RE: surge Z?

2003-03-20 Thread Mike Hopkins
The surge generator specification is 2 ohms source impedance for testing in normal mode (line to line) and 12 ohms for testing in common mode (surges line to ground). Mike Hopkins Thermo Electron KeyTek From: drcuthbert [mailto:drcuthb...@micron.com] Sent: Wednesday, March 19, 2003 3:36 PM

RE: RADIATED IMMUNITY REQUIREMENTS FOR EN61326

2003-03-03 Thread Mike Hopkins
be very close to other sources or radiation from, say, 5W walkies used by security personnel -- how much of a field can you get a 150MHz a foot from a 5W transmitter?? Mike Hopkins Thermo KeyTek From: John Woodgate [mailto:j...@jmwa.demon.co.uk] Sent: Monday, March 03, 2003 12:41 PM To: emc-p

RE: RADIATED IMMUNITY REQUIREMENTS FOR EN61326

2003-03-03 Thread Mike Hopkins
I believe the other bands are television broadcast M. Hopkins Thermo KeyTek From: Ken Javor [mailto:ken.ja...@emccompliance.com] Sent: Monday, March 03, 2003 11:03 AM To: Gordon,Ian; 'IEEE EMC-PSTC GROUP' Subject: Re: RADIATED IMMUNITY REQUIREMENTS FOR EN61326 Hazarding a guess. I am

RE: ESD Problem

2003-05-27 Thread Mike Hopkins
So is mine (hand up, that is) Best Regards, Michael Hopkins Manager, EMC Technologies Thermo Electron Control Technology Division EMC ESD Simulation Systems One Lowell Research Center Lowell, MA 01852 Tel: +1 978 275 0800 ext. 334 Fax: +1 978 275 0850 michael.hopk...@thermo.com One

RE: question on IEEE standards activity addressing immunity stand ards

2003-05-15 Thread Mike Hopkins
The first one to come to mind is ANSI C63.16 for ESD -- finished a document recently for ESD testing of products -- should be published soon Also, there is the IEEE SPD -- Surge Protective Devices -- group under the Power engineering society that just published ANSI/IEEE C62.41.1, C62.41.2

RE: Design of low cost ESD gun.

2003-05-09 Thread Mike Hopkins
Since you can buy a compliant gun for a few thousand dollars (used, demos, etc), why would you want to spend at least that much in time and materials to get something close?? Mike Hopkins Thermo Electron michael.hopk...@thermo.com From: LEUNG YAT WAH DEREK [mailto:ywle...@vtc.edu.hk] Sent

RE: ESD gun verification

2003-05-01 Thread Mike Hopkins
Because you're dealing with a relatively high frequency event, you really do need a good target and measurement system to verify that the waveform is in compliance That said, there are a number of ways to verify that the gun is working and is probably okay without going to any extremes. One

RE: ESD - not applicable ?

2003-06-24 Thread Mike Hopkins
...@nettest.com] Sent: Tuesday, June 24, 2003 11:16 AM To: Mike Hopkins; don_borow...@selinc.com; emc-p...@majordomo.ieee.org Subject: RE: ESD - not applicable ? Mike, I'm still not sold. I understand the specific exemptions for circuit cards, battery compartments and the like; but I can't follow

RE: ESD - not applicable ?

2003-06-24 Thread Mike Hopkins
You always need to apply two heads --- the engineering head says,Good engineering practice says you should test for ESD, but the compliance head only needs to meet the requirement of the standard, which clearly exempts points and ports NOT accessible by an OPERATOR. Points and ports accessible

RE: Automotive ESD

2003-06-09 Thread Mike Hopkins
Lowell, MA 01852 Tel: +1 978 275 0800 ext. 334 Fax: +1 978 275 0850 michael.hopk...@thermo.com One Thermo, committed to integrity, intensity, innovation involvement From: Locke, Darrell [mailto:dlo...@advanced-input.com] Sent: Monday, June 09, 2003 4:37 PM To: Mike Hopkins Cc: EMC-PSTC List

RE: Electrical Fast Transient (EFT) and the Real World

2003-06-04 Thread Mike Hopkins
Actually, the EFT test pre-dates the IEEE reference. IEEE included a reference to IEC 801-4 in the earlier IEEE 587 document, which has now become ANSI/IEEE C62.41 (now reissued as a 2002 document as a Trilogy: C62.41, C62.42, and C62.45). In the 70's, EFT tests were being conducted in Europe

RE: FCC's inquiry for broadband over the powerlines (BPL)

2003-07-18 Thread Mike Hopkins
All I know is that it seems to be a major problem in Europe, with lot's of HF spectrum uses seeing high levels of interference to services. Amateur Radio organizations world-wide are fighting it (including ARRL in the US). I heard a talk regarding this problem in Germany at the last IEEE EMC

