OK, if there is no container and it's just the cups shrinked wrapped I
would have to consider that UNSTABLE, which weird as it is, would put in
in that Column "A"  with the lesser density.  Is it even rigid enough to
stack 18ft high?


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, April 10, 2008 4:47 PM
To: [email protected]
Subject: RE: FM Density for Group A nonexpanded exposed solid pile

Thanks, Craig,

That's what I came up with also. I guess FM favorable is the same as
NFPA Column A. 

The storage arrangement is 40 oz. cups stacked inside each other 4 ft
high on a pallet, shrink wrapped on four sides with a single layer of
cardboard over the top.

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 10, 2008 1:35 PM
To: [email protected]
Subject: RE: FM Density for Group A nonexpanded exposed solid pile

Per Decision Tree 15.2.1: Group A, nonexpanded, stable, exposed leads to
Table 15.2.5(a), Column E, 20 ft storage ht, >30 - 35 ft roof/ceiling
height takes you to 1.1/2500, and .85 @ 15 ft.  Per 15.2.8 you can
interpolate based on storage height so at 18ft of storage you'd be at
1.0/2500.  Plus 500 gpm hose.

But also and depending on how the stuff is contained on the pallet you
may be able to go to Column A @ the 0.6 at 20ft and interpolate that to
.54/2500 at 18ft.  Need to verify how the stuff is packaged onto the
pallets per the definition of Solid Unit Load in NFPA 13.


For ESFR 14K @ 75psi down to 25.2K @ 20psi or anything in between per
Table 15.4.1


Alright, back to business, everybody man your BUCKETS!!!!!!!!



Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, April 10, 2008 3:45 PM
To: [email protected]
Subject: FM Density for Group A nonexpanded exposed solid pile

Sorry to interupt the bucket brigade but what say the forum for 18 ft.
palletized storage in a 35 ft. bldg? I find .6/2500 for favorable
factors and it sends you in a circle for no favorable factors. NFPA is
1.1/2500 or ESFR. Something doesn't compute (probably me).

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to