The output of a 120/240 volt auto transformer shares neutral with the input
when you use to couple a 120 volt device to a 120/240 volt split phase
system... there is no isolation because the neutrals are the same connection.
I've done AC coupling with auto transformer specifically between
As I understand it, backfed referred to the source of energization. Current
flow alternates both ways at line frequency regardless of the direction of
power flow. The reason for marking line and load is because the source of
energization remains powered when the device is turned off. In the
One of the projects I've been working on is a secondary LiIon battery pack
solution using refurbished EV battery modules originally build by AC
Propulsion and now needing a home.
100Ah or 200Ah x 48 volt nominal. The batteries were originally built for
EV use with relatively high performance, so
I've successfully operated isolated temporary installations where the
ac-coupled inverter output significantly exceeds the battery-backup inverter
nameplate rating. Obviously there has to be enough firm AC load to absorb at
least the portion of the AC coupled output that exceeds the grid tie
Code insanity.
There is never voltage on the load side of an open AC switch, arc fault, or
circuit breaker device supplying a solar inverter that meets UL1741. Solar
inverters are current sources only, and only while utility voltage is present.
/wk
William Korthof
714.875.3576
Sustainable
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
On Apr 25, 2014, at 7:59 AM, Jason Szumlanski ja...@fafcosolar.com wrote:
I heard Canadian Solar prices are on the rise, and supply will be tight and
uncertain. Korean made panels were recommended as an alternative.
Jason
as a permanent seal) seem like the real factors, not
flashings. On flat roofs, issues with drains clogging and ponding are the
issues I've seen.
Although I would count among the installers to use flashing, I accept the
arguments from the proponents of no-flashing installation.
/wk
William
service can easily and safely be served by 150A or 175A of utility supply.
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
On Apr 3, 2014, at 9:18 AM, Phil Forest pfor...@southmountain.com wrote:
Troy,
This is my first post.
We install 32 amp rated output inverters, reduce
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
On Mar 27, 2014, at 7:19 AM, Chris Mason cometenergysyst...@gmail.com wrote:
I have a couple of suggestions. A pump motor of that size is likely Class H and
requires a 7x starting current or Locked Rotor Amperage. During starting
I think I'm missing something; 690.10 is part of the solar article. A 240 volt
welder outlet (utility outlet, usually NEMA #6-50) isn't pertinent to solar,
and is allowed anywhere as far as i know, indoors or out. Well, maybe not above
the bathtub...
/wk
William Korthof
714.875.3576
(3 phase inverter) or non-additive if you have a bank of 1 phase
line/neutral (120 or 277 volt) inverters
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
On Mar 4, 2014, at 1:31 PM, Allen Frishman amfr...@aeonsolar.com wrote:
what inverter(s) are you using?In many cases
). Each rack also slopes about ~17
degrees from the back legs to the front legs. Net slope of the array is
effectively turned near more south than the slope, while still optimizing for a
small array footprint.
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
On Feb 16, 2014, at 1:35
code rules.
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
On Feb 14, 2014, at 2:27 PM, Dan Fink danbo...@gmail.com wrote:
Hi Bill;
That was tongue in cheek about watching my back! But wow I've seen the
discussion get heated, even in face to face outreach sessions
I've installed a few and they are working great. No issues or problems to
report.
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
On Feb 12, 2014, at 3:35 PM, toddc...@finestplanet.com wrote:
on a related question, do wrenches have any reviews about the schneider/xantrex
80
.
Even electric water heaters and most AC compressors that I've checked also seem
to be dual rated (208/240V). Electric car chargers are also agnostic.
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
I feel sort of stupid asking this, but it has never come up for me before
?
Are there any class B or A rated modules on the market?
Who's brilliant idea was this?
/wk
--
William Korthof http://www.sustainsp.com/images/SSP_Logo_RGB_email.jpg
714.875.3576 and 800.524.2970
Sustainable Solutions Partners
(also dba: EE Solar)
___
List
experimental beta-test.
I remember the SunCentric from several years ago, but not sure how durable
that turned out, and I was having trouble a vendor for it now. Any
suggestions for today with some favorable track record? Or suggestions on
what to avoid?
William Korthof
Sustainable Solutions Partners
and neutral, and xfmr
losses...
Alternate option is to get an isolation transformer with 208 primary and
120/240 secondary. Bond the midpoint.
Better phase balance, but xfmr losses.
/wk
William Korthof
714.875.3576
Sustainable Solutions
#956904
-
From: Christopher Warfel
We
I haven't seen much discussion about the tariffs, but I think the current
plan is really an outrage. I've toured the SolarWorld factory twice and
used many of their modules---I'd like to see US Solar manufacturers
succeed, but I've also toured Chinese factories, and I'm thoroughly
impressed by how
Interesting update I've installed dozens of non-isolated
transformerless inverters
with LADWP customers since those genius inverters first became available
from
Power-One's inverter ancestor, Magnetek. I don't remember ever having a
conflict or
technical issue with an engineer or inspector
Peter,
Consider getting a used electric forklift.
Every forklift inside a Costco, Home Depot, or Lowe's is electric.
I bought a Crown made in the early '90s about 6 years ago and it has
always worked tirelessly. The distributor was LA Lift; they supplied a
compatible industrial charger and
The batteries in my forklift are from the early 90's and continue to perform,
despite regular abuse and irregular care. I'll second the comment about the
economy of golf cart batteries... They are great for situations where they can
be made to fit.
They've worked well for me in all sorts of
Flashed footings...
Cost shouldn't be the problem.
You can buy solar stand-offs for around $5 each from Ezee manufacturing
(North Hollywood, CA) and Otay rubber flashings for under $5 each.
In SoCal, they appear to work adequately for PV mounts and service risers
(7-10+ years, no sign of
Does anyone have experience with heat pump water heaters?
There are a couple units available now and they seem great---I just purchased
one from
Lowes (GE hybrid water heater), which has a 700 watt heat pump and 2 standard
4500
watt heating elements... the brains of the water heater let you
Yes, Yorba Linda technically requires an electrical PE stamp on PV
projects.
We've probably done a dozen installations in the city, though I
don't think they've
enforced the electrical PE requirement on all projects. They do
require structural
PE on all projects as well, and that
We have three of the Xantrex/Trace GTI units, with one still-in-the-
box-new from applications that got modified.
They're collecting dust on the shelf... I'd be more than happy to
send them to a new home and free up space.
William Korthof
Energy Efficiency Solar/ Acro
(714) 875-3576
1
Why bother with the DC converters if you only have 2 strings?
Get a wide-range, dual-channel inverter (Power One 5000) and plug in
the modules
however you like. The bypass diodes in the modules will bypass the
shaded module
sections as appropriate for the conditions, and rest of the modules
If the angle differs by more than a few degrees, there will be
significant mismatch losses in a single string situation
two parallel strings of equal size but different orientations (Fronius
white paper) present a much smaller issue.
If the angle of modules in a single string varies
I'm beginning to wonder if the allowed voltage range for grid-tie
inverters (+/-10%) is too
sensitive in some networks and contributes more harm than benefit.
This is close to home.
We actually have a significant number of customers who've had trouble
with grid voltage
causing their
1. AC disconnect options (Andrew Truitt)
We used to use a lot of those pull-out air conditioner disconnects, we
liked the low price.
The 60 amp version usually works fine for 15 amps or less, but I
really don't think it's
reliable at anything close to the 60 amp rating. We've had about
30 matches
Mail list logo