We're not required to bring installations up to current codes every time
they change.
Seriously, are we going to be re-calculating 1970's-era pipe-scheduled dry
systems in nursing home attics to the higher pressures now required?
Replace ALL SR sprinklers in existing light hazard occupancies
It certainly does- it gives us the reference pointing out where the
structural engineer of record didn't follow the requirements of the IBC when
designing the steel- if and when we encounter that problem.
It's a perfect qualification to when the AE team attempts to place the onus
on us for
Sure, why use a couple hundred dollar bottle with a connected reserve and
low air alarm when a $25,000 N2 generator is available.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Wednesday,
Are you trying to size a pond without having the hose stream allowance in it;
Size the pump smaller, without the hose allowance?
A pond, insofar as #22 is concerned, is not a tank. However, I'm just a lowly
former alternate on 22, and this hasn't been processed as an official NFPA
Be better quality if you downloaded it off the AFSA website, download area.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
lamarvau...@charter.net
Sent: Tuesday, November 17, 2009 12:12 PM
To:
i.e., if your calc program doesn't give you the option for an end head
pressure and forces you to continue to think in area/density (and DOS?), use
a density derived from spacing and density to equal the minimum end head
pressure needed.
Let's say its K=25.2 end head pres of 25, and 100 sf
If it has a lid it can do a lot more than one class uptick
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Monday, November 16, 2009 10:14 AM
To: sprinklerforum@firesprinkler.org
I'll always wonder how someone actually installed a 6 main in a Wal-Mart
(retrofit into another dept store's vacant mall space) connected to the
bottom chord of joists that was just that wavy Z-purlin material. Didn't the
installers have a clue? Didn't the AHJ see it on the walk-thru? Owner's rep?
I believe a spkr drop penetration can drop thru a rated ceiling without
concern about being overly cautious on the patch- we're allowed the
escutcheon to cover the hole, and I don't know that there was a dimensional
restriction on the size of the penetration. Maybe use pie-pan (metallic)
Using the same logic, would that put a crimp on using CPVC, special
application heads, EC heads, interstitial heads, ESFR (obstructions can be
missed or added later), Attic heads, and anything else that's not
idiot-proof basic stuff from the good old days?
Sounds like threaded pipe and standard
I was waiting for the brothers Sornsin to chime in with waa waaa on the single
digits- but in Oct last year, the freezer going down was about the same as
outside, fitters were starting to talk huntin and ice fishin.
Amazingly, Fargo is a degree warmer than my PA right now. Snowing on Thom
So
It's not IF, it's WHEN
If what your planned course of action is makes you sick to your stomach,
then you need to change it and make sure the problem is identified to the
parties that CAN rectify it. If they don't, its no longer on you. But if it
burned, and someone died, could you live with
No UL/FM marks, year of mfr cast in body as reqd on listed valves, etc?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Wednesday, November 11, 2009 4:43 PM
To:
I'd ask em where in 13R it says you cannot do the individual risers, 13 or
13R or 13D. Short of a high rise needing zoning by floor (I think, we don't
encounter many) we use them in 13R and d all the time, and also did one in a
13 hotel, 4-story over parking garage with rental spaces on 1st that
could not isolate the floors in case of system impairment.
Dewayne
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George
Church
Sent: Tuesday, November 10, 2009 10:37 AM
To: sprinklerforum@firesprinkler.org
Is it March yet? BAF
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Tuesday, November 10, 2009 12:01 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: QR vs SSP sprinklers in LH vs OH
If its a house, then 13d criteria apply.
And you can avoid the 15 sec by swapping cost of dry valve with AF loop, exp
tank and solution. If this is in FL, wouldn't the AF be 10%/90%?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
That's excellent, Ed- Thank you.
USGS right on your screen, printable, for free.
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Vining
Sent: Monday, November 09, 2009 11:05 AM
To:
Sounds like an obstruction to spray.
Might be able to get the IBC exception to the spectator playing surface,
depending on how acrobatic the organist is.
Seriously- I'd call it a room if it is indeed a room full of pipes.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Friday, November 06, 2009 8:09 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Incompatible products with CPVC
I'll hope Top can either confirm
I'd double up on the detection if you're omitting AS in the area- if there's
the preponderance of wood construction I'm visualizing.
