Re: Detached Porte Cochere

2009-04-30 Thread Ron Greenman
Once adopted (with any revisions) a standard becomes a code and will be be given a number in line with whatever system your state might use. For instance here in Washington the state adopts the X edition of the IBC with revisions and if it becomes Revised Code of Washington (RCW) number Y. If the r

RE: Detached Porte Cochere

2009-04-30 Thread Don Lowry
As a follow up, This is the first time anyone has ever questioned us not having sprinklers in a small utility type structure not connected to the building. It's more like a big Gazebo, just for dropping off people. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:

RE: Detached Porte Cochere

2009-04-30 Thread Don Lowry
Yes, I have. If it were attached, as is usually the case there would be no question, we would provide sprinklers as a continuation of the building. This one is 6' from the building not attached. Thanks, any other ideas? Don -Original Message- From: sprinklerforum-boun...@firesprinkler.or

Re: Detached Porte Cochere

2009-04-30 Thread Todd Williams
See NFPA 13 (2002) section 8.14.7, especially handbook commentary. However, local building code may trump this and you will need to check them. At 08:01 PM 4/30/2009, you wrote: >Content-Type: multipart/related; > boundary="=_reb-r4EFA71E5-t49FA3BFB" >Content-Language: en-us > > > >Dear

Detached Porte Cochere

2009-04-30 Thread Don Lowry
Dear Forum, Fully sprinklered ALF building, Detached Porte Cochere 500 SF, with no connectors at all to the building. Does the porte cochere have to be sprinklered. IBC shows it should be a U occupancy <1000 sf so doesn't require separation distances. I looked in the archives but didn'

Re: Servicing and adjusting grooved joints

2009-04-30 Thread Forest Wilson
And that's why its crucial to Always read specs before bidding, and if necessary condition the bid. Forest Wilson Project Manager Cherokee Fire Protection Co. 1855 Bellbrook Ave. Ste C Xenia OH 45385 888-347-3079 ph 614-455-4324 fx

RE: Servicing and adjusting grooved joints

2009-04-30 Thread Rod DiBona
Bingo. Problem is most people reading this already know that and most people not involved only learn the hard way. Just when they learn, in comes the next one. Gotta love it. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org

Re: Servicing and adjusting grooved joints

2009-04-30 Thread Roland Huggins
We're from the federal government and we are here to help you. The technical point to be made is that doing government work is a whole different world and you best learn the dance before stepping onto that floor. I won't belabor the point that it typically doubles with questionable real ben

RE: Servicing and adjusting grooved joints

2009-04-30 Thread Steve Leyton
hnical Assistance, send an email to: techsupp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 4047 (20090430) ___

Re: Servicing and adjusting grooved joints

2009-04-30 Thread Todd Williams
I'll have what he's drinking. >3.4.6 Pipe Joints >Pipe joints shall conform to NFPA 13, except as modified herein. Not more >than four threads shall show after joint is made up. Welded joints will be >permitted, only if welding operations are performed as required by NFPA 13 >at the Contractor'

Re: Servicing and adjusting grooved joints

2009-04-30 Thread Ron Greenman
Welcome to the Corps. On Thu, Apr 30, 2009 at 2:11 PM, wrote: > Boy, welding up that 150ft, 6" main and transporting to the site would be a > challenge since you've got to do it in your shop. > > Do they have a Groove Inspector Division with vernier calipers checking those > grooves? > > Who t

RE: Servicing and adjusting grooved joints

2009-04-30 Thread Craig.Prahl
Boy, welding up that 150ft, 6" main and transporting to the site would be a challenge since you've got to do it in your shop. Do they have a Groove Inspector Division with vernier calipers checking those grooves? Who thinks up these specs? Craig L. Prahl, CET Fire Protection Specialist Mec

