Dan, NFPA 101 may or may not require electrical supervision. The occupancy chapter will require a "supervised" automatic sprinkler system or just an automatic sprinkler system. The "supervised" automatic sprinkler system requires electrical supervision, but the automatic sprinkler system can be supervised via NFPA 13 methods without connection to a fire alarm system. See the new mercantile occupancy requirement (chapter 36-supervised) versus the existing mercantile occupancy requirement (chapter 37-not supervised) for an example. Supervised is defined in Chapter 9. (9.7.2).
Most require supervised automatic sprinkler systems. Pete Larrimer VA -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Tuesday, June 10, 2008 8:29 AM To: [email protected] Subject: RE: Valve Supervision Our rule of thumb has always been that when codes conflict use the most stringent, then you know you are in compliance. If otherwise in doubt, contact the AHJ. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of danarbel Sent: Tuesday, June 10, 2008 2:10 AM To: [email protected] Subject: Valve Supervision Dear all Confusion about electrical supervision of sprinkler control valves: According to NFPA 13, it is sufficient to chain lock the sprinkler control valves. I.E. no requirement to monitor the position of the valves. Other NFPA codes such as 101 and 5000, require such supervision in storage areas. IFC 2006 903.4 requires valves to be electrically supervised. I would appreciate your opinions Dan Arbel No virus found in this outgoing message. Checked by AVG. Version: 7.5.524 / Virus Database: 270.0.0/1490 - Release Date: 08-Jun-08 5:32 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)