RE: voltage dips

2003-07-22 Thread Mike Hopkins
There is a new document in the works, IEC 61000-4-34, for dip interrupt testing of products drawing greater than 16A. It is currently a CD (Committee Draft). TC77A WG6, who is responsible for this document, meets in Spain in September, after which a CDV (Committee Draft for Vote) is possible. It

RE: antennas

2003-08-29 Thread Mike Hopkins
michael.hopk...@thermo.com One Thermo, committed to integrity, intensity, innovation involvement From: John Woodgate [mailto:j...@jmwa.demon.co.uk] Sent: Friday, August 29, 2003 2:49 PM To: emc-p...@majordomo.ieee.org Subject: Re: antennas I read in !emc-pstc that Mike Hopkins michael.hopk

RE: Lightning Surge Characterization/Standards

2003-08-05 Thread Mike Hopkins
For lightning in the power grid, see ANSI/IEEE C62.41.1 - 2002 Guide on the Surge Environment in Low-Voltage (1000V and Less) AC Power Circuits ANSI/IEEE C62.41.2 - 2002 Recommended Practice on Characterization of Surges in Low-Voltage (1000V and Less) AC Power Circuits ANSI/IEEE C62.45

RE: SURGE testing, disturb. meas.

2003-09-21 Thread Mike Hopkins
...@msn.com] Sent: Friday, September 19, 2003 7:13 PM To: Mike Hopkins; Konrad Stefanski; emc-p...@ieee.org Subject: Re: SURGE testing, disturb. meas. So is an ethernet line considered disabled when disconnected since it will drop the link (although it keeps trying to establish link and resume the idle

RE: SURGE testing, disturb. meas.

2003-09-19 Thread Mike Hopkins
There are couplers available from a number of manufacturers; however, none work at data rates much above 100kHz. For that reason, the current draft of 61000-4-5 revision 2 (not yet circulated) inlcudes the following -- keep in mind, it is an EARLY draft, but it will appear in a CD by the end of

RE: SURGE testing, disturb. meas.

2003-09-19 Thread Mike Hopkins
Prices depend on the design: Some contain coupling and backfilter elements for 4 lines plus circuitry to allow coupling using either capacitors (still the preferred method in 61000-4-5) or arrestors. They also allow the addition of clamps of various levels to reduce or eliminate surges back to

RE: Effective length of half wave dipole

2003-10-29 Thread Mike Hopkins
I think the length of a 1/2 wave dipole in feet is basically 468/f(MHz) where the ratio of the length to diameter is very large (wire antennas in the HF region, for example). Making the diameter of the elements larger does two things: it reduces the overall length of the antenna and increases the

RE: ESD for a dev lab work place

2003-10-16 Thread Mike Hopkins
Not aware of any standards for ESD related to development; however, since new products will likely need to meet existing international and national standards, that would be the place to start In my experiance, engineering labs tend to use the standards (IEC 61000-4-2 being the most

RE: IEC and EN standard relationships

2003-11-25 Thread Mike Hopkins
present format for decades and is unlikely to change any time soon. Regards, Peter L. Tarver, PE ptar...@ieee.org From: Mike Hopkins Sent: Tuesday, November 18, 2003 12:42 PM Info from outside the EU: In the US, ANSI and others have been told that any new standards written must be harmonized

RE: Safety Critical etc - the future

2001-11-05 Thread Mike Hopkins
are industry -- Siemens, Philips, Nokia, IBM, Sun, HP, Schneider, Tele Danmark, Allen Bradley, Tokin, etc... Some of these experts run labs within their companies, but they are not NRTL's or Competent Bodies. This composition is similar in the other WG's I'm familiar with, as well as the US TAG's... Mike

RE: Surge (1000-4-5) voltages impedances

2001-10-10 Thread Mike Hopkins
, the tests are performed between lines, or line to ground, in which case the impedances will be higher -- up to several hundred ohms Hope that helps... Mike Hopkins Thermo KeyTek -Original Message- From: Yow, Steve (IndSys, GEFanuc, NA) [mailto:steve@gefanuc.com] Sent: Wednesday

RE: ISO TR 10605 test setup (ESD)

2001-06-19 Thread Mike Hopkins
measured significant potentials between separate grounds in the same building.. Mike Hopkins KeyTek -Original Message- From: Chris Maxwell [mailto:chris.maxw...@nettest.com] Sent: Tuesday, June 19, 2001 8:46 AM To: 'Chris Chileshe'; emc-p...@majordomo.ieee.org Subject: RE: ISO TR 10605

RE: Typing Shortcuts

2001-06-14 Thread Mike Hopkins
How about By The Way Mike Hopkins KeyTek -Original Message- From: rehel...@mmm.com [mailto:rehel...@mmm.com] Sent: Wednesday, June 13, 2001 12:18 PM To: emc-p...@majordomo.ieee.org Subject: Typing Shortcuts Over time I have come across many typing shortcuts using

