RE: Flammable and Combustible Liquid Storage

2018-02-14 Thread Reed A. Roisum, SET
m-boun...@lists.firesprinkler.org] On Behalf Of Ben Young Sent: Wednesday, February 14, 2018 11:45 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Flammable and Combustible Liquid Storage Check out the requirements in NFPA 45 for labs. This should tell you what the hazard is based on the quanti

Re: Flammable and Combustible Liquid Storage

2018-02-14 Thread Ben Young
lists.firesprinkler. > org] On Behalf Of Prahl, Craig/GVL > Sent: Wednesday, February 14, 2018 10:56 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: Flammable and Combustible Liquid Storage > > When the liquids are taken out of the cabinets, what is done with them? > Is

RE: Flammable and Combustible Liquid Storage

2018-02-14 Thread Reed A. Roisum, SET
0:56 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Flammable and Combustible Liquid Storage When the liquids are taken out of the cabinets, what is done with them? Is there any dispensing going on within the area where they are stored? Storing them in a cabinet may not drive the design cr

RE: Flammable and Combustible Liquid Storage

2018-02-14 Thread Prahl, Craig/GVL
: sprinklerforum@lists.firesprinkler.org Subject: Flammable and Combustible Liquid Storage [EXTERNAL] IFC 2012 Table 5003.1.1 gives the maximum allowable quantities of flammable and combustible liquids per control area. If the liquids are stored in approved cabinets you can increase the volume by 100%. I

RE: Flammable and Combustible Liquid Storage

2018-02-14 Thread Reed A. Roisum, SET
| KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Fpdcdesign Sent: Wednesday, February 14, 2018 10:04 AM To: Sprinklerforum Subject: Re: Flammable and Combustible Liquid Storage What is the surrounding occupancy?

Re: Flammable and Combustible Liquid Storage

2018-02-14 Thread Fpdcdesign
Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of Reed A. Roisum, SET > Sent: Wednesday, February 14, 2018 9:39 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: Flammable and Combustible Liquid Storage > > IFC 2012 Table 5003.1.

RE: Flammable and Combustible Liquid Storage

2018-02-14 Thread Matt Grise
Sent: Wednesday, February 14, 2018 9:39 AM To: sprinklerforum@lists.firesprinkler.org Subject: Flammable and Combustible Liquid Storage IFC 2012 Table 5003.1.1 gives the maximum allowable quantities of flammable and combustible liquids per control area. If the liquids are stored in approved

Flammable and Combustible Liquid Storage

2018-02-14 Thread Reed A. Roisum, SET
IFC 2012 Table 5003.1.1 gives the maximum allowable quantities of flammable and combustible liquids per control area. If the liquids are stored in approved cabinets you can increase the volume by 100%. I am trying to determine the proper sprinkler design for areas that contain flammable and co