Dan, The code (IBC/IFC) trumps the standard (NFPA-13), thus electrical supervision is required.
John Drucker Fire Protection Subcode Official (AHJ) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of danarbel Sent: Tuesday, June 10, 2008 2:10 AM To: [email protected] Subject: Valve Supervision Dear all Confusion about electrical supervision of sprinkler control valves: According to NFPA 13, it is sufficient to chain lock the sprinkler control valves. I.E. no requirement to monitor the position of the valves. Other NFPA codes such as 101 and 5000, require such supervision in storage areas. IFC 2006 903.4 requires valves to be electrically supervised. I would appreciate your opinions Dan Arbel No virus found in this outgoing message. Checked by AVG. Version: 7.5.524 / Virus Database: 270.0.0/1490 - Release Date: 08-Jun-08 5:32 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)