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent:
The question is compliance with the 1996 #13 change requiring QR heads in
light hazard occupancies. Since you have a change in use, I believe that you
could require that.
Course if the salespeople are selling groceries, wouldn't that still
constitute OH 2 mercantile since they're selling the same
There ya go, David- common sense and the code coinciding with your initial
reaction. I'd call it a day while you're ahead.
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday
The Chosen One-
well, Top, gotta admit it has a nice ring to it.
Maybe you'll get a Nobel Prize?
While I agree with Forrest, there are reasons why Top is the more likely
prospect- there may be input from the associations, but understand
initiatives take time to implement and may be hampered by
Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George
Church
Sent: Thursday, November 05, 2009 8:36 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Townhouse or Apartment Building
So here's a related question-
Can
You distracted him by waving your arms while typing, no doubt.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, November 05, 2009 1:55 PM
To: sprinklerforum@firesprinkler.org
me?
Steve Leyton
Protection Design Consulting
San Diego, CA
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George
Church
Sent: Thursday, November 05, 2009 11:11 AM
To: sprinklerforum@firesprinkler.org
Might remove the ALV if you've got elec alarms anyway, and a new riser check
might have less friction loss.
Also, calcs that can use a reduced MRA based on lower ceiling height might
help if you change to QR heads.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Dave makes a good point- it is generally NOT the intent of 13 to have us
calc'g pipe schedule- they'd be evaluated as pipe schedule.
If the larger water supply is not available for today's pipe schedule
system, I would- as you likely are- calc what's there as an alternative.
glc
-Original
with is knowledgeable and trustworthy from work at
a previous firm (that I mentioned in my first response). I cannot otherwise
vouch for the firm, but just got their e-newsletter and wanted to pass along
the resource.
George Church
Rowe Sprinkler
___
Sprinklerforum
-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday, November 02, 2009 7:24 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Incompatible products with CPVC
Certainly alternatives exist. However, how much
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Tuesday, November 03, 2009 7:50 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Incompatible products with CPVC
It was pretty seasonal, cathy won
KISS
Keep It Simple, Steve.
Like picking a 1/2 thread sprinkler to prevent foyer head from being mixed
with the 3/4 thread K7.9 EC in the middle of the hotel room.
Advantages and disadvantages- CPVC isn't going to have MIC problems, steel
isn't dry-fit (since FITS went by the wayside). Got to
I saw suggestions but no response-
What exactly is the ITM guy to do with the storz connection?
Pitot?
I guess they didn't read the part of the handbook where the FDC is a
supplement, not a replacement supply- 3- 5 storz to a 12 header?
Does the responding FD have enough oomph to pump in with
Actually, there is no need for the test header on a fire pump- IF you have
standpipe FHVs, hydrants or other means for testing the flow.
And with a flow meter installed, you only have to flow water and measure it
every -3 yrs? Sorry, I didn't commit #25 to memory, but its less than
annually.
IF
Splawn, CFPS
Jacobs
Fire Protection | Mechanical Engineering Dept.
513.674.3822
shannon.spl...@jacobs.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday, November 02, 2009 3:53 PM
Isn't Tommy Duross (FGOL) up your way?
Suggest the owner hire someone competent and fixing this might be as easy as
adjusting a mercoid. While you don't need much in the way of tools to do
this, it would be a knowledge thing. And there are folks in Boston who DO
know their way around a fire pump-
Along that line, Steve, I understand from a discussion with peers (50 of em,
not just our peer group) this Spring that the environmental stress frature
problem is being handled much better than initially.
This was probably THE hottest topic in that discussion - with some wanting
to remain quiet
I believe we're going way back before Spiro to the caste system in India.
Around the world in 80 days had an illustration of some of its pitfalls.
In this case, I'm referring to those that take 10 seconds to see the
pressure requirements for a new sprinkler, skip the installation guidelines
and
Welcome to the new residential world order- compared to some other options,
CPVC looks positively robust!
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Joe Burtell
Sent: Monday, November 02, 2009 5:33 PM
We run seminars for the local AHJs and tell em they can call and ask us
about something that sounds too good to be true, don't tell us the job, but
we'll caution what to watch for.
