You do NOT apply the 3,000 sf since that is a full 13 system
requirement when you do not protect a required area (concealed
combustible). 13R is an entire building system and the location of
protection (not in concealed spaces) does not change based on in or
out of the dwelling unit. Take a look at 13R:A.6.8.2.
Roland
On Jun 15, 2007, at 12:00 PM, Thom McMahon wrote:
Roland:
Having said that you don't apply all of 13, does that mean that in
the 13 areas outside of the dwelling units you 1) Would 2) Would
not apply the 3000 Sf design area for concealed combustible
construction?
Thom McMahon
Firetech, Inc.