That's because you don't see continuous unlimited return grills, you know that Ron. That's like comparing a paper cut to a missing finger and telling me I don't need a band-aid.

Return Plenum is irrelevant (we as far as sprinklers are concerned). As already pointed out, it's no longer a concealed space.

On a related theme, we believe that a small opening (say no more than 12 inches wide) around the perimeter does not present the same problem since the centerline of the fire is away from the wall so a significant amount of the heat will be caught by the ceiling. That naturally must be discussed with the AHJ beforehand.

Roland



On Aug 5, 2008, at 6:59 AM, Fletcher, Ron wrote:

You can have an unlimited number 2'x4' return air grills in the ceiling
without adding sprinklers above but put a 4" wide slot around edge of
the room and sprinklers are required. Go figure.

Where do you get "a plenum thus requiring sprinklers"?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