We were just discussing a competitor that was hanging 4 off toggles in
plaster metal lathe. Unless that's now
be close to the other George's booth I'm sure. Maurice is
giving a 2010 update plus free food.
Tom
3 points; churn, 100% and 150%.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday
Certainly alternatives exist. However, how much time and energy do you have
to track down and verify?
If you want to, you certainly can. However, the option now exists where you
can go to a website, see something that works, and use it. Do you pay a
premium for this? Maybe.
And yes, on mixed
Late last night the NAHB got the message that the IRC mandate for
residential sprinklers is here to stay. A wide cross-section of fire service
and sprinkler industry gathered in Baltimore to make sure if it came to a
floor vote, it would be for life safety- and it was- maybe 1,000 of us
filling
With just one cup of joe so far, I can only think that a false alarm due to
the compressibility of the air vrs water may result in the next
high-pressure surge encountered- IF it is of sufficient force to move the
paddle for the necessary time to go past the retard setting.
I wouldn't lose any
With the limited fire loading, you could ask if AHJ would agree to OH1
instead of II ?
And- what Dave said.
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry, David
Sent: Tuesday, October 27, 2009
I thinkn so long as your design doesn't resemble a grocery store from the
70's with a 1
grid that blows up when one extra head is flowed on a line, you're ok wit
what their intent was otherwise its pretty self-limiting and these guys
understand that.
And I think they're real busy since new
Other than 13 annexing some of 24 for leadins, those are rules for UG and
pumps, under 24 and 20, hence not really sprinkler systems a la 13, 13d,
13r, 13RT (retirees over tires)...
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Try Greg Garber at Pgh Tank and Tower (pitt...@cox.net) or Tank Industry
Consultants in Indiana- one of their principals, Gregory Stein, is on #22,
look in front cover.
There's a couple more, try AFSA NFPA NFSA directories under Tank
inspections.
glc
-Original Message-
From:
.
Especially since this probably wouldn't be realized until the acceptance
test when the client was ready to move into their new facility. Ouch!
Cliff
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
I got shot down in a high-rise on this; but there is an exception in IBC for
the playing surfaces in indoor arenas or similar things that may help-
But from an FPE point of view, there's no cooling of steel without the spkrs
throughout; just because there's no fire load doesn't mean the heat won't
I think the operative phrase is PRICELESS
Cliff gets bonus points for attending, too-
Don't know if he and Ron had a meet and greet.
Aero had numerous attendees that were probably sleep-deprived on the way
home :)
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
I can see where black steel pipe in the basement might be less than
desirable if connected to the rest of the plumbing, but a pair of
rubber-seated checks could address that at lower cost, and without the
friction loss of spring-loaded clappers inherent in a BFP.
As with so many of these
I've never seen any allowance for high piled storage to exceed 40,000
SF/system. You can go 40k hi-piled and another 12k SF of office, loading
dock (if you're persuasive), non- high-piled storage to the total of 52,000
Sf of system.
glc
-Original Message-
From:
-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Tuesday, October 20, 2009 8:11 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR - maximum system limit
I've never seen any allowance for high piled storage
Sam, you DID find it- it's 40k.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of sam b
Sent: Tuesday, October 20, 2009 1:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: ESFR - maximum system limit
And if there's already a megalug and/or thrust block on the 90 below,
they're superfluous code-wise. Only need 1 of the 3 methods of joint
restraint.
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
. 280.8591
mark.sorn...@ulteig.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Tuesday, October 20, 2009 1:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Retaining rod on UG
...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Tuesday, October 20, 2009 4:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Retaining rod on UG-tangent
Set screws?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:701. 280.8591
mark.sorn...@ulteig.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Tuesday, October 20, 2009 1:10 PM
I was just showing Ken and Ben your pics a little while ago- and you're much
handsomer than they thought. Probably because there was little leg showing
on someone next to you and they were distracted ;)
Which email address should I send it to- did u want to get in trouble at
home or at work?
don't want to release pricing publicly.
Thanks!
George Church
Rowe Sprinkler
g...@rowesprinkler.com
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical
Is it a calc program or a special application sprinkler :) ?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Splawn,
Shannon
Sent: Tuesday, October 13, 2009 10:11 AM
To: sprinklerforum@firesprinkler.org
Haven't had the error, but we've done flow tests on 2 drains.
