What is the state of the canola, oil or meal?

Get an MSDS on the material then it's a matter of the occupancy
classification and construction type based on the building code that
will determine what is required.  You also need to know how much of the
material is in the building and stored if in fact it turns out to be
anything significant.

Canola oil has a very high flash point, over 500 deg (F), with some
warning against water as an extinguishing agent.  But you need to know
exactly what you're dealing with. 


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Robert
Sent: Wednesday, May 28, 2008 5:07 PM
To: [email protected]
Subject: (no subject)

I have a canola crushing facility that uses no solvents in the
extraction
process.   Any ideas on the hazard classification?  NFPA 36 is for
solvent
based extraction.
I say that the delivery and load out areas should also be protected.
as
well as the cooling tower and storage tanks.    They say let it burn.

Thank you
 Robert  Thompson 

 DAKOTA
FIRE PROTECTION
1710 N. Washington Street
Grand Forks ND 58206-5327
Phone # (701) 772-8820
Fax # (701) 772-7932
Email [EMAIL PROTECTED] 

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to