Re: 13R local alarm

2013-05-29 Thread Greg McGahan
I am not sure what you are referring to exactly, but we often use a flow switch wored to a 6 electric bell. On Tue, May 28, 2013 at 10:24 PM, Todd - Work t...@fpdc.com wrote: I have an FM that wants local alarms for a 13R system within each unit (3 family house). Any suggestions on a small

Re: 13R local alarm

2013-05-29 Thread John Drucker
Connect via WF switch to the smoke alarms. John Drucker - Mobile Email - Original Message - From: sprinklerforum-boun...@lists.firesprinkler.org sprinklerforum-boun...@lists.firesprinkler.org To: sprinklerfo...@firesprinkler.org sprinklerfo...@firesprinkler.org Sent: Tue May 28

Re: 13R local alarm

2013-05-29 Thread Todd - Work
I was thinking that a 6 bell inside an apartment might be a little overkill as well as obtrusive. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On May 29, 2013, at 7:24 AM, Greg McGahan g...@livingwaterfp.com wrote: I am not sure what you are referring to

Re: 13R local alarm

2013-05-29 Thread Todd - Work
John, Do you really want to connect to smoke alarms (assuming that is feasible in this situation) in an apartment? Wouldn't a separate alarm be better so you know if you have water flow or burned the toast? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On

RE: 13R local alarm

2013-05-29 Thread Johnson, Duane (NIH/OD/ORS) [C]
NFPA 101:30.3.4.2.3In buildings protected throughout by an approved, supervised automatic sprinkler system in accordance with 30.3.5, required fire alarm systems shall be initiated upon operation of the automatic sprinkler system. Someone will need to go through Section 30.3.4.3 for

Racks

2013-05-29 Thread Fire Protection Services
Forum, I performed an Inspection a few days ago and the building is design as Ord2 with the exception of the shipping area which is Class 3. I noticed in a few areas they have installed on single rack against the outside wall with misc storage stacked at various heights. I have never seen

RE: Racks

2013-05-29 Thread Matthew J. Willis
Yes, If the alarms work, and water flows, pass the system and move on. Unless of course you were doing a NFPA 13 Inspection/evaluation. R/ Matt -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of

RE: Racks

2013-05-29 Thread Mark A. Sornsin, P.E.
Chris - there are a couple issues: 1. This was part of an inspection? If done per NFPA 25, you would not be evaluating the adequacy of protection - though as been suggested many times on this Forum, you may consider a separate note apart from the inspection forms indicating a concern

RE: Racks

2013-05-29 Thread Fire Protection Services
Thanks for your replies Matt and Mark They asked if they needed sprinklers in the racks and I was just checking on their behalf. I always write up a situation like this as needing a evaluation as you desiribed and leave it at that, Chris -Original Message- From:

RE: 13R local alarm

2013-05-29 Thread Mike Henke
Todd, Potter makes a small 120 VAC mini horn in white or red, model MH 120. It's the size of a single gang plate. Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 314-595-6740 Direct -Original Message- From:

Re: Racks

2013-05-29 Thread Todd - Work
Chris, The commodity and storage arrangement (length, height, single, double, etc) would need to be evaluated. Next the sprinkler system would need to be hydraulically evaluated. At that point, you can determine if in rack sprinklers are required. One independent rack can be sprinklered and

13R local alarm

2013-05-29 Thread John Drucker
What's the purpose of these local alarms ?, to alert the dwelling unit occupants ? First and foremost is a fire alarm system required in this building in accordance with IBC 907 ? If so then a fire alarm system is required pursuant to IBC 907 and accordingly notification appliances in accordance

Re: 13R local alarm

2013-05-29 Thread Todd - Work
This is an older single story 3 family side-by-side structure. The 13R system is being retrofitted. I believe (am confirming) that they have local hard wired smoke detectors only. Located in MA. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On May 29, 2013,

Re: Racks

2013-05-29 Thread Roland Huggins
Taking a different line of questioning, what is the classification of an individual rack (4 ft deep) that is by itself and located against a wall (say 12 inches off the wall)? Roland On May 29, 2013, at 6:46 AM, Fire Protection Services firepro...@roadrunner.com wrote: I noticed in a few

Re: Racks

2013-05-29 Thread ParsleyConsulting
Could it reasonably meet the definition of miscellaneous storage in 13? If so, depending on the commodity, and height of storage, OH2 may be the required design. * PARSLEY CONSULTING * Ken Wagoner 760.745.6181 voice 760.745.0537 fax website: www.ParsleyConsulting.com

Re: 13R local alarm

2013-05-29 Thread George Church
Couldn't treat em as 13d irc townhouses? Sent from my iPhone On May 29, 2013, at 11:06 AM, Todd - Work t...@fpdc.com wrote: This is an older single story 3 family side-by-side structure. The 13R system is being retrofitted. I believe (am confirming) that they have local hard wired smoke

Re: 13R local alarm

2013-05-29 Thread Mike Cabral
Using smoke detectors at first blush seems like a bad idea. A separate sounder that would indicate water flow in my view be a better choice. Many local jurisdictions require this and the intent is to notify occupants. The sounder Mike Henke noted has been a staple in the State of CA for years.

