Mechanical room and no storage, now that's funny.

Where else is there to put all the holiday decorations and the last 10 years 
worth of business records, I mean like why let all that open space be wasted? 

No way could I see any justification for either one of these rooms being 
considered LIGHT Hazard.

Must have been politicians that came up with that ruling.   ;)



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Tuesday, November 18, 2008 3:21 PM
To: '[email protected]'
Subject: RE: Mech/Electrical room classification (wa Existing Pipe 
ScheduledSystem Water Supply)

Oooh! Good one!

I my experience, we have done it that way out of tradition.  Maybe because 
electrical/mechanical rooms can be combined; many mechanical rooms have fuel 
fired equipment; both kinds of rooms often become storage rooms (rightfully or 
wrongly). If some engineer doesn't specify it, one can certainly argue in many 
cases that these rooms may not warrant protection beyond light hazard. But I 
always spec them OH; as a contractor we designed them that way, too.

The ND members of this forum are all too familiar with the ND Dept of Health 
making them change their non-ordinary temperature heads to ordinary because 
"the mechanical room is really an air handling room with no storage and thus 
warrants light hazard protection and ordinary temp heads." Never mind the 
additional sprinklers, additional density, potential for future storage, and 
lack of human occupancy. "Those head must be changed!"

Mark Sornsin

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, November 18, 2008 1:48 PM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

Out of curiosity where do come up with electrical/mechanical rooms being OH?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, November 18, 2008 11:15 AM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

We need to be careful in our use of words here. This building is a light hazard 
occupancy.

All light hazard occupancy buildings will contain some areas of Ordinary 
hazard, such as kitchens laundry rooms, or electrical/mechanical rooms.
These areas do not change the classification of the hazard for the entire 
building, or the hose stream requirements.

While these areas must be protected per their specific hazard for density, if 
your largest OH II area is only 600 Sf then you only provide OH II density for 
that 600 SF area, and any smaller areas of the same hazard.
Usually this is done by reducing the spacing per head to like 75 Sf per head 
with 5.6K will give you 0.20 at just about 7 PSI. So for your 600 Sf you would 
calc 8 heads unless your Light hazard area required more than 8 heads, or was 
more remote, with the same number of heads.

Now because this was installed pipe schedule, you need to know if OH pipe 
schedule was used in the OH areas? Actually you need to Hydraulic the entire 
system to ensure the loss from the backflow will allow it to work per NFPA 13, 
2007 8.17.4.6.2.  But as far as your question goes "The Occupancy is Light 
Hazard" for the use of 11.2.2.1 so 15 Psi and the 30-60 Min.
duration
is OK.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Timothy:

You must design for Ordinary Hazard in the Ordinary Hazard areas; Light in the 
Light Hazard Areas.  There is no "overall building design approach"; the 
building is not Light Hazard unless ALL areas of the building are light hazard.

Mark A. Sornsin, PE

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)