Here in Seattle we apply the requirements from the Fire Code edition that was 
applicable when the building was originally constructed or substantially 
renovated.  Early fire codes had no electrical monitoring requirement thus 
there are many old sprinklered buildings with no electrical monitoring to this 
day.  The Uniform Code for many years triggered electrical monitoring when the 
system had 100 heads or more and the IFC triggers monitoring at 20 heads.  

We are not going back to the UBC buildings that had less than 100 heads and 
retroactively requiring monitoring.

Rich Richardson
Seattle Fire Department

>>> "danarbel" <[EMAIL PROTECTED]> 06/09/08 11:09 PM >>>
Dear all

Confusion about electrical supervision of sprinkler control valves: 

According to NFPA 13, it is sufficient to chain lock the sprinkler control
valves. 

I.E. no requirement to monitor the position of the valves. 

Other NFPA codes such as 101 and 5000, require such supervision in storage
areas. 

IFC 2006 903.4 requires valves to be electrically supervised. 

I would appreciate your opinions

Dan Arbel




No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 270.0.0/1490 - Release Date: 08-Jun-08
5:32 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 

To Unsubscribe, send an email to:[EMAIL PROTECTED] 
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to