If it aint broke don't fix it. I read about a lot of sprinkler saves but
hardly ever here of a sprinklered office building or anything else
burning to the ground that had a working sprinkler system. Do all the
fuel loading calculations you want but I think history bears out that LH
works. A pet peeve of mine is AHJ's or EOR's that require something
other than the published code with no empirical, scientific or
historical data to support the change.

Ron Fetcher
Aero Automatic Sprinkler
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, November 18, 2008 2:29 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa
ExistingPipeScheduledSystem Water Supply)

Agreed about the office thing.  Recent client wanted to try and convince
me that they didn't need sprinklers in the office because their building
was all concrete.  I said that's nice but a fire will most likely start
INSIDE your concrete building unless you get hit by a meteor, which will
probably still result in a fire inside.  I have noticed some
jurisdictions requiring a minimum design criteria of .15 for office
areas.  The Light hazard classification for office environments needs to
go away. It's just not realistic when it comes to fuel loading and
potential hazards.

In most industrial environments the chance for fire is usually far less
than in most offices.  Reason being the factory environments have
stricter rules on housekeeping and storage than most offices.  Don't see
a lot of overloaded power strips in manufacturing plants either, boxes
of rolled plotter paper on plastic, printer and copy machine toner,
etc......

But we digress, back to the mechanical room...................

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Tuesday, November 18, 2008 4:21 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing
PipeScheduledSystem Water Supply)

About the same funny as where I'm sitting right now and I suspect you
are too.  I'm a room with a lot of class III materials, stored up to 6'
high, some in solid piles and harder to burn, some rolled paper easy to
burn, about 20 lbs of exposed non-expanded plastics and about 5 lbs of
non-exposed expanded plastic, more electrical violations than I like to
admit but some how it's light hazard because I call it an office and our
mech room is OH by tradition and few boxes of holiday decorations.
Maybe we should start calling mechanical room's offices. They are less
hazardous than where I'm sitting even with the decorations.  With modern
odd names and more from other cultures all electrical rooms are now
labeled as Electa's office and the mechanical room is Phan's office.

BTW I've also just always done the OH thing in mech/electrical and let's
throw in kitchens.

Also, thanks to those pointing out the mixed hazard stuff and 400 sq.ft.
Never noticed that before and I don't have a good or bad excuse.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [EMAIL PROTECTED]

Mail: P.O. Box 69
        Waverly, MN 55390

Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, November 18, 2008 2:39 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing Pipe
ScheduledSystem Water Supply)

Mechanical room and no storage, now that's funny.

Where else is there to put all the holiday decorations and the last 10
years worth of business records, I mean like why let all that open space
be wasted?

No way could I see any justification for either one of these rooms being
considered LIGHT Hazard.

Must have been politicians that came up with that ruling.   ;)



Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Sornsin
Sent: Tuesday, November 18, 2008 3:21 PM
To: '[email protected]'
Subject: RE: Mech/Electrical room classification (wa Existing Pipe
ScheduledSystem Water Supply)

Oooh! Good one!

I my experience, we have done it that way out of tradition.  Maybe
because electrical/mechanical rooms can be combined; many mechanical
rooms have fuel fired equipment; both kinds of rooms often become
storage rooms (rightfully or wrongly). If some engineer doesn't specify
it, one can certainly argue in many cases that these rooms may not
warrant protection beyond light hazard.
But I always spec them OH; as a contractor we designed them that way,
too.

The ND members of this forum are all too familiar with the ND Dept of
Health making them change their non-ordinary temperature heads to
ordinary because "the mechanical room is really an air handling room
with no storage and thus warrants light hazard protection and ordinary
temp heads." Never mind the additional sprinklers, additional density,
potential for future storage, and lack of human occupancy. "Those head
must be changed!"

Mark Sornsin

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, November 18, 2008 1:48 PM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

Out of curiosity where do come up with electrical/mechanical rooms being
OH?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, November 18, 2008 11:15 AM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

We need to be careful in our use of words here. This building is a light
hazard occupancy.

All light hazard occupancy buildings will contain some areas of Ordinary
hazard, such as kitchens laundry rooms, or electrical/mechanical rooms.
These areas do not change the classification of the hazard for the
entire building, or the hose stream requirements.

While these areas must be protected per their specific hazard for
density, if your largest OH II area is only 600 Sf then you only provide
OH II density for that 600 SF area, and any smaller areas of the same
hazard.
Usually this is done by reducing the spacing per head to like 75 Sf per
head with 5.6K will give you 0.20 at just about 7 PSI. So for your 600
Sf you would calc 8 heads unless your Light hazard area required more
than 8 heads, or was more remote, with the same number of heads.

Now because this was installed pipe schedule, you need to know if OH
pipe schedule was used in the OH areas? Actually you need to Hydraulic
the entire system to ensure the loss from the backflow will allow it to
work per NFPA 13, 2007 8.17.4.6.2.  But as far as your question goes
"The Occupancy is Light Hazard" for the use of 11.2.2.1 so 15 Psi and
the 30-60 Min.
duration
is OK.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Timothy:

You must design for Ordinary Hazard in the Ordinary Hazard areas; Light
in the Light Hazard Areas.  There is no "overall building design
approach"; the building is not Light Hazard unless ALL areas of the
building are light hazard.

Mark A. Sornsin, PE

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to