RE: Servicing and adjusting grooved joints

2009-04-30 Thread Fletcher, Ron
Where else would you put a requirement for access panels other than in the paragraph titled "Pipe Joints". Ron Fletcher Aero Automatic Sprinkler 21605 N. Central Ave Phoenix, AZ 85024 P: 623.580.7836 F: 623.434.3420 C: 602.763.4160 -Original Message- From: sprinklerforum-boun...@firesprin

RE: Servicing and adjusting grooved joints

2009-04-30 Thread Chris Cahill
"unless an access panel is SHOWN on the drawings for servicing or adjusting the joint." So show it on the drawing, it doesn't say it has to be installed, LOL. I know, I know someplace else it says install per drawing. Just strikes me as a funny way to write a requirement. Chris Cahill, P.E.

RE: CMSA upright

2009-04-30 Thread Chris Cahill
Cut, hand groove, rotate, mechanical coupling, done. Ok if you don't want to hand groove in the air cut remove both sides and insert two pre-fab'ed pieces thread by groove. Chris -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprink

Re: Servicing and adjusting grooved joints

2009-04-30 Thread Ron Greenman
Ron, Here's what it says (see last sentence) and the Corps follows these guidelines by law: 3.4.6 Pipe Joints Pipe joints shall conform to NFPA 13, except as modified herein. Not more than four threads shall show after joint is made up. Welded joints will be permitted, only if welding operations

RE: CMSA upright

2009-04-30 Thread Todd Williams
Upright is the caveat. None of the uprights go to 40 ft, or at least what I can find. There are supposedly heads in for testing at that height, but I don't know if anything has been listed yet. I am trying to retrofit an existing system with uprights. Screwed 2" branch lines on a grid, so rota

RE: Rating of the sprinkler escutcheon (membrane vs through)

2009-04-30 Thread Craig.Prahl
Was that advice from your friend Guido. Was the name Hoffa ever mentioned? lol Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 craig.pr.

RE: Rating of the sprinkler escutcheon (membrane vs through)

2009-04-30 Thread Bobby Gillett
Staggered (membrane). We have passed along the '99 SBC info that Craig supplied earlier, and imagine that - he's satisfied. If that didn't work, I was going to take the advice a friend on the west coast suggested. Thanks to all. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 42

Servicing and adjusting grooved joints

2009-04-30 Thread Fletcher, Ron
Here is a new one (to me) from our friends at the COE. Has anyone out there run into this before and if so what did you do? Unified Facilities Guide Specification, 3.4.6 Pipe Joints. "Grooved joints shall ne be used in concealed locations, such as behind solid walls or ceiling, unless an access pa

Re: Rating of the sprinkler escutcheon (membrane vs through)

2009-04-30 Thread Justin Reid
Bobby, Does the sprinkler line stagger within the wall assembly (making it a membrane penetration)? or is it a straight shot through the wall (making it a through penetration)? Bill, Could you argue that by firestopping the backside of the through penetration essentially makes the escutcheon side

RE: CMSA upright

2009-04-30 Thread Bobby McCullough
Viking as well. Bobby McCullough -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett Sent: Thursday, April 30, 2009 3:00 PM To: sprinklerforum@firesprinkler.org Subject: RE: CMSA upright I thought

RE: CMSA upright

2009-04-30 Thread Bobby Gillett
I thought Reliable had some new listings lately on them, might check theirs as well. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell bobby.gill...@keyfireprotection.com -Original Message- From: sprinklerforum-b

RE: Rating of the sprinkler escutcheon (membrane vs through)

2009-04-30 Thread Bobby Gillett
Just to clarify, if it makes a difference, the sprinklers going to the two rooms are staggered not being fed from a tee or cross. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell bobby.gill...@keyfireprotection.com

RE: CMSA upright

2009-04-30 Thread Fletcher, Ron
Check Victaulic. They have some new CMSA heads. Ron Fletcher Aero Automatic Sprinkler 21605 N. Central Ave Phoenix, AZ 85024 P: 623.580.7836 F: 623.434.3420 C: 602.763.4160 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] O

