Todd,

Yes, I just finished a biodiesel facility.  A straight EH2 approach doesn't
really cut it for the indoor storage of some of those liquids.  It depends a
lot on what sizes and arrangements of tanks you will have, where the
methanol is, whether the process is indoors or outside, etc.  Basically, the
biodiesel itself and raw oils such as cottonseed, palm, and corn oils are
class 3B liquids typically, but the methanol and sodium methoxide are the
nasty ones (class 1B).  Additionally, there is a point in the process
typically where the mixing has already occurred but enough free methanol can
still be present in the mixture to classify the entire vessel contents as
class 1B.  We used a closed head foam system indoors and an open head deluge
system over a separate methanol storage area.  I highly recommend foam for
this application versus just water at a high density as you initially
mentioned.  Feel free to give me a call or email if you would like to
discuss it in more detail.

Good luck,

Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
216 Seagate Avenue Unit B
Neptune Beach, FL 32266
904-652-4200 Phone
904-212-0868 Fax

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- work
Sent: Thursday, June 14, 2007 5:02 PM
To: [email protected]
Subject: Biodiesel mfg

I have been asked to look at some criteria for a small (2500 sqft) 
biodiesel processing facility. Someone (I'm not sure who) defined 
this as a Class !B flammable liquid and called for a 0.40 gpm/sqft 
density over the entire building area. While I'm not necessarily 
challenging this, I cannot find anything to verify it. NFPA 13 and 30 
seem to focus more on storage than processing. Has anyone else run 
into this yet?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to