Since the length of piping and # of fittings can vary on each main drain,
the discharge for each pressure point is VARIABLE.
However, what we've done to quickly get a flow test when we have a small
demand is to place a hose monster on
Rather than St Pete, I'm going to bet Roland will be in San Diego with the
rest of the AFSA Convention this coming week- where we'll discuss a lot more
than just this issue. If this particular item isn't covered in a seminar,
there'll be a dozen experts from Tyco and the other mfrs of heads, CPVC,
I'm not certain that a fire-rated enclosure is required, and its only just
in the 2008 that we added FRT tanks aboveground. The area with the tank must
be sprinklered to OH 2 min, higher if the area where the tank is needs a
higher density.
As for vendor selection, FREIGHT is a major item on
All I could visualize after writing that is Tommy D's FGOL pump test wagon-
look just like FD apparatus.
Actually, I was trying to point out to fix FRP tanks you just toss resin and
stuff on it, we didn't really paint it red. There isn't room in that
pump/tank room for a coat of paint on the
if there's no power.
George Church
Rowe Sprinkler
Alternate member of 22 (Emeritus)
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Randy Knutson
Sent: Friday, October 09, 2009 4:08 PM
To: sprinklerforum
Our installations could win a concours d'elegance?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ben Young
Sent: Friday, October 09, 2009 4:35 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Indoor
I think Tyco International used to be headquartered in a PO box in
Hamilton, Bermuda
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Thursday, October 08, 2009 10:37 AM
To:
That's why we belong to the Sprinkler Associations. The provide a good bit
of PR to aid our industry, in a far more efficient manner than any of us
could do it individually.
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Had two similar DPVs fail to operate, piston stck?
You obviously erred by installing this valve in an area with hard water.
I understand to successfully manage your risk of lawsuit, you should lube
the piston twice a year even if your customer pays for annual.
I didn't say I agree with this, BTW.
Hey, we in PA just left early 80's BOCA in April 2004.
And our SFM doesn't look at sprinklers -
Unless arson or a buried fuel storage tank is involved.
Our SFM is, however, coming out to MC a side-by-side burn next week at the
PennBOC annual convention in Harrisburg.
And this is where the
Firetech Engineering Incorporated
--- On Wed, 9/30/09, George Church for...@ptd.net wrote:
From: George Church for...@ptd.net
Subject: fatal fire from Combustible concelaed space ?
To: sprinklerforum@firesprinkler.org
Date: Wednesday, September 30, 2009, 5:17 PM
I'd ask the AHJ for HIS
It was in the first link, not the 2nd one.
And of course I put my 2cents in, too.
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brown, Mike
Sent: Thursday, October 01, 2009 2:57 PM
To:
...it was so old it disintegrated
I saw that one and Mike seems to be alluding to a link in his email
but for some reason it's not showing up.
On Thu, Oct 1, 2009 at 1:56 PM, George Church for...@ptd.net wrote:
It was in the first link, not the 2nd one.
And of course I put my 2cents in, too.
glc
There ya go beating up on CSC when that's a Grinnell Aquamatic.
I should find a central sprkr salesman to whoop yer butt. Know any?
These were fun - every week would alternate with a new procedure for setting
them up, followed by a yank of the approval, followed by a new procedure
Being over
http://www3.gendisasters.com/new-york/4265/white-plains,-ny-stouffer%2526%25
23039%3Bs-hotel-fire,-dec-1980
White Plains, NY Stouffer's Hotel Fire, Dec 1980
Posted January 3rd, 2008 by Stu Beitler
VICTIMS DIDN'T HAVE A CHANCE.
White Plains (AP) -- Business executives gathered for meetings at a
C'mon, Thom-
Not Central- Grinnell. AQUAMATIC. The ones with the pre-charge manifold.
They were competitors back then.
BT, when you're done with Ben, kick Thom.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
is that a few years ago I learned about 10% of the older
Residence Inns were unsprinklered, and they were being worked out of the
system. One of them is in Valley Forge, PA which my wife noticed before I
did, surprisingly enough.
