It seems like sections 914.1 and 914.3 are a just a round -about way of
establishing the definition of a high-rise as 70 feet in Massachusetts
for the purpose of applying the standpipe requirements.

Are Class III standpipes usually not required when a building is fully
sprinklered? So are we talking about a Class III system or a Class I?

An automatic water supply feels better because it is better. There are a
lot of bells and whistles that come along with a high-rise and an
automatic water supply for a Class I standpipe system is one of them.
The line has to be drawn somewhere and in this case it has been drawn at
a building that is 70 feet according to Section 914.3. Since this
building is less than 70 feet, the owner has the option to not provide
the automatic water supply if they choose not to expend the additional
cost. 

Justin D. Reid, P.E.
Project Engineer
RLH Fire Protection 
3430 Unicorn Road
Bakersfield, CA 93308
Office: (661) 410-1350
Cell: (213) 798-0251
Fax: (661) 322-6816
[EMAIL PROTECTED] 
 

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Saturday, March 01, 2008 11:31 AM
To: [email protected]
Subject: RE: Dumb Question maybe


Tom,

The Mass Code is confusing on this issue. Section 914.1 states that
when standpipes are required to be installed, they shall be automatic
wet type. This would mean that they would need to meet the flow and
pressure demands with the on site supply. However, section 914.3
Exception states that the residual pressures are not required to met
if the building is under 70 feet high, effectively making it a manual
wet standpipe. I think an interpretation may be in order.

Todd

Todd, I'm very familiar with that section BUT these are not manual
standpipes if they're connected to an automatic water supply.  If they
were
separate, OK I can see the justification but they're not.  They're
connected
to the same supply as the sprinklers and the fire (sprinkler) pump.  My
understanding of that section says if I have enough street pressure to
satisfy the sprinklers, I don't have to install a pump just for the hose
demand (only class 3 in MA).  But, these guys designed and installed a
fire
pump connected to two combination class 3 standpipes and only sized it
for
the sprinklers.  I don't think that's right.

Tom


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to