Tom, I know you said in your first post but I've lost that part of the thread--Is this a high rise by your jurisdiction's definition. Out this way if 3 plus stories but under 75' this always works fine. Over 75' and we're highrise and the standpipe becomes automatic no matter what class.
On Sat, Mar 1, 2008 at 5:28 PM, Tom Duross <[EMAIL PROTECTED]> wrote: > I agree Ron but don't think this applies here. > It has sufficient capacity, just a pump that's been sized too small. > 6" underground, 6" supply main to (2) 4" standpipes, wtf. > Sorry Campers, but this really bothered me. (Not nearly like the > Superbowl > though..) > It's the second system like this I've been asked to test in the past year. > I mentioned it to the Inspectors but it fell on deaf ears. > > Tom > > Tom, > > NFPA 14, 2007 > > 5.2.5* Manual Wet. A manual wet standpipe system shall be a wet > standpipe system connected to a small water supply for the purpose of > maintaining water within the system or sharing a water supply with an > automatic sprinkler system, but not having a water supply capable of > delivering the system demand attached to the system. > > On 3/1/08, Tom Duross <[EMAIL PROTECTED]> wrote: > > > > Tom, > > > > The Mass Code is confusing on this issue. Section 914.1 states that > > when standpipes are required to be installed, they shall be automatic > > wet type. This would mean that they would need to meet the flow and > > pressure demands with the on site supply. However, section 914.3 > > Exception states that the residual pressures are not required to met > > if the building is under 70 feet high, effectively making it a manual > > wet standpipe. I think an interpretation may be in order. > > > > Todd > > > > Todd, I'm very familiar with that section BUT these are not manual > > standpipes if they're connected to an automatic water supply. If they > were > > separate, OK I can see the justification but they're not. They're > connected > > to the same supply as the sprinklers and the fire (sprinkler) pump. My > > understanding of that section says if I have enough street pressure to > > satisfy the sprinklers, I don't have to install a pump just for the > hose > > demand (only class 3 in MA). But, these guys designed and installed a > fire > > pump connected to two combination class 3 standpipes and only sized it > for > > the sprinklers. I don't think that's right. > > > > Tom > > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)