I have too. But I have seen a few recently that aren't so I wanted to make sure I wasn't being a "legalist" again.
Thanks, Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack Sent: Saturday, June 16, 2007 12:38 PM To: [email protected] Subject: RE: warehouse offices If the wall separating the offices does not go fully to the deck, you don't have a concealed space. Therefore, I have always protected it. Travis -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Saturday, June 16, 2007 10:29 AM To: [email protected] Subject: warehouse offices I have seen this situation handled 3 ways and have my own opinion but would like to see what you all think. If you have an ordinary metal building warehouse with normal Ord Hazard Group II storage with an office area you often end up with space above the offices. In this case the offices will have lay in tile ceilings with insulation on top of the ceiling and no structure above the ceiling. Therefore there will never be storage on top of the offices. There is Approximately 14' of clear space above the offices of non combustible construction with no separation between the space above the offices and the warehouse. The offices represent approx. 30% of the total area of the building. Sprinklers will be installed under the ceiling of the offices. Do you protect above the offices completely? Do you protect 15' of the space from the warehouse side? Do you ignore it? Thanks, Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ NOD32 2335 (20070616) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)