Jamie,

Is the 18 at the flow switch a maximum to keep the paddle on the
switch or a minimum to insure the switch operates? I would think the
later.

On Tue, Dec 28, 2010 at 4:49 PM, Jamie.seidl <[email protected]> wrote:
> Yes there are velocity requirements in the UFC along with the 3000 sqft HMRA. 
>   While I don't have them in front of me, 20 or 24 fps comes to mind, and 18 
> fps at the flow-switch (per UL). This always brings me back to the point of 
> when your calculating the HMRA, wouldn't you also need to calc the closest 
> area?  No pressure loss = more flow?  I typically do this calc when sizing a 
> tank/pump set up for sizing of the tank v.s. Duration...  Am I wrong?
>
> Jamie
> Sent from my iPhone
>
> On Dec 28, 2010, at 7:25 PM, [email protected] wrote:
>
>> The technical parts of this discussion have been interesting.
>>
>> I may have lost something in the trail of emails, but is there anything in
>> UFC 3-600-01 or other UFC standards that require  velocity limitations.
>>
>> I have to go to Afghanistan in a couple of weeks  to inspect some systems
>> that were done by a South Korean company.  Prior to that we have to
>> evaluate and do calcs. where pipe was schedule sized.  The fire protection
>> work for the bases is supposed to conform to UFC 3-600-01, but no other
>> govt. stds. that I know of.  Because these buildings are not likely to be
>> long term, conservative design is not necessary and as many have pointed
>> out, 0.10/3000 is twice the norm anyway.
>>
>> I respectfully request no political commentary with the answer.
>>
>> Thanks in advance,
>>
>>
>>
>> James L (Jim) Roberts, PE/SET | FLUOR | Principal Fire Protection Engineer
>> – Central Engineering | [email protected] | IODC 20.5149 | O
>> +1.864.281.5149 | www.fluor.com
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> From:       [email protected]
>> To:         [email protected]
>> Date:       12/28/2010 05:49 PM
>> Subject:    Re: USACE Velocity
>> Sent by:    [email protected]
>>
>>
>>
>> Vince,
>> Believe it or not, there are considerable differences between UFC and GSA
>> fire protection requirements.
>>
>> I feel that it is better that we compete at the higher end of fire
>> protection rather at the lower end.
>>
>> There is difference in quality for longetivity.  Anyone who thinks that
>> everything should be equal and minimal across the government only has to
>> remember the volkswagen (peoples car) that was destined to be the same for
>> everyone in another country.
>>
>> Competition is good but it does not have to be at the low end of a business
>> and specs do not have to be same from owner to owner or agency to agency.
>>
>> Rahe
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> ------------------------------------------------------------
>> The information transmitted is intended only for the person
>> or entity to which it is addressed and may contain
>> proprietary, business-confidential and/or privileged material.
>> If you are not the intended recipient of this message you are
>> hereby notified that any use, review, retransmission, dissemination,
>> distribution, reproduction or any action taken in reliance upon
>> this message is prohibited. If you received this in error, please
>> contact the sender and delete the material from any computer.
>>
>> Any views expressed in this message are those of the individual
>> sender and may not necessarily reflect the views of the company.
>> ------------------------------------------------------------
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to