Thom, I agree with that.

It's why I asked if anybody knows about any successful or unsuccessful tests with hi-ex and aerosol canisters,
either by FM, UL or any other recognized testlab, to get a clear picture.

Yes, may be our well-respected colleague Joe feels tempted to share his views?

Frans Stoop

At 08:32 13-6-2008 -0600, you wrote:
The FM data sheets are the result of their testing, and I believe that the
ESFR or high density area's and specific head temp's are the only way they
recommend protection of these commodities. If they don't list foam, then it
is either because they don't recommend it or haven't tested it with these
products.

Joe H. are you out there? Any insider info on this?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Frans Stoop
Sent: Friday, June 13, 2008 3:20 AM
To: [email protected]
Subject: RE: Aerosols and hi-ex foam

Thom,

The FM datasheets didn't help me any further:
FM 7-31 does not mention foam at all.
FM 4-3N has only 3 pages and points to NFPA 11A.
I'm open for other suggestions...

Frans Stoop

At 09:07 12-6-2008 -0600, you wrote:
>Frans:
>
>You need to look at FM 7-31 "Storage of Aerosol Products" as well as FM
>4-3N "Medium and High Expansion Foam"
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Frans
>Stoop
>Sent: Wednesday, June 11, 2008 6:17 PM
>To: [email protected]
>Subject: Aerosols and hi-ex foam
>
>Dear colleagues,
>
>NFPA 11 - 2007 reads in paragraph
>6.3.2 Medium- and high-expansion foam systems shall not be used on
>fires in the following hazards:
>(1)... skip...
>(5)     Liquefied flammable gas
>
>Does anyone of you know if it is the intention of this paragraph to
>prevent that storage of aerosol cans will be protected by high-expansion
foam?
>We are looking at aerosol cans that contain some butane and/or propane
>as propellant, besides a flammable liquid like paint and solvent.
>NFPA 30B only speaks about sprinkler; it doesnot tell us wether it is
>possible or not to protect storage of aerosols with foam.
>
>Are there any testresults available regarding the protection of storage
>of aerosol cans with high expansion foam?
>
>Frans Stoop
>TOS architecture & fire protection
>Netherlands