transducers and new headaches from point of view of sourcing and
maintenance, calibration.  EMC today is where Safety was 10 years ago. I am
of the opinion that EMC testing should be simplified and reasonably
accessible to all end users.

Continued progress and urban development has led to increasing levels of
broad and narrowband noise to the extent that ambient profiles sometimes
swamp out the limits; this has led to most test houses in the EU to opt for
GTEMS or semi-anechoics (referred to as alternative all weather test
sites) at considerable expense.

Current techniques such as emission E Field prescanning in shielded rooms
prior to OATS based testing with biconilog antennae have the drawbacks of
peaking the emissions and reflections/standing waves.

Hence:

I propose to develop near or surface probe H (inverse of E)  field
techniques which actually senses the emission profiles and correlate them
to
an Absorber clamp, or OATS or LISN (Common mode fix) or whatever. Cables,
panels, slots etc could be sniffed with a Loop and if it is possible to
correlate this near or induction field data to compliance limits then it
becomes very easy for individuals and organisations to do precertification.
Transducers could be simple and light weight, rugged, and physically
defined
so that minimal calibration is required. EMI receivers will still need
calibration.

With these techniques, you measure actually what comes off the source and
not the peak value of the bounced and direct rays within say the Fresnel
ellipse, or move the Absorbing clamp up and down the rail and peak the
field.

Conducted emissions could be scanned by common mode techniques and radiated
emissions by  surface or near scans.

Currently, these techniques are 

ITE Equipment installed in hospitals

1999-06-18 Thread Grasso, Charles (Chaz)

Does anyone know if ITE equipment is required to
meet any Medical requirements if installed in
a hospital. (No patient connections!!)
Thank you
Charles Grasso
StorageTek
2270 Sth 88th Street
Louisville CO 80027
Tel: (303)673-2908
Fax(303)661-7115


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2

1999-06-18 Thread Patrick Lawler

I was asked the following question, and wasn't sure about the answer:

1) A manufacturer can claim his system complies with the Medical Device
Directive by testing to EN 60601-1-2:1993.

2) EN 60601-1-2:1993 does not have any requirements to test to IEC 1000-3-2.

3) Does that mean that the harmonic standard does not apply to this system when
it becomes mandatory in 2001?


I realize the Second Edition of IEC60601-1-2 is just around the corner, and
that edition _does_ call out the harmonic test.  However, I've been told that
it may not take effect until 2003.
--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2

1999-06-18 Thread reheller



It is my understanding that 61000-3-2 is a family standard (at least that
is what it says in the introduction of the copy that I have) and as such
includes all equipment equal to or less than 16 amps.

Bob Heller

===
===




plaw...@west.net (Patrick Lawler) on 06/17/99 06:55:21 PM

Please respond to plaw...@west.net (Patrick Lawler)


To:   emc-p...@majordomo.ieee.org
cc:(bcc: Robert E. Heller/US-Corporate/3M/US)
Subject:  Medical Device Directive, IEC 601-1-2, and IEC 1000-3-2





I was asked the following question, and wasn't sure about the answer:

1) A manufacturer can claim his system complies with the Medical Device
Directive by testing to EN 60601-1-2:1993.

2) EN 60601-1-2:1993 does not have any requirements to test to IEC
1000-3-2.

3) Does that mean that the harmonic standard does not apply to this system
when
it becomes mandatory in 2001?


I realize the Second Edition of IEC60601-1-2 is just around the corner, and
that edition _does_ call out the harmonic test.  However, I've been told
that
it may not take effect until 2003.
--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).









-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Near/ Far Field Correlation Issues

1999-06-18 Thread Javor, Ken

With regard to the CISPR 11 limits below 30 MHz.  A magnetic loop
measurement is made because the loop measurement is more accurate than
an E-field measurement.  The practice of converting the measurement to a
far field equivalent electric field intenisty is purely an algebraic
conversion.  

 -Original Message-
 From: Arun Kaore [SMTP:kao...@sg.adi-limited.com.au]
 Sent: Thursday, June 17, 1999 11:42 PM
 To:   'emc-p...@majordomo.ieee.org'
 Subject:  Re: Near/ Far Field Correlation Issues
 
 
 Hi, all
 
 You are absolutely right about correlation issues at 3 m/10 m, which
 arise
 predominantly from near field effects/ mutual coupling which is best
 demarcated from the far field by the equation 2*D*exp 2/lambada.
 Depending
 on the size of the object under test, the 3/10 m correlation,
 particularly
 in the frequency range say  30-100MHz could be out by as much as 5-6
 dB
 (Remember the Mutual Impedance Correction Factors in Table G4 of CISPR
 16-1,
 they were supposed to fix Site Attenuation defects at 3 metres !!). A
 baseline with some of the less complex artifacts would provide some
 assistance.
 
 Pauls Cook is right in saying that both E and H fields ought to be
 measured
 and mutual coupling effects between loop  and object under test be
 accounted.(ie. the effect of the measurement transducer on the EUT)
 
 I have recently been quite puzzled by CISPR 11: 1992,  when they
 quoted that
 below 30MHz the quasi-peak limits refer to the magnetic component of
 electromagnetic radiation. Contrary to this the limits are specified
 in
 dBuV/m instead of dBuA/m (Group 2 Class A, Table 5)!! Now, Because of
 the
 frequencies, test object sizes and test distance lengths involved I
 cannot
 invoke the golden 120*pi rule and make the conversion. But, is this
 what is
 expected of a test house?
 
 Also, ITE frequencies have shot past 500MHz, is an equivalent CISPR 22
 frequency upgrade in the pipeline?
 
 
 Arun Kaore
 EMC Engineer
 
 ADI Limited 
 Systems Group
 Test  Evaluation Centre
 Forrester Road, St Marys, NSW 2760
 P O Box: 315, St Marys NSW 1790
 
 Tel: 61 2 9673 8375
 Fax: 61 2 9673 8321
 Email: kao...@sg.adi-limited.com.au
 
  -Original Message-
  From:   Douglas McKean [SMTP:dmck...@corp.auspex.com]
  Sent:   Friday, 18 June, 1999 6:40
  To: emc-p...@majordomo.ieee.org
  Subject:Re: NEAR/ FAR FIELD CORRELATION ISSUES
  
  
  At 11:18 AM 6/17/99 +1000, you wrote:
  
  
  Even now, correlation between 3 meters and 10 meters 
  is not guaranteed.  And further, 3 meter to 10 meter 
  correlation is at least better (define better anyway 
  you wish) in the horizontal.  Vertically it's terrible 
  (define terrible anyway you wish). At least in my 
  experience. 
  
  And a product could be analyzed as being constructed of 
  a variety of antennas - slots, corner reflectors, tuned 
  cavity, tuned arrays, and either electric or magnetic 
  dipoles ... each reacting it's own way in the far field. 
  
  Now I'm not going to say it's impossible, but it seems to 
  me that one must assume something to begin with instead of 
  being able to blindly take a surface current measurement 
  or near field measurement of X and state confidently that 
  it WILL be Y in the far field under all circumstances. 
  
  That's ultimately what one would have to be able to do 
  without regard to the product.  After a few rounds with 
  a particular product, I've done this.  I'm sure everyone 
  at some point has done this.  But with NO prior history 
  of the product, I don't see how it's done. 
  
  Regards,  Doug McKean 
  
  
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).