You do NOT apply the 3,000 sf since that is a full 13 system requirement when you do not protect a required area (concealed combustible). 13R is an entire building system and the location of protection (not in concealed spaces) does not change based on in or out of the dwelling unit. Take a look at 13R:A.6.8.2.

Roland

On Jun 15, 2007, at 12:00 PM, Thom McMahon wrote:

Roland:

Having said that you don't apply all of 13, does that mean that in the 13 areas outside of the dwelling units you 1) Would 2) Would not apply the 3000 Sf design area for concealed combustible construction?

Thom McMahon