When doing vertical turbine calcs, I have given my pump a dummy source, such as a 5 foot long 10" diameter pipe and then run this through the pump curve in the calculation software. My source is zero pressure and flow so all pressure and flow at the discharge of the pump is a result of the pump curve that I input.
Keep in mind that your pump discharge elevation is actually at about the top of the bowls. What looks like the "discharge flange" for a vertical turbine pump is actually just a 90 degree turn for where the water enters your piping above your tank or reservoir. I believe the rated capacity of vertical turbine pumps is assuming a drained tank with the water level just above the bowls; so, if your water level is any higher than this, you will have a higher discharge pressure than shown on the pump rating. Justin D. Reid, P.E. Project Engineer RLH Fire Protection 3430 Unicorn Road Bakersfield, CA 93308 Office: (661) 410-1350 Cell: (213) 798-0251 Fax: (661) 322-6816 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dyce Geoffrey H. Sent: Thursday, February 28, 2008 12:56 PM To: [email protected] Subject: (no subject) I am becoming very lazy in my old age and should know this answer. Using a vertical shaft pump, is it acceptable to begin my calcs at the pump discharge. For example...a 1000 gpm pump at 100 lbs. My source node will be 1000 at 100 psi. Any problem doing this?? Thanks in advance. Geoffrey H. Dyce Sales Manager Industrial Fire & Safety 12075-34th St N, Unit A St. Petersburg, Fl 33716 Ph: 727-573-1556 Fx: 727-572-7266 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)