Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread frenergy
The only thing I would add to William's list of things to do to solve this issue is that there is a proper sequence in shutting down and rebooting the inverter, found in Outback  docs.  There is also firmware for the HUB but not sure if that would help or is necessary in this situation. Bill

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread Steve Higgins
I don't know if this will help, but there is a setting under the AGS menus called DC Generator. There is DC Absrob timer and DC Absrob Votlage. It's imperative that this is left alone if you are using an AC source, I find many systems that are doing this the customer or installer freaked out

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread jay
Lones is correct as usual The newer Mate3 when battery charging with the generator has to have time below rebuik or it won’t work. So your options are to raise the rebulk voltage, this allows more time below the rebulk, which allows for a complete charge. This situation is especially often

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread jay
Yes SOC is a calculation and with proper setup it works perfectly. This includes changes over its lifespan etc. However one issue that I’ve found is if you tie the PV to the SOC it does set up problems and usually creates short cycling, sulfation and premature battery life. The fix is: Go

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread Ray
I agree with William, SOC is just a calculation, that can change with temperature, age of batteries, and even when the last full charge occurred. We just had trouble with an inherited Sunny Island system that only allows gen start settings based on SOC. The actual battery SOC didn't correspond

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread William Miller
Drake: I would suggest the following course of action: 1. Reboot Mate 2. Reboot inverter 3. Reset all equipment to factory defaults and manually reprogram each item 4. Update Mate Firmware 5. Update Inverter Firmware. We have solved mystery Radian problems

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread Jay
Is it ags start and is it starting on volts or %, or load? > On Jan 8, 2021, at 1:10 PM, Dave Angelini Offgrid Solar > wrote: > > You said both, it will go into absorb for an hour only and it will net go > into absorb. Which one please? > > Is there an AGS? > > > Dave Angelini Offgrid

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread William Miller
Mick: Here’s a thought: If the system has an FNDC, the charging may be programmed to terminate at a specific SOC. I have been told by OB tech support, and I believe this, that using SOC and battery voltage over time and/or charge taper to control charging is like the old adage, “too many

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread drake . chamberlin
It will initially go into absorb, but only stay there for 1 hour. He has tried to get it back in absorb by shutting the generator off. He turns the generator back on, and it doesn't trigger an absorb charge. The system will only take a charge from the generator for 1 hour each calendar day.

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread Tuss, Lones
Hello Drake Have the customer initiate a new bulk cycle from the Mate3. Do this by Pressing the Charger button on the Mate3 Select Bulk Charge then Start Bulk. This will initiate a full Bulk/Absorb Cycle as programmed in the inverter. If the Absorb time is set to 2 hours that is what will happen.

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread Dave Angelini Offgrid Solar
Same page with you Jay, as usual... Does the battery system go to absorb with solar still even if it is cloudy? Maybe a bad battery? Tis the season! Can the user go thru the set-points and make sure nothing has changed? Gen sets can do weird surges that can corrupt settings. If he has to

[RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread Mick Abraham
Happy Friday, Mechanix~ Drake Chamberlin wrote about the Radian inverter that began running a "too short" absorption interval after several years of normal operations. Drake said the possible culprit is inverter firmware per Outback; I wish to add a data point & follow up questions: I sold an

Re: [RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread Dave Angelini Offgrid Solar
You said both, it will go into absorb for an hour only and it will net go into absorb. Which one please? Is there an AGS? Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 On Fri, 08 Jan 2021 13:33:56

[RE-wrenches] Radian Charges 1 hour per calendar day

2021-01-08 Thread drake . chamberlin
Hello Wrenches, An off grid, Radian / Mate 3 system we set up some years back has worked flawlessly. The client is now reporting that his system will only go into absorption charge for 1 hour per calendar day. The setting was previously to absorb for 2 hours. He has tried shutting off the