RE: ESD generators max Contact discharge level

2001-06-14 Thread Mike Hopkins
Another point is that at lower voltages, the real rise times (the dv/dt) can be quite a bit higher --- especially below about 5kV Mike Hopkins KeyTek -Original Message- From: Cortland Richmond [mailto:72146@compuserve.com] Sent: Wednesday, April 25, 2001 2:33 AM To: jrbar

RE: consumer electronics used on board aircraft

2001-01-25 Thread Mike Hopkins
That might be right, but if the FCC didn't ban the use of cell phones in airplanes, I'd bet the airlines or FAA would. Mike Hopkins -Original Message- From: rbus...@es.com [mailto:rbus...@es.com] Sent: Thursday, January 25, 2001 12:26 PM To: emc-p...@majordomo.ieee.org Subject: RE

RE: consumer electronics used on board aircraft

2001-01-24 Thread Mike Hopkins
controls might cause the airplane to do something erratic, but that sort of thing should be recoverable as long as someone in the cockpit is paying attention. Enough of that -- need to get back to my real job Mike Hopkins KeyTek -Original Message- From: Colgan, Chris

RE: EN 61000-4-8

2001-01-16 Thread Mike Hopkins
Blvd. Torrance, CA 90505 Tel: 310 891 0635 Fax: 310 891 0644 Hope this helps, Mike Hopkins KeyTek -Original Message- From: wo...@sensormatic.com [mailto:wo...@sensormatic.com] Sent: Tuesday, January 16, 2001 11:42 AM To: emc-p...@majordomo.ieee.org Subject: EN 61000-4-8 We

RE: EN 61000-6-2 Table 2.3 inticates signal ports = 30 M +/- 1k v?

2001-01-05 Thread Mike Hopkins
You read the table correctly, and it seems to be confusing a lot of people. To go through it logically (I think) The longer the line, the more likely surge energy would be coupled into a cable -- certainly the case for induced lightning transients. Terminated lines shorter than a few meters are

CEPT Standards

2001-01-02 Thread Mike Hopkins
I've had a request to meet CEPT T/TR 02-02E, but can find no references to this. I found the CEPT web site, but they don't mention any standards at all. Can only find references to radio conferences, postage stamps and amateur radio -- nothing specific to testing products. Anyone out there have

RE: surges on 24VAC

2001-12-18 Thread Mike Hopkins
Most Surge testers having ac mains couplers will also work with DC power (some require minor options to work), so actually doing the test is pretty easy Question as I read it was if it is in fact reasonable Mike Hopkins Thermo KeyTek -Original Message- From: KC CHAN [PDD

RE: surges on 24VAC

2001-12-17 Thread Mike Hopkins
system bring DC into homes and buildings from wires strung on telephone poles) and for these systems, lightning testing might make sense -- hence no provision in the standard that makes DC systems exempt from testing. Hope this is helpful... Mike Hopkins Thermo KeyTek -Original Message

RE: 2 Phases in North America

2001-12-17 Thread Mike Hopkins
harmonic is fundamental plus the fundamental (once); second is the fundamental plus the fundamental x 2, etc. ). I like it! Mike Hopkins Thermo KeyTek -Original Message- From: bogdan matoga [mailto:bogda...@pacbell.net] Sent: Sunday, December 16, 2001 8:03 PM To: Cortland Richmond Cc

RE: Surge (immunity) requirement for equipment in telecommunicati on c enters

2000-12-20 Thread Mike Hopkins
is that shorter cables won't pick-up any significant energy from a radiated surge event. Hope this helps, Mike Hopkins -Original Message- From: Zohar Zosmanovich [mailto:zohar_zosmanov...@radwin.com] Sent: Wednesday, December 20, 2000 6:47 AM To: 'emc-p...@majordomo.ieee.org' Subject

RE: Crossed Vane ESD Simulator

2000-12-19 Thread Mike Hopkins
Hi Sandy -- KeyTek built many of the crossed vane testers used by IBM and their suppliers. Older units (pre 1980's) were built by another company -- don't remember who. The crossed vane tester produces a ringing waveform which more closely resembles the kind of waves you would see from a

RE: Standards

2000-12-18 Thread Mike Hopkins
Theoretically Already we have EN's that are NOT identical with the IEC standards What's the odds of the EU (CENELEC) coordinating closely with IEC on these issues?? I'd say close to zero -- as convenor of IEC SC77B WG11 responsible for such things as Surge and EFT

RE: Blocking Cap for 1000-4-4 (EFT)

2000-12-05 Thread Mike Hopkins
Virtually all commercially available EFT simulators with built-in coupler/decouplers for the ac mains contain the 33nF capacitors internally. The only reason you might need to use them externally is if you were building your own coupler/decoupler, which also includes the necessary backfilter

RE: How does RF travel through outer space?

