Generator rooms are at .25 gpm/sf NFPA 13, 21.32.1.7

Fire Pump rooms the same. (next paragraph)

That would put them into the OH II category.

Most electrical rooms don't require sprinklers if they follow the NFPA 13 and 
bldg. code requirements for rated construction and the other items listed 
including no liquid filled transformers.

Elevator pits, well that's kind of obvious.

Mechanical rooms aren't given any options so height of room or other "logic" 
has no Code support.  



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, November 18, 2008 5:07 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa ExistingPipe 
ScheduledSystem Water Supply)

I knew there was a SF limit but without looking it up I said 600 SF(Just too 
lazy today!). Thanks Ed! 400 Sf and my post remains unchanged.

The question is can we call Electric and mechanical rooms OH I? I'd say that 
one limit is if the ceiling is less than 9'-6" (18" clear below heads should 
not be more than 8'-0" high storage) why not? How about emergency generator or 
fire pump rooms?(NFPA 20, 5.12.1.1.2 only says fully sprinklered, no Design 
density.) Same kind of thing? For kitchens see A21.36.1, or 5.3.1. 

And if you look at A5.4.1, Elevator Equipment rooms and pits should be EX I if 
you CANNOT prove the Hyd. Fluid is "Non-Combustible"

I would say that if the rest of the building is OH II then don't sweat the M/E 
rooms, just use the same coverage. But if the rest of the building is LH, then 
you may want to look at the actual conditions in the space.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



With modern odd names and more from other cultures all electrical rooms are now 
labeled as Electa's office and the mechanical room is Phan's office.

BTW I've also just always done the OH thing in mech/electrical and let's throw 
in kitchens.  


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to