RE: Grounding

2003-11-14 Thread Bill Flanigan
Ned, See EN61010-1:20001, 6.5.1.1.d... Movable conductive connections, for example, hinges, slides, etc., shall not be the sole PROTECTIVE BONDING path unless they are specifically designed for electrical inter-connection and meet the requirements of blah...blahhh There are similar provisions,

IEC and EN standard relationships

2003-11-14 Thread Ablewisp - Compliance Engineers
Dear group A client located outside the EU has a large number of IEC standards. They would like to determine the differences between their IEC standards and the equivalent EN standards. I was told by BSI that if the BSEN60xxx number is identical to the IEC60xxx number, the standards are the

System test PCs - Are we cops?

2003-11-14 Thread Cortland Richmond
John Woodgate wrote: Telling us here won't have any effect. If you are concerned about violations, tell the regulatory authority. This is worth some discussion, I think. Most of the time, EMC engineers are not cops. Among other things, we want to be sure our OWN employers are regulation

Experiance with the PMM-9000 emi receiver?

2003-11-14 Thread Garnier, David S (MED)
Hello, Anybody have any experiance with this box that they would be willing to share? This is a 9 Khz to 1.2 Ghz emi receiver that is fully CISPR 16-1 compliant. Thanks, dave garnier David Garnier e GE Medical Systems

Re: IEC and EN standard relationships

2003-11-14 Thread richhug...@aol.com
John, There are not always technical deviations between IEC and EN standards, for instances there are no differences in the body of the standard between the latest versions of IEC 60825-1 and EN 60825-1. Of course, CENELEC standards have a Date of Withdrawal of conflicting standards which IEC

RE: 10/100 Ethernet transformers meeting IEC60950 Basic insulation

2003-11-14 Thread Peter L. Tarver
Thank you for the update, John. I didn't plan to look it up; it's kind of you to do so for us. The document contains a number of other items, not related to reliance on enamel magnet wire as insulation. Could've bounced on any or all accounts. Regards, Peter L. Tarver, PE ptar...@ieee.org

Re: IEC and EN standard relationships

2003-11-14 Thread John Woodgate
I read in !emc-pstc that Ralph McDiarmid ralph.mcdiar...@xantrex.com wrote (in 67C475A5ECE7D4118AEC0002B325CAB60581A444@BCMAIL1) about 'IEC and EN standard relationships' on Fri, 14 Nov 2003: What would be an example of a Common Deviation? Common Modification. An example from BS EN

Re: IEC and EN standard relationships

2003-11-14 Thread John Woodgate
I read in !emc-pstc that Ablewisp - Compliance Engineers s...@ablewisp.com wrote (in ncbbihmocpcglbmhbpkpmeeedeaa...@ablewisp.co m) about 'IEC and EN standard relationships' on Fri, 14 Nov 2003: A client located outside the EU has a large number of IEC standards. They would like to determine

RE: IEC and EN standard relationships

2003-11-14 Thread Ralph McDiarmid
What would be an example of a Common Deviation? thanks, Ralph McDiarmid, AScT Compliance Engineering Group Xantrex Technology Inc. From: John Allen [mailto:ja014d7...@blueyonder.co.uk] Sent: November 14, 2003 12:13 PM To: Ablewisp - Compliance Engineers; Emc-Pstc Subject: Re: IEC and EN

RE: Machinery Directive acoustic requirements

2003-11-14 Thread Nick Williams
At 9:03 -0800 14/11/03, Peter L. Tarver wrote: Thanks to the responders to my query. SNIP I know I must purchase some standards, but I'd like to minimize the financial hit. I'd appreciate opinions regarding these three standards in particular: EN ISO 4871:1996 [Acoustics - Declaration and

Re: 10/100 Ethernet transformers meeting IEC60950 Basic insulation

2003-11-14 Thread John Woodgate
I read in !emc-pstc that Peter L. Tarver peter.tar...@sanmina-sci.com wrote (in nebbkemlgllmjofmopleaeilenaa.peter.tar...@sanmina-sci.com) about '10/100 Ethernet transformers meeting IEC60950 Basic insulation' on Fri, 14 Nov 2003: FWIW, there is a proposal in TC108 (108/69/CD) to permit limited

RE: Machinery Directive acoustic requirements

2003-11-14 Thread Peter L. Tarver
I know I must purchase some standards, but I'd like to minimize the financial hit. I'd appreciate opinions regarding these three standards in particular: That's one...two...thr...FOUR standards...yeah four... (whudduh week) EN ISO 4871:1996 EN ISO 9614-1:1995 EN ISO

Re: Does anyone system test PCs anymore? - Q on new procedures

2003-11-14 Thread John Woodgate
I read in !emc-pstc that Grasso, Charles charles.gra...@echostar.com wrote (in DEDA59C30D344E4182D1A4DAB86C5B78082868C2@riv- exch2.echostar.com) about 'Does anyone system test PCs anymore? - Q on new procedures' on Fri, 14 Nov 2003: If I understand the new methodology then I (a mnaufacturer)

