It seems like sections 914.1 and 914.3 are a just a round -about way of establishing the definition of a high-rise as 70 feet in Massachusetts for the purpose of applying the standpipe requirements.
Are Class III standpipes usually not required when a building is fully sprinklered? So are we talking about a Class III system or a Class I? An automatic water supply feels better because it is better. There are a lot of bells and whistles that come along with a high-rise and an automatic water supply for a Class I standpipe system is one of them. The line has to be drawn somewhere and in this case it has been drawn at a building that is 70 feet according to Section 914.3. Since this building is less than 70 feet, the owner has the option to not provide the automatic water supply if they choose not to expend the additional cost. Justin D. Reid, P.E. Project Engineer RLH Fire Protection 3430 Unicorn Road Bakersfield, CA 93308 Office: (661) 410-1350 Cell: (213) 798-0251 Fax: (661) 322-6816 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Saturday, March 01, 2008 11:31 AM To: [email protected] Subject: RE: Dumb Question maybe Tom, The Mass Code is confusing on this issue. Section 914.1 states that when standpipes are required to be installed, they shall be automatic wet type. This would mean that they would need to meet the flow and pressure demands with the on site supply. However, section 914.3 Exception states that the residual pressures are not required to met if the building is under 70 feet high, effectively making it a manual wet standpipe. I think an interpretation may be in order. Todd Todd, I'm very familiar with that section BUT these are not manual standpipes if they're connected to an automatic water supply. If they were separate, OK I can see the justification but they're not. They're connected to the same supply as the sprinklers and the fire (sprinkler) pump. My understanding of that section says if I have enough street pressure to satisfy the sprinklers, I don't have to install a pump just for the hose demand (only class 3 in MA). But, these guys designed and installed a fire pump connected to two combination class 3 standpipes and only sized it for the sprinklers. I don't think that's right. Tom _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)