RE: Rating of the sprinkler escutcheon (membrane vs through)

2009-04-30 Thread bill . brooks
Back to the original question - it looks like you have through-penetrations of fire rated separation walls in each case. Room sprinklers fed off a bullhead tee, in the case of the stair you are going from the corridor to the stair. Neither is a membrane penetration, both would be through-penetrat

CMSA upright

2009-04-30 Thread Todd Williams
I am working on a warehouse that is in need of significant upgrading. Is there a CMSA upright sprinkler for rack storage that is approved for buildings 40 ft in height? (Actual building height 38'-3") Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860

RE: Fire rated escutcheon

2009-04-30 Thread Bobby Gillett
Thanks to all. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell bobby.gill...@keyfireprotection.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.

RE: Fire rated escutcheon

2009-04-30 Thread Johnson, Duane (NIH/OD/ORS) [C]
BOCA 714.1.6.2 (1999) permits noncombustible escutcheons to be used in lieu of firestopping...sorry no SBC in the office. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institute of Health -Original Message- From: Bo

Re: Fire rated escutcheon

2009-04-30 Thread Ron Greenman
You gotta love the local yokels. On Thu, Apr 30, 2009 at 10:52 AM, wrote: > He might need to make a call to the State F.M. since TN adopted the IFC > Effective December 16, 2008 and IBC Effective September 1, 2008. > > http://www.tennessee.gov/commerce/sfm/fpcesect.shtml > > > > Craig L. Prahl,

RE: Fire rated escutcheon

2009-04-30 Thread Craig.Prahl
He might need to make a call to the State F.M. since TN adopted the IFC Effective December 16, 2008 and IBC Effective September 1, 2008. http://www.tennessee.gov/commerce/sfm/fpcesect.shtml Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 I

RE: Fire rated escutcheon

2009-04-30 Thread Bobby Gillett
Thanks, Craig. He is using SBC '99. This project is in Northwest TN - local city fire marshal. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell bobby.gill...@keyfireprotection.com -Original Message- From: sprink

RE: Fire rated escutcheon

2009-04-30 Thread Todd Williams
Slept in the parking lot.. At 12:51 PM 4/30/2009, you wrote: >Must have stayed in a Holiday Inn Express last night. ;) > > >Craig L. Prahl, CET >Fire Protection Specialist >Mechanical Department >CH2MHILL >Lockwood Greene >1500 International Drive >PO Box 491, Spartanburg, SC 29304-0491 >

RE: Fire rated escutcheon

2009-04-30 Thread Craig.Prahl
Must have stayed in a Holiday Inn Express last night. ;) Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 craig.pr...@ch2m.com http://www.ch

RE: Fire rated escutcheon

2009-04-30 Thread Craig.Prahl
Not recognizing the IBC, what state is he from BTW? The SBC 1999 section 705.6.2 (3) says the same thing we've quoted from the IBC s far as exceptions.This is dealing with membrane penetrations like the line going into the wall with a sidewall sprinkler on the other end. Tell him to lo

RE: Fire rated escutcheon

2009-04-30 Thread Matthew J. Willis
-->triumvirate Good Word! Matthew J. Willis Norred Fire Systems L.L.C. 318-387-1134 Voice 318-387-1163 Facsimile m...@norredfire.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Thur

Re: Fire rated escutcheon

2009-04-30 Thread Todd Williams
SBC? Southern Building Code? I thought that was part of the triumvirate that created the ICC? At 11:44 AM 4/30/2009, you wrote: >Well the rating of the escutcheon is back, we replied to the fire marshall >with the comments from the IBC. His response was - show me the rating on the >escutcheon or

Fire rated escutcheon

2009-04-30 Thread Bobby Gillett
Well the rating of the escutcheon is back, we replied to the fire marshall with the comments from the IBC. His response was - show me the rating on the escutcheon or show me in the SBC, I'm not recognizing the IBC. Anybody have it in the SBC? Thank You, Bobby Gillett Sr. Project Manager K