RE: Shield for electrical equipment

2018-02-02 Thread Bob
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Phillips, Mark Sent: Friday, February 02, 2018 4:31 PM To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org Subject: Re: Shield for electrical equipment Bob Most cases it's only one or two lines in a small

Re: Shield for electrical equipment

2018-02-02 Thread Phillips, Mark
esident of Fire Protection, Kirlin Carolinas, LLC t: 919-526-1584 mphill...@jjkllc.com | http://www.kirlingroup.com Raleigh, NC 27617 Original message From: Bob Date: 2/2/18 6:23 PM (GMT-05:00) To: sprinklerforum@lists.firesprinkler.org Subject: RE: Shield for electrical equip

RE: Shield for electrical equipment

2018-02-02 Thread Bob
, Mark Sent: Friday, February 02, 2018 2:33 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Shield for electrical equipment Are we maybe describing drip pans under pipe in electrical room? Military jobs like this in their specs It's usually sheet metal bent into a u shape a

Re: Shield for electrical equipment

2018-02-02 Thread Phillips, Mark
forum@lists.firesprinkler.org Subject: Re: Shield for electrical equipment Peter, By 2019 ed. I assume you mean NEC? Best. Bruce Verhei On Feb 2, 2018, at 11:20, Matthew J Willis mailto:ma...@rapidfireinc.com>> wrote: Or.., what if it's the panel on fire?? Sent from my Verizon 4G LTE Droid O

Re: Shield for electrical equipment

2018-02-02 Thread Bruce Verhei
um-boun...@lists.firesprinkler.org] > On Behalf Of Matthew J Willis > Sent: Friday, February 2, 2018 1:40 PM > To: Forum ; b...@firebyknight.com > Subject: Re: Shield for electrical equipment > > I still sleeve pipe because I disagree with the shield allowance. To me it

RE: Shield for electrical equipment

2018-02-02 Thread Matthew J Willis
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matthew J Willis Sent: Friday, February 2, 2018 1:40 PM To: Forum ; b...@firebyknight.com Subject: Re: Shield for electrical equipment I still sleeve pipe because I disagree with the shield allowance. To me

RE: Shield for electrical equipment

2018-02-02 Thread Pete Schwab
This requirement has been removed in the 2019 edition. Peter Schwab VP of Purchasing and Engineering technologies Wayne Automatic Fire Sprinklers Inc. 222 Capitol Court Ocoee, Fl 34761 Mobile: (407) 468-8248 Direct: (407) 877-5570 Fax: (407) 656-8026 www.waynefire.com

RE: Shield for electrical equipment

2018-02-02 Thread Michael Goodis
illis Sent: Friday, February 2, 2018 1:40 PM To: Forum ; b...@firebyknight.com Subject: Re: Shield for electrical equipment I still sleeve pipe because I disagree with the shield allowance. To me it is an obstruction For your case, I would defer that to electrical folks as we do not know

Re: Shield for electrical equipment

2018-02-02 Thread Matthew J Willis
I still sleeve pipe because I disagree with the shield allowance. To me it is an obstruction For your case, I would defer that to electrical folks as we do not know their requirements per se. R Matt Sent from my Verizon 4G LTE Droid On Feb 2, 2018 11:36 AM, Bob wrote: Has anyone installed a hoo

RE: Shield for electrical equipment

2018-02-02 Thread Micah Davis, SET
Bob I've had to do it a few times. I usually get with the HVAC guys on the project and work with them to fabricate it. Simplest ones are like the drip pans they use for condensation on HVAC units. Definitely want to clear it with the electrical inspector first though to make sure he will acce