Re: Machinery Directive acoustic requirements

2003-11-14 Thread John Woodgate
I read in !emc-pstc that Peter L. Tarver peter.tar...@sanmina-sci.com wrote (in nebbkemlgllmjofmopleceimenaa.peter.tar...@sanmina-sci.com) about 'Machinery Directive acoustic requirements' on Fri, 14 Nov 2003: There are 23 standards containing acoustic requirements called out in the 14AUG2003

Re: IEC and EN standard relationships

2003-11-14 Thread richhug...@aol.com
Stuart, Technically, BS EN 60xxx is the same as NF 60xxx with the exception that the BS version is in English and the NF version is in French. All language variants of an EN contain all national differences and Common Modifications. If you look at the listing of standards in the OJEC you will

Re: IEC and EN standard relationships

2003-11-14 Thread John Allen
Stuart As many people in this group can tell you, when CENELEC adopts an IEC as an EN (almost always under the same numeric reference) it declares any Common deviations in an annex at the back of the EN version - hence the need to (in theory, at least) buy the EN! However, any deviations in

RE: Grounding

2003-11-14 Thread Gary McInturff
John, You are correct, but you have just presented the conundrum of the thread. Reliably grounded can be determined through test - 25 or 30 amps for a minute. A new hinge will likely pass that test. A used one may likely fail because of the corrosion and wear discussed by others.

RE: 10/100 Ethernet transformers meeting IEC60950 Basic insulation

2003-11-14 Thread douglas_beckw...@mitel.com
There is such beast made by pca electronics (www.pca.com). The part number is EPF819 SL. I have the datasheet if anyone wants it. Doug

RE: Machinery Directive acoustic requirements

2003-11-14 Thread Peter L. Tarver
Thanks to the responders to my query. There are 23 standards containing acoustic requirements called out in the 14AUG2003 list of harmonized standards. Some of these standards clearly don't apply in this particular instance (those related to ducting or workstations that would apply to the final

RE: Grounding

2003-11-14 Thread Crabb, John
2.6.1 of IEC 60950-1 refers to parts of equipment shall be reliably connected to the main protective earthing terminal.A hinge would certainly not be regarded as a reliable connection. As far as your door is concerned, is there any single insulated hazardous voltage wiring likely to contact

RE: Grounding

2003-11-14 Thread Gary McInturff
Hinges will likely meet the 0.1 ohm criteria when new but fail over time. They typically don't have enough contact pressure to insure any type of EMC grounding/bonding and could potentially be a bigger problem. Gary From: drcuthb...@micron.com [mailto:drcuthb...@micron.com] Sent: Friday,

RE: Grounding

2003-11-14 Thread Roman, Dan
Ned, You are right, I could not find anything in recent ITE standards specifically stating that hinges are not allowed. Older standards like UL1459 did specifically state that bearings and hinges can not be used. I believe however that the onus would be on the manufacturer to prove that the

RE: Grounding

2003-11-14 Thread Ned Devine
Scott, I agree, but why is it not in the standard? Thanks to Bill and Dave, I now know it is in IEC/EN 61010-1 (See IEC/EN61010-1:20001, 6.5.1.1.d.). So, why not in IEC 60950-1 and IEC 60601-1? Ned From: Scott Douglas [mailto:sdoug...@ptcnh.net] Sent: Friday, November 14, 2003 11:43 AM

Re: Grounding

2003-11-14 Thread Scott Douglas
Ned, I had this discussion with a TUV engineer way back in time. It is not in the UL or IEC standards specifically AFAIK. What the TUV guy asked me to do was consider the life of the product. The door hinge may have good (low) resistance today, but what will it be like in a few years? Hinges

RE: Grounding

2003-11-14 Thread drcuthb...@micron.com
Ned, I know this isn't the standard you are using but I happen to have been using it lately and quickly found a similar situation. EN61010-1:2001, 6.5.1.1 Integrity of protective bonding: d) Movable conductive connections, for example, hinges, slides, etc., shall not the sole PROTECTIVE BONDING

RE: Machinery Directive acoustic requirements

2003-11-14 Thread Gary McInturff
On the same, bigger than a breadbox, piece of equipment I ran a test in both a reverberating chamber and sweeping the microphone around the equipment - as described in the ETSI 300-019 (I think) tests, and those described in the NEBS suite using a hand held sound meter. The

Grounding

2003-11-14 Thread Ned Devine
Hi, I need some help. I told someone that you can not depend on mechanical contact only (i.e. in this case a door hinge) for protective earth. Even if it passes the test, it would still not be acceptable because it does not meet the construction requirements. He then asked me to show him were

