Thom, The FM datasheets didn't help me any further: FM 7-31 does not mention foam at all. FM 4-3N has only 3 pages and points to NFPA 11A. I'm open for other suggestions...
Frans Stoop At 09:07 12-6-2008 -0600, you wrote:
Frans: You need to look at FM 7-31 "Storage of Aerosol Products" as well as FM 4-3N "Medium and High Expansion Foam" Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Frans Stoop Sent: Wednesday, June 11, 2008 6:17 PM To: [email protected] Subject: Aerosols and hi-ex foam Dear colleagues, NFPA 11 - 2007 reads in paragraph 6.3.2 Medium- and high-expansion foam systems shall not be used on fires in the following hazards: (1)... skip... (5) Liquefied flammable gas Does anyone of you know if it is the intention of this paragraph to prevent that storage of aerosol cans will be protected by high-expansion foam? We are looking at aerosol cans that contain some butane and/or propane as propellant, besides a flammable liquid like paint and solvent. NFPA 30B only speaks about sprinkler; it doesnot tell us wether it is possible or not to protect storage of aerosols with foam. Are there any testresults available regarding the protection of storage of aerosol cans with high expansion foam? Frans Stoop TOS architecture & fire protection Netherlands