Re: 13R local alarm

2013-05-29 Thread Todd - Work
Tried that, George. Local FM wants 13R. I'm not sure these units have proper fire separation. Two of them built in the late 1940s and the 3rd one added in the 1960s. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On May 29, 2013, at 11:20 AM, George Church

13R local alarm

2013-05-29 Thread John Drucker
What's the purpose of these local alarms ?, to alert the dwelling unit occupants ? First and foremost is a fire alarm system required in this building in accordance with IBC 907 ? If so then a fire alarm system is required pursuant to IBC 907 and accordingly notification appliances in accordance

RE: Racks

2013-05-29 Thread Matthew J. Willis
Group A Plastics, with plastic pallets, encapsulation ESFR with pump... R/ Matt -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland Huggins Sent: Wednesday, May 29, 2013 11:07 AM To:

RE: 13R local alarm

2013-05-29 Thread Mike Henke
It may be possible to activate both the smoke alarms and a separate waterflow alarm. The flowswitch should have 2 sets of contacts. One switch can activate a local alarm such as the 120 vac mini horn The other switch may be able to activate the smoke alarms. This would provide the additional

RE: 13R local alarm

2013-05-29 Thread Tom Duross
We had a local town home rule go into effect 15+ years ago requiring sprinklers in anything 3+ units substantially renovated but it forgot to mention annunciation (also forgot water supply). Many slick property owners got together and sued and after the dust settled, it was decided to put an

Re: 13R local alarm

2013-05-29 Thread Todd - Work
The FM asked for the sprinkler alarms to be connected to ring the smoke detectors. I asked if a separate bell would be acceptable. The present system is essentially residential hard wired smokes. I'm not sure if all of the devices in each unit go off when one activates. There is no

RE: 13R local alarm

2013-05-29 Thread John Drucker - Home
Todd, How old are the smoke alarms ?, at 10 yrs. their due for replacement anyway. As I commented earlier, a prescriptive way to solve the issue. John Drucker, CET Fire Protection Subcode Official Fire / Building / Electrical Inspector New Jersey -Original Message- From:

Re: 13R local alarm

2013-05-29 Thread Todd - Work
My contract does not include alarms, only the sprinklers. It will be up to the owner and the FM to work that detail out. I have been asked to show a strobe outside and a local interior alarm on the drawing. My original post was asking for a specific product in a small, reasonably unobtrusive

RE: 13R local alarm

2013-05-29 Thread Steve Leyton
Last cycle, when we were discussing yet another proposal to require a mandatory local waterflow alarm in 13D, I asked out loud why it would be so difficult to do just as Todd's fire official directed, i.e. use the smoke detector loop as an audible network. And the answer is as simple as most of

Re: 13R local alarm

2013-05-29 Thread Ron Greenman
I don't think this is your problem. It's an alarm problem. You just need to provide a means to trigger an alarm. Hereabouts a normal is a fire alarm system in common areas with an attached peizo in each unit and local smoke alarms throughout the units. But I don't care about this as the sprinkie.

Re: 13R local alarm

2013-05-29 Thread George Church
Horn strobe? Sent from my iPhone On May 29, 2013, at 5:14 PM, Todd - Work t...@fpdc.com wrote: My contract does not include alarms, only the sprinklers. It will be up to the owner and the FM to work that detail out. I have been asked to show a strobe outside and a local interior alarm on

Re: FIre Alarm forum mail list

2013-05-29 Thread Ron Greenman
There's this: fireal...@yahoogroups.com It's sponsored by AFAA. http://www.afaa.org/ On Wed, May 29, 2013 at 6:04 PM, Phong - Indochine Engineering ph...@indoeng.com wrote: Dear All, This is the sprinkler forum, I wonder if there is a similar forum with mail list similar to this, for

13D local alarm

2013-05-29 Thread John Drucker
Steve, Absolutely valid idea to use the interconnected smoke alarms (ps the interconnect doesnt even have to be hardwired with the 2012 I-Codes) as alarm notification for a waterflow condition on 13D systems where a household fire alarm system is not required or provided. This is consistent

Re: 13R local alarm

2013-05-29 Thread Ron Greenman
My friend Mike pointed out he represents an equivalent peizo. So in the spirit of fairness. http://www.pottersignal.com/Fire/pdf/8850049_HP25T.pdf On Wed, May 29, 2013 at 5:28 PM, Ron Greenman rongreen...@gmail.com wrote: This seems ridiculous if here will be a fire alarm system as that will