About the same funny as where I'm sitting right now and I suspect you are
too. I'm a room with a lot of class III materials, stored up to 6' high,
some in solid piles and harder to burn, some rolled paper easy to burn,
about 20 lbs of exposed non-expanded plastics and about 5 lbs of non-exposed
expanded plastic, more electrical violations than I like to admit but some
how it's light hazard because I call it an office and our mech room is OH by
tradition and few boxes of holiday decorations. Maybe we should start
calling mechanical room's offices. They are less hazardous than where I'm
sitting even with the decorations. With modern odd names and more from
other cultures all electrical rooms are now labeled as Electa's office and
the mechanical room is Phan's office.
BTW I've also just always done the OH thing in mech/electrical and let's
throw in kitchens.
Also, thanks to those pointing out the mixed hazard stuff and 400 sq.ft.
Never noticed that before and I don't have a good or bad excuse.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [EMAIL PROTECTED]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, November 18, 2008 2:39 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing Pipe
ScheduledSystem Water Supply)
Mechanical room and no storage, now that's funny.
Where else is there to put all the holiday decorations and the last 10 years
worth of business records, I mean like why let all that open space be
wasted?
No way could I see any justification for either one of these rooms being
considered LIGHT Hazard.
Must have been politicians that came up with that ruling. ;)
Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Tuesday, November 18, 2008 3:21 PM
To: '[email protected]'
Subject: RE: Mech/Electrical room classification (wa Existing Pipe
ScheduledSystem Water Supply)
Oooh! Good one!
I my experience, we have done it that way out of tradition. Maybe because
electrical/mechanical rooms can be combined; many mechanical rooms have fuel
fired equipment; both kinds of rooms often become storage rooms (rightfully
or wrongly). If some engineer doesn't specify it, one can certainly argue in
many cases that these rooms may not warrant protection beyond light hazard.
But I always spec them OH; as a contractor we designed them that way, too.
The ND members of this forum are all too familiar with the ND Dept of Health
making them change their non-ordinary temperature heads to ordinary because
"the mechanical room is really an air handling room with no storage and thus
warrants light hazard protection and ordinary temp heads." Never mind the
additional sprinklers, additional density, potential for future storage, and
lack of human occupancy. "Those head must be changed!"
Mark Sornsin
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, November 18, 2008 1:48 PM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply
Out of curiosity where do come up with electrical/mechanical rooms being OH?
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, November 18, 2008 11:15 AM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply
We need to be careful in our use of words here. This building is a light
hazard occupancy.
All light hazard occupancy buildings will contain some areas of Ordinary
hazard, such as kitchens laundry rooms, or electrical/mechanical rooms.
These areas do not change the classification of the hazard for the entire
building, or the hose stream requirements.
While these areas must be protected per their specific hazard for density,
if your largest OH II area is only 600 Sf then you only provide OH II
density for that 600 SF area, and any smaller areas of the same hazard.
Usually this is done by reducing the spacing per head to like 75 Sf per head
with 5.6K will give you 0.20 at just about 7 PSI. So for your 600 Sf you
would calc 8 heads unless your Light hazard area required more than 8 heads,
or was more remote, with the same number of heads.
Now because this was installed pipe schedule, you need to know if OH pipe
schedule was used in the OH areas? Actually you need to Hydraulic the entire
system to ensure the loss from the backflow will allow it to work per NFPA
13, 2007 8.17.4.6.2. But as far as your question goes "The Occupancy is
Light Hazard" for the use of 11.2.2.1 so 15 Psi and the 30-60 Min.
duration
is OK.
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
Timothy:
You must design for Ordinary Hazard in the Ordinary Hazard areas; Light in
the Light Hazard Areas. There is no "overall building design approach"; the
building is not Light Hazard unless ALL areas of the building are light
hazard.
Mark A. Sornsin, PE
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)