Tom,
I know you said in your first post but I've lost that part of the thread--Is
this a high rise by your jurisdiction's definition. Out this way if 3 plus
stories but under 75' this always works fine. Over 75' and we're highrise
and the standpipe becomes automatic no matter what class.

On Sat, Mar 1, 2008 at 5:28 PM, Tom Duross <[EMAIL PROTECTED]> wrote:

> I agree Ron but don't think this applies here.
> It has sufficient capacity, just a pump that's been sized too small.
> 6" underground, 6" supply main to (2) 4" standpipes, wtf.
> Sorry Campers, but this really bothered me.  (Not nearly like the
> Superbowl
> though..)
> It's the second system like this I've been asked to test in the past year.
> I mentioned it to the Inspectors but it fell on deaf ears.
>
> Tom
>
> Tom,
>
> NFPA 14, 2007
>
> 5.2.5* Manual Wet. A manual wet standpipe system shall be a wet
> standpipe system connected  to a small water supply for the purpose of
> maintaining water within the system or sharing a water supply with an
> automatic sprinkler system, but not having a water supply capable of
> delivering the system demand attached to the system.
>
> On 3/1/08, Tom Duross <[EMAIL PROTECTED]> wrote:
> >
> >  Tom,
> >
> >  The Mass Code is confusing on this issue. Section 914.1 states that
> >  when standpipes are required to be installed, they shall be automatic
> >  wet type. This would mean that they would need to meet the flow and
> >  pressure demands with the on site supply. However, section 914.3
> >  Exception states that the residual pressures are not required to met
> >  if the building is under 70 feet high, effectively making it a manual
> >  wet standpipe. I think an interpretation may be in order.
> >
> >  Todd
> >
> >  Todd, I'm very familiar with that section BUT these are not manual
> >  standpipes if they're connected to an automatic water supply.  If they
> were
> >  separate, OK I can see the justification but they're not.  They're
> connected
> >  to the same supply as the sprinklers and the fire (sprinkler) pump.  My
> >  understanding of that section says if I have enough street pressure to
> >  satisfy the sprinklers, I don't have to install a pump just for the
> hose
> >  demand (only class 3 in MA).  But, these guys designed and installed a
> fire
> >  pump connected to two combination class 3 standpipes and only sized it
> for
> >  the sprinklers.  I don't think that's right.
> >
> >  Tom
> >
> >
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to