2000-12-01 Thread Mike Hopkins
An excellent explanation -- I've seen these issues explained many times, either over simplified or overly detailed. The explanation below is a superb balance. Thanks Michael Hopkins KeyTek -Original Message- From: Nick Rouse [mailto:100626.3...@compuserve.com] Sent: Thursday,

RE: Ringing wave surge testing for Modem

2000-09-11 Thread Mike Hopkins
Also, refer to IEC 61000-4-5 section on telecom and FCC Part 68 for surge testing modems. Mike Hopkins KeyTek -Original Message- From: j...@aol.com [mailto:j...@aol.com] Sent: Monday, September 11, 2000 11:19 AM To: matt.aschenb...@echostar.com; emc-p...@majordomo.ieee.org Subject: Re

RE: 90 V gas-filled arrestors source?

2000-09-11 Thread Mike Hopkins
You can also get coupler/decouplers that meet the spec from KeyTek (1-800-753-9835) and other manufacturers. Mike Hopkins KeyTek -Original Message- From: Dan Kinney (A) [mailto:dan.kin...@heapg.com] Sent: Friday, September 08, 2000 1:37 PM To: David Gelfand; emc-p...@majordomo.ieee.org

RE: 90 V gas-filled arrestors source?

2000-09-11 Thread Mike Hopkins
An MOV won't work - it's a clamping device as opposed to a crowbar device. Gas filled arrestors are common in the telecom industry -- try CP Clare, Reltech (near Chicago), TII New York, Sankosha, Shinko, --- probably others, but can't remember them. Good luck Mike Hopkins KeyTek

RE: Heavy Industrial vs. Light Industrial

2000-07-31 Thread Mike Hopkins
which are characterized by being supplied directly at low voltage from the public mains network are considered to be residential, commercial or light industrial. How's that?? Mike Hopkins, KeyTek -Original Message- From: don_macart...@selinc.com [mailto:don_macart...@selinc.com] Sent

RE: Electrical safety of firearms

2000-07-31 Thread Mike Hopkins
My favorite is the light bulb and socket - simply changing a light bulb is inherently unsafe.. Mike Hopkins -Original Message- From: Peter Tarver [mailto:ptar...@nortelnetworks.com] Sent: Thursday, July 27, 2000 12:08 PM To: emc-p...@majordomo.ieee.org Subject: RE: Electrical safety

RE: Immunity measurement uncertainty

2000-09-14 Thread Mike Hopkins
yet.. Best Regards, Mike Hopkins -Original Message- From: Leslie Bai [mailto:leslie_...@yahoo.com] Sent: Thursday, September 14, 2000 4:24 PM To: IEEE EMC-PSTC (E-mail) Subject: Immunity measurement uncertainty Hello, members, Is there anyone who can direct me to somewhere I can

RE: EFT/Burst

2000-06-12 Thread Mike Hopkins
You are correct for purposes of COMPLIANCE to EN55024 and application of a CE Mark, you test each line with respect to a reference ground (PE), but as I'm sure you're aware, a customer can ask for whatever they think is relevant. Mike Hopkins mhopk...@keytek.com -Original Message

RE: EMC vs. Exi equipment

2000-05-12 Thread Mike Hopkins
Not sure I understand what a zener barrier is, but if you mean there are zener diodes across the line or even in series with the line, this has no bearing on the applicability of 61000-4-5. IEC 61000-4-5 is a method of surge testing a product without regard to the signal line type, data,

RE: Surge

2000-05-05 Thread Mike Hopkins
EUT will behave with the surge, will it be possible to determine how they will behave in parallel.. Good luck... If you have any other questions, please give me a call or email -- Mike Hopkins mhopk...@keytek.com or 1-800-753-9835. Mike Hopkins -Original Message- From: Dale Albright

RE: EN61326-1 Harmonics

2000-03-28 Thread Mike Hopkins
electronic products. Mike Hopkins mhopk...@keytek.com -Original Message- From: Barry Ma [SMTP:barry...@altavista.com] Sent: Tuesday, March 28, 2000 12:40 PM To: chr...@gnlp.com Cc: bkundew...@qtm.net; nprov...@foxboro.com; emc-p...@ieee.org Subject: RE: EN61326-1 Harmonics

RE: Lightning Surge Equipment

2000-03-24 Thread Mike Hopkins
of handling both the voltage (1500V) plus the 100A surge currents. Let me know if you need help there. Mike Hopkins KeyTek -Original Message- From: David Spencer [SMTP:dspen...@oresis.com] Sent: Thursday, March 23, 2000 11:16 AM To: 'n...@world.std.com'; 'EMC PSTC' Subject

RE: Split or Not to Split?

