The only time we were involved in anything resembling your situation we were
told by the Foam manufacturer to NOT use Galvanized piping and we were also
told the system would have to be recharged every 3-5 years.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Monday, February 11, 2008 3:40 PM
To: [email protected]
Subject: pre-primed foam system.

I am designing a foam system to be fed from a limited volume public 
water supply. NFPA 16 mentions a pre-primed foam system with 
significant decreases in demand. I spoke to someone who knows foam 
and he said that the system is filled with the foam-water mixture 
instead of just water (and the foam mixed in at the riser). The 
biggest problem being that the mixture breaks down over time, so it 
ends up as pretty much dirty water. My questions are this: Has anyone 
worked with this type of system before? I was thinking recommending a 
three year pre-priming schedule, does this make sense? If the pipe is 
going to contain a mixture full-time, should it be galvanized? The 
difference in using could be  the difference between a pump and tank 
for a 12,000 sqft warehouse.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to