NFPA does allow it.

Take a look at Life Safety Code (2000 Edition) 9.7.3.1

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Tuesday, April 08, 2008 11:23 AM
To: [email protected]
Subject: Re: fm200 vs sprinkerls

Gregg,

I'm not an AHJ although I do train them on occasion. My interpretation  
is that the sprinkler system is general protection for the building  
and that the wonder gas d'jour is equipment protection (hence special  
hazard in an otherwise general building environment) therefore the  
sprinklers are required by building code and NFPA 13. Unless amended  
all building codes I'm familiar with reference NFPA 13 for sprinkler  
coverage if the building occupancy, type and size requires sprinklers.  
NFPA states sprinklered throughout with no proviso for alternatives.
On Apr 8, 2008, at 9:10 AM, Greg McGahan wrote:

> We have done multiple projects in which the server rooms have been  
> protected
> with FM200 systems and had no sprinklers.
> We now have a bldg like this in which the AHJ is stating that a room  
> with
> FM200 is not exempted from NFPA 13's requirement to be protected  
> throughout
> and therefore must have both FM200 and sprinklers.
>
> Is this a true statement in you other AHJ's eyes?
>
> Thank you,
> Greg McGahan
>
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Tom  
> Duross
> Sent: Monday, April 07, 2008 6:48 AM
> To: [email protected]
> Subject: Fitter Question
>
> Maybe more suited for chat but I'll throw it out here.
>
> I need to get an in-place groover for an upcoming job.
> I've borrowed a friends rigid before but it's gone.
> Can any fitters share their likes and dislikes?
> Rigid vs. Reed, or others...
>
> I wish they made one for a 700 as I have to groove old 4" and 6"  
> sch. 40.
> I've got to cut-in about 12 FCV's 8-10' in the air.
> All recommendations and advice accepted.
> (I don't like roustabouts)
>
> Tom
> GRS
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

Ron Greenman
...at home





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to