2000-03-17 Thread Mike Hopkins
Thought this was over by now;;; but since it continues, my vote is NO split. Mike Hopkins mhopk...@keytek.com -Original Message- From: Mark Hassebrock [SMTP:mhass...@qualcomm.com] Sent: Friday, March 17, 2000 3:46 PM To: emc-p...@majordomo.ieee.org Subject: Split

RE: Surge Testing per EN 55024/EN61000-4-5

2000-03-01 Thread Mike Hopkins
connections. For example, many television sets have two wire power plugs, are in plastic cases, but if you have cable tv, the odds are that coax cable is grounded. Same thing applies if there is a telecom line involved -- very likely one of the telecom lines is ground. .. Mike Hopkins

RE: EN61000-4-11

2000-01-25 Thread Mike Hopkins
You can't really use an AC power source for this requirement. The way its done is with a tap switched transformer (KeyTek) or via a switch between two or more variacs or other fixed ac sources. Mike Hopkins KeyTek -Original Message- From: fwhitfi...@rheintech.com [SMTP:fwhitfi

RE: EN 61000-4-2

2000-01-17 Thread Mike Hopkins
of the designated discharge points is the minimum. Mike Hopkins -Original Message- From: kim.boll.jen...@lasat.com [SMTP:kim.boll.jen...@lasat.com] Sent: Monday, January 17, 2000 5:41 AM To: emc-p...@ieee.org Subject: EN 61000-4-2 Dear all I'm writing on a internal

RE: transient suppression

2000-01-12 Thread Mike Hopkins
Keep in mind rise time (really - turn on time) doesn't mean much on the AC mains. Most specs assume the measurement is made right at the body of the device, so even short wires will add enough inductance for a fast wave to make the arguement moot. -Original Message- From: Dan Kwok

RE: transient suppression

2000-01-12 Thread Mike Hopkins
and if you go over the number even slightly, they'll blow. Avalanche devices in series with a resistor or clamp are sometimes used, but not as effective as a simple MOV. Mike Hopkins KeyTek -Original Message- From: Robert Macy [SMTP:m...@california.com] Sent: Tuesday, January 11, 2000 7:26

RE: Tiger Tail for 27 MHz?

2000-01-11 Thread Mike Hopkins
than gain.. Mike Hopkins -Original Message- From: Lacey,Scott [SMTP:sla...@foxboro.com] Sent: Tuesday, January 11, 2000 8:33 AM To: 'emc-p...@ieee.org' Cc: 'sla...@foxboro.com' Subject: Tiger Tail for 27 MHz? Fellow Listmembers, I have a question regarding tiger

RE: Radiation levels.

2000-01-11 Thread Mike Hopkins
this is useful. Mike Hopkins mhopk...@keytek.com -Original Message- From: David Monreal [SMTP:dmonr...@advancedshielding.com] Sent: Tuesday, January 11, 2000 5:15 AM To: emc-p...@majordomo.ieee.org Subject: Radiation levels. Hi all! Could anyone tell me the radiation

RE: Y3K

2000-01-07 Thread Mike Hopkins
case) as milli. The 1998 EMC Encyclopedia shows M = mega and m = milli. Mike Hopkins KeyTek -Original Message- From: Gary McInturff [SMTP:gmcintu...@telect.com] Sent: Thursday, January 06, 2000 5:50 PM To: 'Egon H. Varju'; EMC-PSTC Subject: RE: Y3K Oh my last birthday my

RE: Methods Equipment; Surge Dips

2001-11-20 Thread Mike Hopkins
-- they were one of the few AC sources that weren't upset with transients on the output stage coming back from an EUT. Mike Hopkins -Original Message- From: Ehler, Kyle [mailto:keh...@lsil.com] Sent: Tuesday, November 20, 2001 3:57 PM To: 'Mike Hopkins'; Ehler, Kyle; 'wmf...@aol.com

RE: Methods Equipment; Surge Dips

2001-11-20 Thread Mike Hopkins
in the AC levels you require via a variac or some other transformer and simply switch between them Mike Hopkins -Original Message- From: Ehler, Kyle [mailto:keh...@lsil.com] Sent: Tuesday, November 20, 2001 1:19 PM To: 'wmf...@aol.com'; emc-p...@ieee.org Subject: RE: Methods Equipment

RE: Pre-amps

2001-11-16 Thread Mike Hopkins
length acts as an impedance transformer.) For specific frequencies, one could use the cable as an impedance matching section between the source and load, but this is clearly unusable for broad-band applications. Mike Hopkins -Original Message- From: Ken Javor [mailto:ken.ja

