No, 2 1/2" angle valves with 1 1/2" reducers. 5 sty., 56' sidewalk to parapet Steve. Mixed use.
Tom: Does the building have 1-1/2" hose stations or not? I don't mean to over-simplify, but if not, a wet-manual Class I system is acceptable unless the local (or state) building code calls for something more. The pump sized for the sprinklers is okay so long as the path from the FDC to the remote outlets calc's out based on whatever inlet pressure the responding fire department specifies. Steve Leyton Protection Design & Consulting The foregoing is my opinion only and is not intended to represent the Technical Committee on Standpipe Systems, nor serve as an interpretation of NFPA 14. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)