m-boun...@lists.firesprinkler.org] On
Behalf Of Ben Young
Sent: Wednesday, February 14, 2018 11:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Flammable and Combustible Liquid Storage
Check out the requirements in NFPA 45 for labs. This should tell you what the
hazard is based on the quanti
lists.firesprinkler.
> org] On Behalf Of Prahl, Craig/GVL
> Sent: Wednesday, February 14, 2018 10:56 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Flammable and Combustible Liquid Storage
>
> When the liquids are taken out of the cabinets, what is done with them?
> Is
0:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flammable and Combustible Liquid Storage
When the liquids are taken out of the cabinets, what is done with them? Is
there any dispensing going on within the area where they are stored?
Storing them in a cabinet may not drive the design cr
: sprinklerforum@lists.firesprinkler.org
Subject: Flammable and Combustible Liquid Storage [EXTERNAL]
IFC 2012 Table 5003.1.1 gives the maximum allowable quantities of flammable and
combustible liquids per control area. If the liquids are stored in approved
cabinets you can increase the volume by 100%.
I
|
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Fpdcdesign
Sent: Wednesday, February 14, 2018 10:04 AM
To: Sprinklerforum
Subject: Re: Flammable and Combustible Liquid Storage
What is the surrounding occupancy?
Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Reed A. Roisum, SET
> Sent: Wednesday, February 14, 2018 9:39 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Flammable and Combustible Liquid Storage
>
> IFC 2012 Table 5003.1.
Sent: Wednesday, February 14, 2018 9:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Flammable and Combustible Liquid Storage
IFC 2012 Table 5003.1.1 gives the maximum allowable quantities of flammable and
combustible liquids per control area. If the liquids are stored in approved
IFC 2012 Table 5003.1.1 gives the maximum allowable quantities of flammable and
combustible liquids per control area. If the liquids are stored in approved
cabinets you can increase the volume by 100%.
I am trying to determine the proper sprinkler design for areas that contain
flammable and co