RE: Frequency Allocations

1998-08-21 Thread Mike Hopkins
I've ordered the chart in June and recieved a post card thanking me for the order and notifying me that the charts are back ordered -- no idea when I'll recieve it. Mike Hopkins mhopk...@keytek.com -Original Message- From: ed.pr...@cubic.com [SMTP:ed.pr...@cubic.com] Sent: Thursday

RE: Re[2]: Professional Equipment EN 61000-3-2

1998-10-02 Thread Mike Hopkins
one, but if I had to guess, I'd say it will end up being actual power being taken by the device during the test. Mike Hopkins mhopk...@keytek.com -Original Message- From: Crabb, John [SMTP:jo...@exchange.scotland.ncr.com] Sent: Friday, October 02, 1998 4:35 AM To: emc-p...@ieee.org

RE: Room grounding

1998-10-07 Thread Mike Hopkins
may be minimal, but why take any at all. Mike Hopkins mhopk...@keytek.com -Original Message- From: lfresea...@aol.com [SMTP:lfresea...@aol.com] Sent: Tuesday, October 06, 1998 3:36 PM To: emc-p...@majordomo.ieee.org Subject: Room grounding Chaps, The grounding of a shield

RE: EFT/B Generator for EN61000-4-4 Test

1998-10-07 Thread Mike Hopkins
I can recommend Transient Speialists, Tel: 708 246 3297; fax 708 482 3972 or email lpit...@aol.com. They will do short term rentals plus provide some support. Mike Hopkins mhopk...@keytek.com -Original Message- From: Bailin Ma [SMTP:b...@namg.us.anritsu.com] Sent: Wednesday, October

RE: IEC 1000-X-X vs EN 61000-X-X

1998-10-09 Thread Mike Hopkins
. Hope this helps. Mike Hopkins mhopk...@keytek.com -Original Message- From: Bailey, Jeff [SMTP:jbai...@sstech.on.ca] Sent: Friday, October 09, 1998 12:53 PM To: 'EMC-PSTC' Subject: IEC 1000-X-X vs EN 61000-X-X Hello group, I currently have a number of the IEC 1000-X-X

RE: Metric Directive in Japan??

1998-03-06 Thread Mike Hopkins
regulation which makes it illegal for HIM to resell the product to his customer. That's all I know Mike Hopkins mhopk...@keytek.com -- From: Mike Morrow[SMTP:mmor...@compuserve.com] Reply To: mmor...@compuserve.com Sent: Monday, February 23, 1998 4:33 PM

RE: Signatory for US based Manufacturer

1998-12-15 Thread Mike Hopkins
of that My own opinion is that the manufacturer in any country can sign a Declaration of Conformance, but it must be kept on file in the EU by a representative of the manufacturer or by the importer. Happy Holidays to all That's all the document research time I have this month Mike Hopkins

RE: Signatory for US based Manufacturer

1998-12-15 Thread Mike Hopkins
That's certainly our interpertation. We do the tests here, sign the DofC here, then place a copy on file with one of our divisions in The Netherlands. Mike Hopkins mhopk...@keytek.com -Original Message- From: Robert Tims [SMTP:rt...@emx.ericsson.se] Sent: Tuesday, December 15, 1998 1

RE: EN 61000-4-4

1998-12-14 Thread Mike Hopkins
or adjecent to I/O lines. It's not likely the signals would be coupled to one line and not to another; in fact, because of the very fast pulses, everything gets very well coupled very quickly. Mike Hopkins mhopk...@keytek.com -Original Message- From: Collins, Erik D. [SMTP:collin...@lxe.com

RE: Transient/Surge/Lightning Standards for DC power equipment

1998-12-09 Thread Mike Hopkins
for things like 48VDC lines up to 20-30A. Let me know if you want more information. Mike Hopkins mhopk...@keytek.com -Original Message- From: salba...@hns.com [SMTP:salba...@hns.com] Sent: Tuesday, December 08, 1998 5:04 PM To: emc-p...@majordomo.ieee.org Subject: Transient/Surge

MITI

1998-12-09 Thread Mike Hopkins
I've been asked about testing and certification requirements for MITI but have been unable to locate any information. Anyone out there know where i can find such ?? Tried their web page, but couldn't see anything about testing requirements. Thanks, Michael Hopkins mhopk...@keytek.com Tel:

RE: Ground Hog Day.

1998-02-23 Thread Mike Hopkins
I'm getting the same thing : had over 100 email's this morning, and many were duplicates and some triplicates. What's up ?? -- From: Chris Dupres[SMTP:chris_dup...@compuserve.com] Reply To: Chris Dupres Sent: Monday, February 23, 1998 9:16 AM To: emc-pstc

RE: Pros/Cons of Using TEM Cells for 801-3, 61000-4-3...