George Church
Rowe Sprinkler
Marriott Gold Level ;) - support those
I don't know of any exception for the fitter grabbing the hanger
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Monday, September 28, 2009 3:46 PM
To: sprinklerforum@firesprinkler.org
Been tempting to ASK the AHJ to use all 30 days in the allotted review
process.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross
Sent: Monday, September 28, 2009 7:36 PM
To:
Wait a minute. Are you saying you found a dry system where the accelerator
is actually ON?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of ETHER BARLOW
Sent: Thursday, September 24, 2009 10:02 PM
To:
Friction losses vary tremendously between the two diameters; might want to
check the brand as well as just their usage. Calc big, install cheap.
Another field change that can blow a calc is a couple 90's on 1 drop to EC
heads, ESPECIALLY when its an OH2 occupancy. And the loss in a pair of 1
90's
Wouldn't fusible plugs been able to take care of the powerhouse??
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Friday, September 25, 2009 10:10 AM
To: sprinklerforum@firesprinkler.org
] On Behalf Of Ron Greenman
Sent: Friday, September 25, 2009 10:25 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Inadequte Water
You might have something there George but maybe sidewalls screwed into
the back wall. Pattern development after all.
On Fri, Sep 25, 2009 at 7:25 AM, George Church
! And then you went all PLUMBER on
us! Floor Flange indeed? You should have stuck with base of the riser
Apples and cabbage my friend.
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
George Church
And a flow test off
We faced a similar situation as we neared completion of design for an ESFR
box; water co noted a new tank was going on line in approx 3-6 months, and
would boost the pressure between 5 and 18 PSI.
Not knowing what it would go to, we switched from an electric pump to a
diesel with PLD to
I don't recall that one, but the Kmart DC fire in 1981 in Falls Twp, PA
burned to the ground from aerosols rocketing thru openings in fire walls
that were protected by water curtains instead of linked doors- or maybe the
doors didn't activate from the trace heat of residual aerosol rocket trail?
Or get acceptance of a water curtain with closed heads 6' o/c, .3/ft, calc #
hds along the length = to 1.2 x MRA?
Right or wrong, let them direct YOU in writing and I'd push for the water
curtain compared to the cost of the WS and the existence of mullions anyway.
Assume you're trying to redeem a
And I've seen where your firm does windows, too.
At last AFSA-San Diego hotel, creatively.
Must have been nice to have a showcase jobsite right out the window, right
behind the picketers.
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
An adjustment for lowest tank gradient is not only prudent, sound
engineering, it may stop the N word (negligence) from coming up at trial.
We ask the water purveyor for the tank level during the flow test and the
lowest level they reasonably anticipate where the tank low point is, and we
adjust
How about the system that dropped 45 PSI at our demand flow-
from when the FM flow test used as basis of calc and ordering 2500 GPM
diesel pump in 12~18 month time frame was performed till we did the
acceptance test? Pump worked great, but what happened to the city?
Eight flow tests later, and
We've had an instance where the water co bumped a PRV up a bit for us to
make a system work. Unusual, but we found a human.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Wednesday,
Bobby, you're right but-
That language is unenforceable, and inspectors aren't always competent to
recognize a a distinct hazard to life...
glc
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby
) 937.1852 | Cell (850) 554.3231
g...@livingwaterfp.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Tuesday, September 22, 2009 10:09 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Walk
If the Owner hires an idiot, he pays for that mistake- just as if I hire an
idiot or bank robber, I pay for it.
Naturally, those of us who get it will point out to a PE when he crosses
into the ludicrous- maybe even enjoying it. I was directed to test a DI
Preaction system with 200 PSI air in
Forest-
Nothing wrong with telling the Owner, just not on the Inspection Report.
Separate letter.
FE firm got what they deserved, I suppose- reinforced by trying to change
out just the bottoms of the dry pendents. That'll change the cost of the
changeout dramatically!
Good point you make about
Matt, you could quote both ways, and note that the electrically supervised
adds the central station monitoring for increased reliability and security;
you may have another dilemma if you're under the I-Codes, depending on when
system was installed and what was the prevailing building code. It's
or by calling Cherokee Fire Protection Co. at
888-347-3079 toll free.
-Original Message-
From: George Church for...@ptd.net
To: sprinklerforum@firesprinkler.org
Sent: Fri, 18 Sep 2009 11:55:48 -0400
Subject: RE: Chewable topic.Omegas
The liabilities we ITM contractors can inadvertently inherit