I did a couple of them about 15 years ago.  As I remember (always
suspect) the criteria was .16/1500 with 250 hose.  Essentially all you
need to do to refresh the solution is drain the system and refill.  With
MIC now running rampant, this may be an invitation to a different
problem though.  Galvanized is a no no with most AFFF solutions. 


B K

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Monday, February 11, 2008 4:40 PM
To: sprinklerforum@firesprinkler.org
Subject: pre-primed foam system.

I am designing a foam system to be fed from a limited volume public
water supply. NFPA 16 mentions a pre-primed foam system with significant
decreases in demand. I spoke to someone who knows foam and he said that
the system is filled with the foam-water mixture instead of just water
(and the foam mixed in at the riser). The biggest problem being that the
mixture breaks down over time, so it ends up as pretty much dirty water.
My questions are this: Has anyone worked with this type of system
before? I was thinking recommending a three year pre-priming schedule,
does this make sense? If the pipe is going to contain a mixture
full-time, should it be galvanized? The difference in using could be
the difference between a pump and tank for a 12,000 sqft warehouse.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to