IFC 903.1.1 Alternative protection. Alternative automatic fire-extinguishing 
systems complying with Section 904 shall be permitted in lieu of automatic 
sprinkler protection where recognized by the applicable standard and approved 
by the fire code official.


Travis Ripley
Fire Prevention Officer
Bellevue Fire Department
Ph. 425-452-6042
[EMAIL PROTECTED]



-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez
Sent: Tuesday, April 08, 2008 9:19 AM
To: [email protected]
Subject: RE: fm200 vs sprinkerls

Doesn't the "equivalency" clause in beginning of NFPA 13 allow the use
of other type systems?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Tuesday, April 08, 2008 11:11 AM
To: [email protected]
Subject: fm200 vs sprinkerls

We have done multiple projects in which the server rooms have been
protected with FM200 systems and had no sprinklers.
We now have a bldg like this in which the AHJ is stating that a room
with FM200 is not exempted from NFPA 13's requirement to be protected
throughout and therefore must have both FM200 and sprinklers.

Is this a true statement in you other AHJ's eyes?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Monday, April 07, 2008 6:48 AM
To: [email protected]
Subject: Fitter Question

Maybe more suited for chat but I'll throw it out here.

I need to get an in-place groover for an upcoming job.
I've borrowed a friends rigid before but it's gone.
Can any fitters share their likes and dislikes?
Rigid vs. Reed, or others...

I wish they made one for a 700 as I have to groove old 4" and 6" sch.
40.
I've got to cut-in about 12 FCV's 8-10' in the air.
All recommendations and advice accepted.
(I don't like roustabouts)

Tom
GRS
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to