What that section is saying is that he can't take power for the jockey
pump out of the fire pump controller.  When he runs his main feeder into
the pump room he will have one circuit dedicated to the fire pump and
it's controller,  everything else in the space will be on a different
circuit or circuits.

Refer to NEC Article 695, FIRE PUMPS, specifically section 695.3.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, June 15, 2007 10:11 AM
To: [email protected]
Subject: jockey pump power

An electrician informed me this morning that the NEC requires him to
size his electrical feed for the fire pump and the jockey pump.

NFPA #20 states the following: 
10.3.4.8 Electrical supply conductors for pressure maintenance (jockey
or
make-up) pump(s) shall not be connected to the fire pump controller.

We are not electricians nor did we stay in a Holiday Inn Express last
night; but he wants to know where he is supposed to get his power from
for the Jockey Pump. Can he come off the feed from the transformer prior
to entering the Fire Pump Control Panel?

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to