RE: Does anyone system test PCs anymore? - Q on new procedures

2003-11-14 Thread Grasso, Charles
Dear Wan Juang Foo, That's a very good question! AFAIK FCC + FCC does NOT = FCC and systems integrators are bound to test. However, I am not sure of this anymore as there has been changes to the FCC Class B certification procedures (for PCs). Best Regards Charles Grasso Senior Compliance

RE: Does anyone system test PCs anymore? - Q on new procedures

2003-11-14 Thread Grasso, Charles
John et al. Thanks for your observations. If I understand the new methodology then I (a mnaufacturer) can market as a SYSTEM two pieces of hardware that are independently certified without a retest? Don't I become a systems integrator? In the old days the systems integrator was responsible for

10/100 Ethernet transformers meeting IEC60950 Basic insulation

2003-11-14 Thread Charles Blackham
All I wish to provide a safety barrier between the User connecting to the 10/100 RJ45 Ethernet port and the TNV3 circuitry within my unit. Can anyone recommend a suitable Ethernet transformer that is a UL recognised component and meets the Creepage and clearance distances for Basic insulation?

Re: Re: Immunity testing mitigations

2003-11-14 Thread T.Sato
On Fri, 14 Nov 2003 10:38:01 +0100 (CET), r...@rpgarner.freeserve.co.uk wrote: Be warned, something like this was tried by a UK manufacturer. They failed the tests, then persauded a Competent body to sign off a TCF stating that the failed tests were not applicable or were unpassable by

RE: Security and Alarm Systems

2003-11-14 Thread richwo...@tycoint.com
I have the version dated 1996 and it does explain which directives apply to various types of alarms. The report is intended as a guide for the various standards committees. Also check out ETSI TR 102070-1 -2 which provides guidelines for the integration of radio devices with other devices. You

RE: Machinery Directive acoustic requirements

2003-11-14 Thread Gordon,Ian
John et al Yes - ISO 37xx not IEC. Sorry for the confusion. Ian Gordon _ This e-mail has been scanned for viruses by MCI's Internet Managed Scanning Services - powered by MessageLabs. For further information visit

Re: Machinery Directive acoustic requirements

2003-11-14 Thread John Woodgate
I read in !emc-pstc that Gordon,Ian ian.gor...@bocedwards.com wrote (in E1BA0362B28ED211A1E80008C71EA3060206FE62@z- 160-100-30-252.est.ibm.com) about 'Machinery Directive acoustic requirements' on Fri, 14 Nov 2003: The tests required therein will undoubtedly be based on the IEC 37xx series and

Re: Machinery Directive acoustic requirements

2003-11-14 Thread Nick Williams
Peter, It's not quite true to say 'this is a nightmare' but it's certainly a pain to deal with! Over a period of years, I have ended up buying most of the noise standards just so that I can answer this question, but frankly I'm still not much the wiser. Our experience is that you can use the

RE: Security and Alarm Systems

2003-11-14 Thread Crabb, John
A limited amount of information may be found in CENELEC Report R079-001:1998 Guide to achieving compliance with EC directives for alarm systems I don't have a copy, however. Regards, John Crabb, (Product Safety) , NCR Financial Solutions Group Ltd., Discovery Centre, 3 Fulton Road,

Re: Re: Immunity testing mitigations

2003-11-14 Thread r...@rpgarner.freeserve.co.uk
Tom, Be warned, something like this was tried by a UK manufacturer. They failed the tests, then persauded a Competent body to sign off a TCF stating that the failed tests were not applicable or were unpassable by their equipment. They then CE marked and placed on the market. Within their

RE: Machinery Directive acoustic requirements

2003-11-14 Thread Gordon,Ian
Peter You need to see if there is a relevant product standard which will detail the required uncertainty of measurement e.g. do you need a fully anechoic room etc. The tests required therein will undoubtedly be based on the IEC 37xx series and IEC 3744 in particular. My understanding is as

Re: Does anyone system test PCs anymore? - Q on new procedures

2003-11-14 Thread John Woodgate
I read in !emc-pstc that Cortland Richmond 72146@compuserve.com wrote (in 200311131630_mc3-1-5a13-7...@compuserve.com) about 'Does anyone system test PCs anymore? - Q on new procedures' on Thu, 13 Nov 2003: Can a monitor purchased from an OEM have a company label slapped on it and sold

Re: opinions, please

2003-11-14 Thread John Woodgate
I read in !emc-pstc that Cortland Richmond 72146@compuserve.com wrote (in 200311131630_mc3-1-5a13-7...@compuserve.com) about 'opinions, please' on Thu, 13 Nov 2003: I will note that the marketing rationale for placing a CE mark on components which may be installed by the public could well

RE: Security and Alarm Systems

2003-11-14 Thread Henry Rutjes
Hi Peter, The CEI Standards you mention are Italian National security standards. In Europe most individual member states do have their own national requirements (standards). There are a few harmonized published standards in Europe i.e. the EN 50131-1 (general requirements on alarm equipment) but