1998-01-19 Thread Mike Hopkins
I agree, there are a lot of look-alike cells on the market: None of which are truely compliant to the 1000-4-3 requirements, although many have made various claims in the past (including us!)... There is a new amendment to 1000-4-3 that deals specifically with the issues of using TEM cells, and

RE: Odd Immunity Problems

1998-07-08 Thread Mike Hopkins
is legislation in towns which restrict antennas -- often to keep cell phone towers out! There is FCC rulings to pre-empt local statutes, but sometimes it becomes a court fight. Mike Hopkins mhopk...@keytek.com (K1VLB) -Original Message- From: Keith Armstrong [SMTP:karmstr...@iee.org] Sent

RE: odd immunity problems ?

1998-07-08 Thread Mike Hopkins
I don't have details, but do know that a number of manufacturers of gaming machines do perform so pretty tought immunity testing -- ESD to 20kV, surge, and the like.. Mike Hopkins mhopk...@keytek.com -Original Message- From: cefa...@mksinst.com [SMTP:cefa...@mksinst.com] Sent

RE: Japan EMC/Safety Requirements

1998-07-08 Thread Mike Hopkins
We sell a number of instruments into Japan without any special test requirements. Our products are CE Marked, but wev'e had no requirement to do any additional testing. Mike Hopkins mhopk...@keytek.com -Original Message- From: CollinJJ [SMTP:colli...@perkin-elmer.com] Sent: Tuesday

RE: Ce versus FCC

1998-07-02 Thread Mike Hopkins
Hard to do in simple words but: FCC -- many emissions requirements for digital products; lightning immunity requirements for telecom (part 68). EEC EMC Directive -- both emissions an immunity requirements; specifics depend on the product. Suggest you look at a couple of these web pages to get

RE: EN61000-3-2 Harmonics testing 16 amps ITE equipment

1998-07-02 Thread Mike Hopkins
EN61000-3-2 is a product family standard on its own and is not part of EN 50082-1-1997. For ITE it becomes mandatory on 1/1/2001. -Original Message- From: Gary McInturff [SMTP:gmcintu...@packetengines.com] Sent: Thursday, July 02, 1998 11:18 AM To: 'emc-pstc list server' Subject:

RE: GS Requirements

1998-04-24 Thread Mike Hopkins
!! Have a ball. Mike Hopkins mhopk...@keytek.com -Original Message- From: WOODS, RICHARD [SMTP:wo...@sensormatic.com] Sent: Friday, April 24, 1998 11:43 AM To: Mike Hopkins Cc: '@IEEE' Subject: RE: GS Requirements How quickly we forget. Recall that the Low Voltage

RE: GS Requirements

1998-04-24 Thread Mike Hopkins
I don't believe Germany or any other EU country can impose additional legal restraints on the importation or use of equipment beyond the CE requirements. If this were allowed, each nation could, and probably would, impose additional restrictive requirements for the importation and use of products

RE: FDA Modernization Program

1998-03-26 Thread Mike Hopkins
Try http://www.fda.gov/cdrh/ode/parad501.html I think that will give you the complete information. You can also try www.aami.org. Mike Hopkins mhopk...@keytek.com -Original Message- From: sitar...@kodak.com [SMTP:sitar...@kodak.com] Sent: Thursday, March 26, 1998 3:51 PM To: emc

RE: Required number of pulses per minute

1998-03-26 Thread Mike Hopkins
hot. For this reason, most surge specifications don't require surge testing at rates faster than one per minute - this keeps the average power very low, won't affect MOV performance, and keeps the MOV cool! Mike Hopkins mhopk...@keytek.com -Original Message- From: Ing. Gert Gremmen

RE: Transient overvoltage field study paper

1998-08-10 Thread Mike Hopkins
of such a study, I'd love to see it. Mike Hopkins mhopk...@keytek.com -Original Message- From: Peter E. Perkins [SMTP:peperk...@compuserve.com] Sent: Monday, August 10, 1998 2:01 AM To: PSNetwork Subject: Transient overvoltage field study paper PSNet info on a paper

RE: GTEM cell

1999-07-07 Thread Mike Hopkins
is now being circulated that would allow TEM cells, but ONLY if a TEM wave can be demonstrated throughout the frequency range being used (3-axis measurement, undesired vectors 6 db down). For emissions to EN's, TEM cells are not allowed for compliance testing. Mike Hopkins mhopk...@keytek.com

RE: Power Amps for Immunity Testing

1999-11-19 Thread Mike Hopkins
Try Kalmus -- Leo Smale at leosm...@seanet.com or 11807 North Creek Parkway S. Suite 109 Bothell, WA 98011 Tel: 1-800-344-3341 1-206-485-9000 Fax: 1-206-486-9657 Mike Hopkins -Original Message- From: dber...@wlgore.com [SMTP:dber...@wlgore.com] Sent: Friday, November 19, 1999 11

