Well it would seem that there is no engineered solution to this at the time.
Perhaps Roland will pursue his testing.





"As a PE, lacking any further guideance or test data to make any sort of 
engineering judment or equivalency argument, NFPA 13 only gives you one 
obvious interpretation.  In my opinion, based on the situation described, it

is not a concealed space, therefore sprinklers may not be omitted above the 
ceiling, and I would not entertain any offers to make a contrary judgement."