The Fitter makes good sense. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: Thursday, March 08, 2007 5:39 PM
To: [email protected]
Subject: Re: What I'm Hearing About Hydrostatic Testing

The owner may not care but the firefighters that were expecting the water at
the fire area would sure be disappointed.  If we are actually scared our
systems are going to blow-up during pressurization, like will normally
happen during firefighter response, then we are offering a false sense of
security by installing our systems.  I am not saying the official's
requirement is good or bad, but I think scare tactics are a bad idea.
Repeatedly stating we believe our system piping and fittings will explode
during simple pressurization of a system could really come back to bite us
all in the butt.
Say it was not part of the bid, say you want a disclaimer of liability as
part of your proposal for this "extra" work, but making nuances that a 20
year old system is somehow dangerous when pressurized should not be part of
this process.

Garth
a fitter
----- Original Message -----
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, March 08, 2007 2:22 PM
Subject: RE: What I'm Hearing About Hydrostatic Testing


That would depend on your point of view.  As an owner he may not care if
the cap blows off while the FD is pumping it up during a fire as mush as
he would if there was no emergency and someone just wanted a test
because they wanted to see what happens to the system.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brooks,
Bill
Sent: Thursday, March 08, 2007 2:19 PM
To: '[email protected]'
Subject: What I'm Hearing About Hydrostatic Testing

I'm concerned about the undertone of the discussions.  That is,
hydrostatic testing of existing systems will lead to unpredictable
results (things leaking and coming apart).

If this is the case, then we may have many very fragile systems out
there that shouldn't be in service in the first place.

Perhaps it's time to add a hydrostatic testing requirement to NFPA 25.
Isn't it better to find out the 6" cap comes off during the hydrostatic
test than to find out when the fire department pumps in during a fire?

Bill Brooks
Pittsburgh, PA

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of mail
Sent: Thursday, March 08, 2007 2:09 PM
To: [email protected]
Subject: RE: Hydrostatic testing recalled sprinkler heads


Because this building is a US Air Force building, I don't think it will
go to a code appeals process, but I can always ask.

We make a quote to change the heads and they issued a purchase order for
the heads and labor.  There is no contract language that I can rely on
in this case.  Their purchase order did not state a hydro test at 200
psi was a requirement.

Martin Campbell
List Member


At 11:54 AM 3/8/2007, you wrote:
>We call these folks "inventors" and they generally give us AHJ-types a
>bad reputation. I struggle to get folks to comply with the minimum
>standards, let alone invent new requirements!
>
>I think the technical code issues have been well addressed. My only
>recommendation to add - avoid turning this into a people problem (or
>one of those biological function contests). You have a code problem you

>need to resolve. You should have some recourse through a code appeals
>process or, inevitably, a court appearance. Agree to disagree with the
>AHJ and send it into the legal system.
>
>Jim Kettler
>Fire Marshal
>Buckingham, PA
>
>
>
>
> > > They cannot ask for whatever they want.  We have to get the
> > thought
> > > they can
> > > ask for whatever they want out of the industry.  They can only ask

> > > for what the law says they can ask for.
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to