Tom:

Does the building have 1-1/2" hose stations or not?  I don't mean to
over-simplify, but if not, a wet-manual Class I system is acceptable
unless the local (or state) building code calls for something more.  The
pump sized for the sprinklers is okay so long as the path from the FDC
to the remote outlets calc's out based on whatever inlet pressure the
responding fire department specifies.

Steve Leyton
Protection Design & Consulting

The foregoing is my opinion only and is not intended to represent the
Technical Committee on Standpipe Systems, nor serve as an interpretation
of NFPA 14.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Saturday, March 01, 2008 5:28 PM
To: [email protected]
Subject: RE: Dumb Question maybe

I agree Ron but don't think this applies here.
It has sufficient capacity, just a pump that's been sized too small.
6" underground, 6" supply main to (2) 4" standpipes, wtf.
Sorry Campers, but this really bothered me.  (Not nearly like the
Superbowl
though..)
It's the second system like this I've been asked to test in the past
year.
I mentioned it to the Inspectors but it fell on deaf ears.

Tom

Tom,

NFPA 14, 2007

5.2.5* Manual Wet. A manual wet standpipe system shall be a wet
standpipe system connected  to a small water supply for the purpose of
maintaining water within the system or sharing a water supply with an
automatic sprinkler system, but not having a water supply capable of
delivering the system demand attached to the system.

On 3/1/08, Tom Duross <[EMAIL PROTECTED]> wrote:
>
>  Tom,
>
>  The Mass Code is confusing on this issue. Section 914.1 states that
>  when standpipes are required to be installed, they shall be automatic
>  wet type. This would mean that they would need to meet the flow and
>  pressure demands with the on site supply. However, section 914.3
>  Exception states that the residual pressures are not required to met
>  if the building is under 70 feet high, effectively making it a manual
>  wet standpipe. I think an interpretation may be in order.
>
>  Todd
>
>  Todd, I'm very familiar with that section BUT these are not manual
>  standpipes if they're connected to an automatic water supply.  If
they
were
>  separate, OK I can see the justification but they're not.  They're
connected
>  to the same supply as the sprinklers and the fire (sprinkler) pump.
My
>  understanding of that section says if I have enough street pressure
to
>  satisfy the sprinklers, I don't have to install a pump just for the
hose
>  demand (only class 3 in MA).  But, these guys designed and installed
a
fire
>  pump connected to two combination class 3 standpipes and only sized
it
for
>  the sprinklers.  I don't think that's right.
>
>  Tom
>
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to