Assuming you are in a part of the world applying US codes and  
standards, as already stated the IBC requires NFPA 13 systems to be  
electrically monitored (over 20 sprinklers that is).  The next  
question that comes to mind is what about when other factors drive  
installing sprinklers and the IBC does not require them?  The IBC  
states they too must comply with the code so must be electrically  
supervised.

Roland

On Jun 9, 2008, at 11:09 PM, danarbel wrote:

> Dear all
>
> Confusion about electrical supervision of sprinkler control valves:
>
> According to NFPA 13, it is sufficient to chain lock the sprinkler  
> control
> valves.
>
> I.E. no requirement to monitor the position of the valves.
>
> Other NFPA codes such as 101 and 5000, require such supervision in  
> storage
> areas.
>
> IFC 2006 903.4 requires valves to be electrically supervised.
>
> I would appreciate your opinions
>
> Dan Arbel
>
>
>
>
> No virus found in this outgoing message.
> Checked by AVG.
> Version: 7.5.524 / Virus Database: 270.0.0/1490 - Release Date: 08- 
> Jun-08
> 5:32 PM
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 270.2.0/1493 - Release Date: 09-Jun-08
5:25 PM
 

No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 270.2.0/1493 - Release Date: 09-Jun-08
5:25 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to