RE: Hanger Loading

2018-05-10 Thread Ed Kramer
I agree. The loads given on the data sheets have safety factors built-in. If for some reason you needed to do an engineering analysis of that hanger, you’d have to contact Tolco for the load at which it failed during testing. Ed Kramer Bamford Fire From: Sprinklerforum

Re: Hanger Loading

2018-05-10 Thread Parsley Consulting
Mike is correct, Jerry.  That 5x+250 only comes into play when using a hanging method which isn't listed. *Ken Wagoner, SET *Parsley Consulting*** *350 West 9th Avenue, Suite 206 *Escondido, California 92025 *Phone 760-745-6181* Visit the website *** On

Re: Hanger Loading

2018-05-10 Thread Mike B Morey
I believe if you look at the wording of the standard the only time the phrase 5 times the weight of the water filled pipe plus 250 pounds occurs is in situations that require an "engineered" solution to hanging. EG multiple system supports, pipe stands outside the scope of NFPA etc. I can't

RE: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread John Drucker
Here's the NEC Code Section; 2017 NEC 250.104 Bonding of Piping Systems and Exposed Structural Metal. (A) Metal Water Piping. The metal water piping system shall be bonded as required in (A)(1), (A)(2), or (A)(3) of this section. (1) General. Metal water piping system(s) installed

RE: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread John Drucker
Correct cannot be used for "GROUNDING". However per the NEC all metallic water piping including sprinkler piping is required to be "BONDED". GROUNDING = Used to connect the building electrical system to Earth. Fire Sprinkler piping including Underground, FDC's etc are not considered ground

RE: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread cliff
Mike, Don't hold me to this but I believe it's been in the Standard for many years. Cliff Whitfield, SET President Fire Design, Inc. 184 Comfort Place Burnsville, NC 28714 Ph: 828-284-4772 cl...@fire-design.com

RE: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread JD Gamble
10.6.8 2010 ed. Life Safety Solutions of Sheridan JD Gamble jgam...@lssofsheridan.com (307) 763-3361 From: Sprinklerforum On Behalf Of Mike Hairfield Sent: Thursday, May 10, 2018 12:37 PM To:

Re: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread Mike Hairfield
Here in VA we are under the NFPA 13-2010 so I guess the electrician gets a free ride. From: Sprinklerforum on behalf of Larry Keeping Sent: Thursday, May 10, 2018 2:31 PM To:

RE: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread JD Gamble
10.5.1 2016 ed Life Safety Solutions of Sheridan JD Gamble jgam...@lssofsheridan.com (307) 763-3361 From: Sprinklerforum On Behalf Of Mike Hairfield Sent: Thursday, May 10, 2018 12:28 PM To: Sprinkler Forum

RE: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread Larry Keeping
NFPA 13 - 2016: Section 8.18 & Section 10.5. Larry Keeping From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Hairfield Sent: May-10-18 2:28 PM To: Sprinkler Forum Subject: Grounding Electrical Wire to

Re: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread Mike B Morey
13 2016 8.18 and 10.5 for underground, both have annex material worth looking at depending on what the goal is. Mike Morey CFPS 3229 • NICET S.E.T. 123677 Project Manager • Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive • Fort Wayne, IN • 46825 direct

Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread Mike Hairfield
Where in NFPA 13 does it say that the sprinkler system can not be used to ground the electrical system? Thanks, Mike ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org

Hanger Loading

2018-05-10 Thread Jerry Van Kolken
I'm doing this right? I'm looking at a Tolco Fig 200-2 hanger ring. The max load is 400lbs. 400 - 250 = 150 / 5 = 30lbs 2" sch ~5.13lbs This means if I use this ring I will have to space my hangers about 5'8" on center. Jerry Van Kolken Millennium Fire Protection Corp.

RE: Main Drain Test Question NFPA 25

2018-05-10 Thread Brad Casterline
Thank you very much Anthony. Brad From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of anth...@archerconstruction.com Sent: Thursday, May 10, 2018 9:57 AM To: 'Brad Casterline' ; sprinklerforum@lists.firesprinkler.org Subject:

Re: Software

2018-05-10 Thread Fire Design
Mike, If you're taking what you think is 3x as long to design and coordinate a 3D system over a 2D system then you're not doing anything wrong - it just takes time. Sure these fancy software packages might make things easier but there is still a lot of work to be done over a 2D design.

RE: Main Drain Test Question NFPA 25

2018-05-10 Thread anthony
Brad, you just hit the tip of the iceberg.. you are correct about the need to do Quarterly main drain testing, this is about 99.9 percent of the systems we install. >From NFPA 25-2014: Also see 13.3.3.1 Each control valve shall be operated annually through its full range and returned to its

RE: Main Drain Test Question NFPA 25

2018-05-10 Thread Brad Casterline
Thank you very much Jason. Brad From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jason Williams Sent: Thursday, May 10, 2018 8:41 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Main Drain Test Question NFPA 25 Yes sir you’re reading

Re: Main Drain Test Question NFPA 25

2018-05-10 Thread Jason Williams
Yes sir you’re reading correctly, 2002 it was introduced. In my field experience though, a whole lot of places it’s not getting done. Regards, Jason > On May 10, 2018, at 8:16 AM, Brad Casterline wrote: > > From NFPA 25-2014: > > "13.2.5.2 In systems where the sole

Re: Software

2018-05-10 Thread Travis Mack
As Matt mentioned, it is just the platform you are using. Honestly, I would find a way to switch platforms or no longer take jobs requiring BIM. That may pigeon hole you into tenant improvements and other small projects while you work on making the switch to a more friendly 3D platform. Yes,

RE: Software

2018-05-10 Thread tstone52
Autodesk BIM Glue 360 works well for 3d Coordination. It is a cloud based software. It handles exports from other platforms. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old

RE: Software

2018-05-10 Thread Matthew J Willis
It is not you. You are doing all you are able to with the platform you are using. It is a hard struggle using Navis to clash check. I have been on AutoSPRINK for damn, going on 19 years. If you cannot upgrade at this time, best advice I can give is let the BIM coordinator tell you where the

Main Drain Test Question NFPA 25

2018-05-10 Thread Brad Casterline
>From NFPA 25-2014: "13.2.5.2 In systems where the sole water supply is through a backflow preventer and/or pressure-reducing valves, the main drain test of at least one system downstream of the device shall be conducted on a quarterly basis." I've tried to make sure I am not taking this out of

Software

2018-05-10 Thread Mike Stossel
I am having a tremendous amount of problems performing 3D coordination's. It is taking me approximately 3 times longer than the old flat way of a standard coordination overlay. I know a lot of you are using AutoSprink and HydraCAD, but I am not. I am a SprinkCAD user and at this time cannot

Re: Non-Combustible Concealed Space (NFPA 13 2013)

2018-05-10 Thread Jay Stough
I agree about being accessable thru ceilings. I just mentioned it as to describe what it is: not a mezzanine or deck area above the ceiling. I agree with the single (or two) sprinklers at the unit idea, was just looking for some backup. As said before, the information from this group, more than