RE: Bellcore GR1089

1999-01-07 Thread Mike Hopkins
simultaneously with respect to ground), but there are also 4-wire tests (two, 3-wire pairs) and 12 pair tests. Additionally there is a 10/250us impulse used for coaxial lines that is HUGE energy... Mike Hopkins mhopk...@keytek.com -Original Message- From: tdonnelly [SMTP:tdonne

Magnetic field monitors

1999-12-16 Thread Mike Hopkins
Our customers have asked us to supply a meter which can be used to monitor/measure magnetic fields in Amps/meter for setting up tests IAW IEC 61000-4-8. We've been offering a meter made in the U.S that reads in Gauss (seems okay for U.S. customers), but some customers in the far east are

RE: IEC 61000-4-28

1999-11-29 Thread Mike Hopkins
sense. If product committees want to use these for compliance, they are free to do so, but the IEC guidelines in 1000-4-1 make it clear which have general applicability and which do not. This one does NOT. Mike Hopkins mhopk...@keytek.com -Original Message- From: Martin Rowe (TMW

RE: Doubt on household equipment interference

1999-09-02 Thread Mike Hopkins
Sounds like a definate maybe... Mike Hopkins -Original Message- From: Muriel Bittencourt de Liz [SMTP:mur...@grucad.ufsc.br] Sent: Wednesday, September 01, 1999 3:55 PM To: Lista de EMC da IEEE Subject: Doubt on household equipment interference Dear Members I'd

RE: Concrete as an insulator??? -- and now FCC/FAA

1999-08-24 Thread Mike Hopkins
If I'm not mistaken, there IS an FAA regulation prohibiting the use of cell phones in airplanes -- I have the regs at home and will look it up. Mike Hopkins mhopk...@keytek.com -Original Message- From: miksher...@aol.com [SMTP:miksher...@aol.com] Sent: Tuesday, August 24, 1999 11:13

RE: re: EN50082-1:1997 EN55024

1999-08-20 Thread Mike Hopkins
mode and 2kV intervals for air discharge. It's clear these requirements will go forward -- there's just too much evidence for the existance of the phenomena, even though the reasons aren't always clearly understood for a specific EUT. Mike Hopkins mhopk...@keytek.com -Original Message

Position open with KeyTek

1999-07-01 Thread Mike Hopkins
Having seen numerous postings relating to job openings in EMC, I trust the following is not out of line: Electronic Design Engineer Position Senior electrical/electronic engineer with analog design background to work on design of KeyTek's pulsed-EMI (surge, EFT) and ESD test systems. The

RE: Transmission Line Theory

1999-05-13 Thread Mike Hopkins
to the load. If this extra line is a single line and not paired with a return, it will likely operate as an antenna. If that line were the same impedance as the load, half the energy from the source would go to the antenna and half to the load... Mike Hopkins mhopk...@keytek.com -Original Message

RE: RE: ESD in Power Station

1999-04-01 Thread Mike Hopkins
the higher levels are required NOT because ESD is more of a problem, but because a failure could be more catastrophic than in your average office. Improper switching could cause realitively large scale outages and possible damage to the system. Mike Hopkins mhopk...@keytek.com -Original

RE: I/O Surge

1999-04-01 Thread Mike Hopkins
than 42 ohms (if it's only 42 ohms for the surge voltage frequencies, you'll only get 50% of the desired surge voltage -- ohms law). Anyway, it isn't simple. If someone does have a good way of increasing the signal frequency capability of the CDN's, we'd like to hear about it. Mike Hopkins mhopk

RE: ESD in Power Station

1999-04-01 Thread Mike Hopkins
as soon as you entered the sub-station.. Mike Hopkins -Original Message- From: b...@namg.us.anritsu.com [SMTP:b...@namg.us.anritsu.com] Sent: Wednesday, March 31, 1999 5:36 PM To: emc-p...@ieee.org Subject: ESD in Power Station Hi, Please allow me to pose two questions

RE: EMC for automation control - Electricity utilities (UNIPEDE )

1999-03-31 Thread Mike Hopkins
discharge from the end of your finger is something you'd remember! Even 10kV is pretty uncomfortable.. Hope this is helpful, but I doubt it would influence the people who wrote the standard... Mike Hopkins mhopk...@keytek.com -Original Message- From: s_doug...@ecrm.com [SMTP:s_doug

RE: Australian Telecom Surge testing

2002-05-01 Thread Mike Hopkins
generators designed to meet only the CCITT or IEC specification may not also meet the 9/720us requirements of FCC. Both specify a 20uF energy storage capacitor for this waveform... Hope this helps... Mike Hopkins Thermo KeyTek -Original Message- From: John Cronin [mailto:croni