Roland:
Having said that you don't apply all of 13, does that mean that in the 13
areas outside of the dwelling units you 1) Would 2) Would not apply the 3000
Sf design area for concealed combustible construction?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Roland Huggins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, June 15, 2007 9:49 AM
Subject: Re: 13R RETIREMENT HOME
Other considerations aside (such as increased fire area as well as the
whole issue of mixed occupancies) let's say we are starting with a
building that a 13R system is acceptable. The answer is that you are
on the right path but 1500 sf is not the only answer. Outside the
dwelling unit (barring exceptions), you do have to follow 13 for the
discharge criteria ALONG WITH ITS MODIFIERS. Although not part of the
question allow me to say (due to extensive misunderstandings) that you do
not apply all of 13, ie locations such as concealed combustible spaces or
hose demand.
Roland
On Jun 14, 2007, at 3:03 PM, Bill Minkel wrote:
I have a two story retirement facility with dwelling unit wings and a
large
common area with kitchen, restaurant style seating, lobbies, activity
rooms,
etc. Am I correct in reading 13R 6.7.2.1 "Design Criteria - Outside
Dwelling
Unit" as essentially requiring me to do a 1500 sq. ft. calc for the most
remote portion of the common area? The conditions of 6.7.2.2 are not met
in
that many rooms exceed 500 sq. ft.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)