If it's Class III and there are 1-1/2" hose stations, then I would say the water supply should be automatic and satisfy the demand of the Class II connections. But the standard doesn't do an adequate job of explaining how to design the water supply if the exception is taken for fully sprinklered buildings and there aren't any hose stations. If it's a Class III that looks like a Class I with 2-1/2" x 1-1/2" reducers at the hose connections, then I think you're okay with a manual-wet system, because those connections are intended to be used by trained responders.
Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Parsley Consulting Sent: Saturday, March 01, 2008 12:16 PM To: [email protected] Subject: Never a dumb question Tom, If these are truly class III standpipes by the definition in NFPA-14, then they are required by automatic wet systems unless they're subject to freezing, per 5.4.3. I think your conclusions is correct, they've sized the pump incorrectly if the standpipe isn't dry. My only word of caution was your comment that the standpipes aren't manual if they're connected to an automatic water supply. Manual wet standpipes are connected to an automatic water supply, but that supply isn't capable of providing the demand for standpipes. Several NFPA-14 references suggest that this could be accomplished by a combined standpipe sized and calc'd only for the sprinkler system demand. Just my thoughts. Ken Wagoner San Diego, CA Tom Duross wrote: > Todd, I'm very familiar with that section BUT these are not manual > standpipes if they're connected to an automatic water supply. If they were > separate, OK I can see the justification but they're not. They're connected > to the same supply as the sprinklers and the fire (sprinkler) pump. My > understanding of that section says if I have enough street pressure to > satisfy the sprinklers, I don't have to install a pump just for the hose > demand (only class 3 in MA). But, these guys designed and installed a fire > pump connected to two combination class 3 standpipes and only sized it for > the sprinklers. I don't think that's right. > > Tom _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)