As a PE, lacking any further guideance or test data to make any sort of
engineering judment or equivalency argument, NFPA 13 only gives you one
obvious interpretation. In my opinion, based on the situation described, it
is not a concealed space, therefore sprinklers may not be omitted above the
ceiling, and I would not entertain any offers to make a contrary judgement.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by one
or more legal privileges. It is intended solely for the use of the
addressee identified above. If you are not the intended recipient, any use,
disclosure, copying or distribution of this e-mail is unauthorized. If you
received this e-mail in error, please notify the sender immediately at the
above captioned address.
----- Original Message -----
From: "Russell" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, August 05, 2008 12:23 PM
Subject: RE: Floating Ceilings
As a PE, what approach would you take if faced with this situation?
Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
"My gut feeling here is that if you choose to support the more liberal
interpretation, that this will NOT require both above and below
protection,
especially without any significant test data to back it up at this point,
that this is not the place for a NICET technician to make this decision,
or
for that matter to try to "sell" it to the local AHJ. Do you really want
that liability? Not to mention whether you are exceeding your "authority"
under NICET rules for practicing engineering?"
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)