CAF would be a good option (an industry friend from IL also suggested
this), but this, like most jobs has a history. The company in
question hired a contractor (and client of mine) to install rack
sprinklers in their warehouse to accommodate the new rack
arrangement, based on what was there. When I was brought in, I asked
'what was going to be stored?'; that is when the feces hit the fan.
This company has neither policy nor insurance company input regarding
storage of flammables. I had to start from scratch to figure out what
was needed. Among other things, we have had them remove the 40-50 275
gallon PVC totes of class III liquids from the building. Since this
is mid-project and the contractor involved is familiar with
foam-water systems, that was the natural choice for this project. The
totes have to go somewhere and the CAF might be a good option for that storage.
At 09:27 PM 2/11/2008, you wrote:
Todd,
What about CAF?
On 2/11/08, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote:
> I will confess that I have never done a High-X system, but with the
> relative small size of the building, the racking and the arrangement
> of exits, I would be concerned from a life-safety standpoint about
> it. If we use the pre-primed design, we would be OK with the water
> supply. With the standard arrangement, we are right at the maximum
> point that the water company will allow.
>
>
> At 06:41 PM 2/11/2008, you wrote:
> >Have you considered High-X foam if your water supply is challenged?
> >
> >Thom McMahon
> >Firetech, Inc.
> >2560 Copper Ridge Dr
> >Steamboat Springs, CO 80488-2136
> >Tel: 970-879-7952
> >Fax: 970-879-7926
> >----- Original Message ----- From: "Todd Williams - FPDC" <[EMAIL PROTECTED]>
> >To: <[email protected]>
> >Sent: Monday, February 11, 2008 3:48 PM
> >Subject: RE: pre-primed foam system.
> >
> >
> >>Chemical storage warehouse.
> >>
> >>At 04:53 PM 2/11/2008, you wrote:
> >>>Check with your foam supplier on the life of the foam. Not all will
> >>>last 3 years and life span can depend on the water quality too.
> >>>
> >>>Again check with the supplier on the galvanized. Some of the foams
> >>>react with Galvanized at certain concentration levels. Usually it's not
> >>>a problem for foam-water systems as the foam isn't in the pipe for a
> >>>long duration of time.
> >>>
> >>>Also don't forget to check about containment. In some jurisdictions this
> >>>type of discharge has to be contained and removed as hazardous waste.
> >>>
> >>>What are you trying to protect?
> >>>
> >>>
> >>>Craig L. Prahl, CET
> >>>Fire Protection Group
> >>>Mechanical Department
> >>>CH2MHILL
> >>>Lockwood Greene
> >>>1500 International Drive
> >>>PO Box 491, Spartanburg, SC 29304-0491
> >>>Direct - 864.599.4102
> >>>Fax - 864.599.8439
> >>>[EMAIL PROTECTED]
> >>>http://www.lg.com
> >>>
> >>>
> >>>-----Original Message-----
> >>>From: [EMAIL PROTECTED]
> >>>[mailto:[EMAIL PROTECTED] On Behalf Of Todd
> >>>Williams - FPDC
> >>>Sent: Monday, February 11, 2008 4:40 PM
> >>>To: [email protected]
> >>>Subject: pre-primed foam system.
> >>>
> >>>I am designing a foam system to be fed from a limited volume public
> >>>water supply. NFPA 16 mentions a pre-primed foam system with significant
> >>>decreases in demand. I spoke to someone who knows foam and he said that
> >>>the system is filled with the foam-water mixture instead of just water
> >>>(and the foam mixed in at the riser). The biggest problem being that the
> >>>mixture breaks down over time, so it ends up as pretty much dirty water.
> >>>My questions are this: Has anyone worked with this type of system
> >>>before? I was thinking recommending a three year pre-priming schedule,
> >>>does this make sense? If the pipe is going to contain a mixture
> >>>full-time, should it be galvanized? The difference in using could be
> >>>the difference between a pump and tank for a 12,000 sqft warehouse.
> >>>
> >>>Todd G. Williams, PE
> >>>Fire Protection Design/Consulting
> >>>Stonington, Connecticut
> >>>www.fpdc.com
> >>>860.535.2080
> >>>_______________________________________________
> >>>Sprinklerforum mailing list
> >>>[email protected]
> >>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>>To Unsubscribe, send an email
> >>>to:[EMAIL PROTECTED]
> >>>(Put the word unsubscribe in the subject field)
> >>>_______________________________________________
> >>>Sprinklerforum mailing list
> >>>[email protected]
> >>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> >>>(Put the word unsubscribe in the subject field)
> >>Todd G. Williams, PE
> >>Fire Protection Design/Consulting
> >>Stonington, Connecticut
> >>www.fpdc.com
> >>860.535.2080
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>[email protected]
> >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >>(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting